ANSWER ::
Reinforced concrete columns
The design of reinforcement can be either spiral or tied. Spiral columns are cylindrical with a continuous helical bar wrapped around the column. This spiral provides support in the transverse direction. Tied columns have closed lateral ties spaced approximately uniformly across the column.
Problem 2 Assume normal weight concrete with fe' = 3,500 psi and steel bars of Grade...
Assume normal concrete weight (wc = 143 lb/ft) with specified compressive strength fc = 4,000 psi, and steel Grade 60 (fy = 60,000 psi). For design loads assume dead load wd = 30 lb/ft? (excluding self-weight) and live load we = 100 lb/ft. Finally assume that the steel percentage ratio is equal to p= 0.18fc/fy. Design an interior one-way simply supported slab with a 15 ft span using the above assumptions. Show sketches of one-way slab cross section, including reinforcing...
Design a square tied column to carry axial service loads of 320 kips dead load and 190 kips live load. There is no identified applied moment. Assume that the column is short. Use f’c =4000 psi and fy = 60,000 psi. Also, draw the flexural and shear reinforcement on a sketch. Case 3: Design of Short Columns - Small Eccentricity Design a square tied column to carry axial service loads of 320 kips dead load and 190 kips live load....
Problem 3 Assume normal concrete weight (wc = 143 lb/ft) with specified compressive strength fc = 4,000 psi, and steel Grade 60 (fy = 60,000 psi). For design loads assume dead load wd = 30 lb/ft? (excluding self-weight) and live load wų = 100 lb/ft. Finally assume that the steel percentage ratio is equal to p= 0.18fc'/fy. Design an interior one-way simply supported slab with a 15 ft span using the above assumptions. Show sketches of one-way slab cross section,...
. Deisgn a reinforced concrete cross-section with unknown dimensions Problem 1 Design the steel reinforcement for the beam shown in Figure 1 that supports its own self-weight, a uninformly distributed dead load, a uniformly distributed live load, and a live point load located at midspan. In your solution, you should select the area of reinforcement, the number and size of reinforcing bars, and the section depth in order to receive full credit. Assume J 5,000 psi, fy 60,000 psi. 16...
Problem 4 (30 points) Design a short square tied column to carry an axial dead load of 150 kips and a live load of 400 kips. Assume that the applied moments on the column are negligible. Use fc = 4,000 psi and fy = 60,000 psi. Assume a steel ratio of 3% (pg = 0.03).
15.3. psi. Design a single-column footing (including dowels) to support an 11 in. square column reinforced with eight No. 9 (No. 29) bars centered 2.5 in. from the column faces (equal number of bars on each face). The unfactored axial dead load = 135 kips, and the unfactored axial live load=125 kips. For the column, f=4000 psi and f=60,000 psi. The base of the footing will be 3 ft below grade. The allowable soil bearing pressure is 3000 lb/ft2. Material...
concrete design Design a circular column with spiral reinforcement to resist a service dead load of 350 kips and a service live load of 325 kips. For your design: Use fe'-5 ksi and f, 60 ksi. Utilize an initial reinforcement ratio, Ps 0.03. . Use a clear cover of 1.5 inches. . Limit your design to #8 bars for longitudinal reinforcement. Design both longitudinal and spiral reinforcement. Design a circular column with spiral reinforcement to resist a service dead load...
Name: Date: Part II: Numerical responses 1. (+35) Design a rectangular reinforced concrete beam (tension steel only) for a simply span of 30 ft. Uniform service loads are 2 kips/ft dead load (included the beam weight) and 3.0 kips/ft live load. The beam is to be not exceed 16 inch wide due to column size. Use fe'=4000psi and fy 60000psi. Sketch your design and calculate Mn for the beam you design. Note: this is an open-end design for you to...
Show Diagrams Case 2: Design of Short Columns - Small Eccentricity Determine whether the spiral column of cross section shown in Figure 2.1 is adequate to carry a factored axial load Pu of 540 kips. Assume small eccentricity. Check the spiral. Use fc 4000 psi and fy -60,000 psi. 큠.φ @ 2 7-'8 bars 1cover Figure 2.1 Spiral Column Case 2: Design of Short Columns - Small Eccentricity Determine whether the spiral column of cross section shown in Figure 2.1...
m 3: (20 points) Design the stirrup spacing for the beam shown below. Change your design between Zones 1, 2, and 3 of the beam length, using a uniform spacing in each zone. Ignore the self-weight of the beam. Loads on the beam are service loads so load factors must be applied according to ACI 318 (subscripts "d" and T" denote dead and live loads, respectively). Material strengths are fe 4,0oo psi and fy 60,000 psi. The total factored shear...