Question

The generator has an internal voltage of 1.5 pu and an inertia constant (H) of 3 MJ/MVA. Determine whether the generator is transiently stable or not if the fault clearing time is 0.15 seconds.

Q23.PNG

A generator, with a transient reactance of j0.5 pu, delivers 1.0 pu real power to an infinite bus through a transformer and two transmission lines in parallel as shown below. A solid three phase fault occurs at position near “F” which is cleared by opening both ends of the transmission leaving only one line in service. 

The generator has an internal voltage of 1.5 pu and an inertia constant (H) of 3 MJ/MVA. Determine whether the generator is transiently stable or not if the fault clearing time is 0.15 seconds.

1 0
Add a comment Improve this question Transcribed image text
Answer #1

hot rohtul Generator infinite bus go.spu E = Lolopu tj +5%8p* 7 jo.zpur Yg - jo.5pu, delivered real power (P) = 124 H = 3 M4 f=bottz 8 = 1x 21TX60 X 6.152 Чx3 0.34 Pm= Pe initially at balance Pm=1 8= 0.37 rad 8= 21.2° As we com see athat LScr ie t

Add a comment
Know the answer?
Add Answer to:
The generator has an internal voltage of 1.5 pu and an inertia constant (H) of 3 MJ/MVA. Determine whether the generator is transiently stable or not if the fault clearing time is 0.15 seconds.
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT