Question

= A 50 Hz synchronous generator with an inertia constant of 3 MWS/MVA and Xd 0.3 per unit delivers power to a large metropol

a) Calculate the generator internal voltage E’ and the initial generator power angle δ prior to the fault.

b) Write the swing equation for the machine. What will be the generator angle δ' at the instant when the fault is cleared after 0.1 s?

c)Determine whether the synchronous generator will remain stable after the fault is cleared.

d) If the fault clearing is delayed, determine the critical clearing angle and critical clearing time.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

TL mm mm x=0.1 PU ~) Infinite Bus N=1.05 Lo f-502 9 xd=0.3pu P = 0.8 pu at 0.85 power factor P = V 1 cos o 0.8 = 6.05) (1) (swing Equation, 2h des Wo (Pm- Pe) pu Pe=0 fault . when fault occurred , Pm = Pe before Pe = E.V. sing = 0.8 pu Уl+X 228 2x3-remains &table () If 8<8c ý system Pmax PMA EV = 6.275) (ros) Xarx OY PM = 0.epu Semo Ilmax = 3.34 SC Aso pu so Using equal

Add a comment
Know the answer?
Add Answer to:
a) Calculate the generator internal voltage E’ and the initial generator power angle δ prior to...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through trans...

    A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...

  • Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to...

    Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to an infinite us through a transformer and the transmisiones as shown in the Figure. All system reactances are marked on the diagram and are expressed on a common MVA base. The generator dies a power of Auto busbar 1. The magnitude of the generator's excitation voltage e'is 12 pu, and the infinite bus voltage is -1.00u. If a 3-phase fault occurs at the middle...

  • A synchronous generator is connected to an infinite bus via a transformer and a network of...

    A synchronous generator is connected to an infinite bus via a transformer and a network of transmission lines, as illustrated in Figure 1 below. Per unit reactances for all elements are shown to a common system base. The generator is delivering 1.1 per unit real power to the infinite bus, and the infinite bus voltage is regulated to 1.05 per unit. The excitation voltage of the synchronous generator is set to 1.30 per unit. The inertia constant of the generator...

  • The generator has an internal voltage of 1.5 pu and an inertia constant (H) of 3 MJ/MVA. Determine whether the generator is transiently stable or not if the fault clearing time is 0.15 seconds.

    A generator, with a transient reactance of j0.5 pu, delivers 1.0 pu real power to an infinite bus through a transformer and two transmission lines in parallel as shown below. A solid three phase fault occurs at position near “F” which is cleared by opening both ends of the transmission leaving only one line in service.  The generator has an internal voltage of 1.5 pu and an inertia constant (H) of 3 MJ/MVA. Determine whether the generator is transiently stable...

  • Power system analysis

    Figure shows a single-line diagram of a three-phase, 60-Hz synchronous generator, connected through a transformer and parallel transmission lines to an infinite bus. All reactances are given in perunit on a common system base. If the infinite bus receives 1.0 per unit real power at 0.95 p.f. lagging. If circuit breakers B13 and B22 are opened after three cycles and then reclosed when the power angle reaches 35°.123.png Assume ωpu(t) = 1.0 pu in the swing equation. Assume that the temporary...

  • XTR-0.10 B12 X12-0.20 B21 V= 1-0 x,-0.30 X23-0.20 B13 X13-0.10 B22 Fig. 1. Single-machine infinit...

    XTR-0.10 B12 X12-0.20 B21 V= 1-0 x,-0.30 X23-0.20 B13 X13-0.10 B22 Fig. 1. Single-machine infinite bus system (Simple system-I) 1. The synchronous generator in Fig.1 delivers 0.8 p.u. real power at 0.85 power factor leading at voltage at infinite bus (1.0 р.u. voltage). Determine a) The real and reactive power output of the generator b) The generator internal voltage c) An equation for the electrical power delivered by the generator as a function of 8. d) For a three-phase-to ground...

  • Help Q4)A generator operating at 60 Hz delivers 1.0 pu power to an infinite bus through...

    Help Q4)A generator operating at 60 Hz delivers 1.0 pu power to an infinite bus through a transmission circuit in which resistance is ignored. A fault took place reducing the maximum power transferable to 0.5 p.u whereas before the fault, this power was p.u and after the clearance of the fault, it is 1.5 p.u. Using equal area criterion, determine the critical clearing angle. 2.0

  • A 100MVA synchronous generator is connected to a 25kV infinite bus through two parallel transmission lines....

    A 100MVA synchronous generator is connected to a 25kV infinite bus through two parallel transmission lines. The synchronous reactance of the generator is 2.5Ω. Each transmission line has inductive reactance of 2Ω and 0.2Ω resistance. The generator delivers 90MVA to the infinite bus at 0.8 power factor lagging.    For the above conditions, calculate: a. The terminal voltage of the generator      b. The equivalent field voltage and power angle      c. The real power output at the generator terminals    d. The reactive...

  • A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature...

    A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter

  • Figure 1 shows a single-line diagram of a three phase, 60-Hz, synchronous generator, connected th...

    Figure 1 shows a single-line diagram of a three phase, 60-Hz, synchronous generator, connected through a transformer and parallel transmission lines to an infinite bus. All reactances are given in per unit on a common system base. In steady state, the infinite bus receives 1.0 per unit real power at 0.95 power factor lagging. The generator in Figure 1 is initially operating in steady state, when circuit breaker B12 inadvertently opens. Use the equal area criterion to calculate the maximum...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT