Given Data:
!) Cold storage maintained at 200 f
2) Outside air temperature at 900f
3) Heat Removal= 120000 Btu/h
4) Power input= 20 hp
To Determine:
1) The actual coefficient of the air conditioning unit
2) The minimum theoretical horsepower required to operate a cooling unit under these conditions
Solution
1) Actual coefficient of air conditioning unit
Actual coefficient of performance= 2.36
2) Minimum theoretical horsepower required
Provided T1= Higher temperature & T2= Lower temperature
Here T1= 900F= 32.220C & T2= 200F= -6.670C
Theoretical COP= 6.85
Minimum power required= 6.88 hp
3. A cold storage facility is maintained at 20°F when the outside air temperature is 90°RF...
Q.3 Outside air at 90°F, 1 atm, and 95% relative humidity with a flow rate of 4000 cfm is blown over an evaporator of a refrigeration system and exits at 75°F and 60% relative humidity. The refrigeration system has operating with the COP of 2.5. Determine (a) the amount of cooling provided by the evaporator Btu/hr (b) the amount of water condensed in the evaporator, lbm/hr and (c) the power required by the compressor of the refrigerator in kW. 1...
Question 4 Page 15 It is required to 125 marks] design a cold storage for storing vegetables with the following available data Outside design conditions 36°C DBT. 28 C WBT Inside design conditions T2 19°C DBT, 60% RH Infiltrated air 180 mhr V ms-7.83 kg/s Fresh air supplied from outside 4500 mhr Total mass of air supplied to the room Sensible heat gain through glass SH,5.5AW Sensible heat gain through walls and roof H 10.8 kW Ihr KJ Sensible heat...
1.3 127 5.3 3.(10 pts) A cold storage room (10 m x 10 m x 10 m) is being maintained at 2 °C using a vapor compression refrigeration system that uses R-134a. The evaporator and condenser temperatures are -20 and 40°C, respectively. The walls and ceiling of the storage room is constructed of 15 cm thick concrete (thermal conductivity-1.37 WIm K]) and 4.3 cm thick insulation (thermal conductivity-0.04 W/[m K). The outside insulation surface temperature of the walls (or ceiling)...
System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22 oC Heat Load = 4.2 kJ/sec rate at which heat must go in to the air conditioner to be removed from the car’s interior Refrigerant: R134a HINT: Heat enters an air conditioning system where? Refrigerant 134a … - leaves the evaporator coil and enters the compressor as a saturated vapor at the evaporator pressure of 2.8 bars. - It leaves the compressor at...
Two large parallel plates with surface conditions approximating those of a blackbody are maintained at 800°C and 100°C, respectively. Determine the rate of heal transfer by radiation between the plates in Wim and the radiative heat transfer coefficient in W/m K ) 12 Write down the one-dimensional sent heal conduction equation for a plane wall with constant thermal conductivity and heat generation in its simplest form, and indicate what each variable represents 13 Write down the one-dimensional transient heat conduction...
summatize the following info and break them into differeng key points. write them in yojr own words apartus 6.1 Introduction—The design of a successful hot box appa- ratus is influenced by many factors. Before beginning the design of an apparatus meeting this standard, the designer shall review the discussion on the limitations and accuracy, Section 13, discussions of the energy flows in a hot box, Annex A2, the metering box wall loss flow, Annex A3, and flanking loss, Annex...
Should World Kitchen outsource Pyrex production and close the Charleroi plant? If so, how many suppliers should the company employ and where should they be located? We were unable to transcribe this imagedishwas resulted from a process that pressed together yers of thin, strengthened opaque glass. products if they were moved overseas and simply source the lower-cost private-label versions directly sales and marketing functions. THE MARKET Givsn its extensive experience with outsourcing the Giobal Sourcing Department at World Kitchen had...