Sol
(a) To calculate the fault at F1:
Network Data
SYSTEM DESCRIPTION | VALUE | UNIT | |||
Service Voltage Un | 13.2 | kV | |||
Short Circuit Current at 11kV System Ik | 4.37 | kA | |||
Short Circuit Apparent Power of System Sk = √3*Un*Ik | 100 | MVA |
Transformer Data
Apparent Power Transformer Pn | 2000 | kVA | |||
Utilization Current Rating In | 2406 | A | |||
Impedance Uz | 5.75 | % | |||
Voltage VL-L (cU'n) | 480 | V | |||
Voltage VP-N | 277 | V |
DESCRIPTION | SYMBOL | EQUATION | VALUE | REMARKS | |||||||
Network | |||||||||||
Impedance of Source Network | Zs | ( cU'n/1000)^2/Sk | 0.002304 | Ohm | Refer IS 13234 page no 17 eq. 5a | ||||||
**Voltage Factor,c of 1.1 has been considered for medium voltage (> 1KV to 35KV) as per IS 13432,Pg-41,Table-1 | |||||||||||
X/R=12 | 1.487655095 | ||||||||||
Reactance of Source | Xs | 0.002296041 | Ohm | ||||||||
Resistance of Source | Rs | 0.00019134 | Ohm |
Transformer | |||||||||||
X/R=5 | 1.373400767 | ||||||||||
Impedence of Transformer | Ztr | (VL-L)^2*Uz/((Pn*100)*1000) | 0.006624 | Ohm | Refer IS 13234 page no 18 eq. 6 | ||||||
Resistance of Transformer | Rtr | 0.001299073 | Ohm | ||||||||
Reactance of Transformer | Xtr | 0.006495366 | Ohm | ||||||||
Total Resistance | Rt | Rs + Rtr | 0.00149041 | Ohm | |||||||
Total Reactance | Xt | Xs + Xtr | 0.008791408 | Ohm | |||||||
Cable Impedance | Zb | 0.00013 | Ohm | ||||||||
Total Impedence | Zt | Sqrt(Rt^2+Xt^2) | 0.009046848 | Ohm | |||||||
3 Phase Fault Just After Transformer (in kA) | Isc 3PH | VL-L/(3^0.5*Zt*1000) | 30.63 | kA | Refer IS 13234 page no 22 eq. 14 |
2) To calculate the fault at F2
225KVA transformer Data
Apparent Power Transformer Pn | 225 | kVA | |||
Utilization Current Rating In | 625 | A | |||
Impedance Uz | 5.75 | % | |||
Voltage VL-L (cU'n) | 208 | V | |||
Voltage VP-N | 120 | V | |||
X/R, Ratio | 1 |
Transformer -225 KVA | |||||||||||
X/R=5 | 0.785398163 | ||||||||||
Impedence of Transformer | Ztr | (VL-L)^2*Uz/((Pn*100)*1000) | 0.011056356 | Ohm | Refer IS 13234 page no 18 eq. 6 | ||||||
Resistance of Transformer | Rtr | 0.007818024 | Ohm | ||||||||
Reactance of Transformer | Xtr | 0.007818024 | Ohm | ||||||||
Total Resistance | Rt | Resitance of Network + Resistance of transformer 2000KVA & Resistance of 225KVA transformer | 0.00930843 | Ohm | |||||||
Total Reactance | Xt | Network Reactance + 2000KVA Reacatce + 225KVA Reacatnce | 0.016609432 | Ohm | |||||||
Cable Impedance | Zb | 0.00026 | Ohm | ||||||||
Total Impedence | Zt | Sqrt(Rt^2+Xt^2) | 0.019299962 | Ohm | |||||||
3 Phase Fault Just After Transformer (in kA) | Isc 3PH | VL-L/(3^0.5*Zt*1000) | 6.22 | kA | Refer IS 13234 page no 22 eq. 14 |
3) Refer to the one line diagram on the next page. Assuming copper conductor and using...
1. The color of the outer finish of the insulation or tape marking a grounded conductor must be A. black B. green. C. white or gray D. yellow finish. 2. When the main bonding jumper in a residential el ectrical system is a screw only, the screw must be identified with a A. white B. red C. green D. black The grounding electrode conductor should be installed without a splice, unless the splice is made using exothermic welding or by...
what information needed? 3. Repeat Example 7.8, using a 100 kVA transformer and #3/0 AWG and #2 AWG cables for the SLs and SDs, respectively Show the procedure to arrive at the following answers (a) 0.72 pu A (b) 0.050 pu V Example 7.8 residential secondary distribution system. Assume that the distribution trans- Figure 7.11 shows former capacity is 75 kVA (use Table 7.1), all secondaries and services are single-phase three wire, nominally 120/240 V, and all SLs are of...
5. (5pts) The figure is a CMOS clock circuit using an inverter. Because R1 resistor is ten times larger than R2, we can neglect any current through R2. Then, you can approximate this circuit as a familiar simple RC transient circuit. Mathematically, this approximation leads to a simple differential equation according to Kirchhoff's junction rule: cdiz-n.W-Y. Since Z is constant, this equation R1 IM W .001uF R2 100k UIC 4069 UID 4069 becomes dwwr The solution of this equation is...
and negligible shunt admittance. Calculate the resistance and reactance from the table on Page 4. It delivers 500KVA at 2400V to the load and a 0.90 lagging power factor. Calculate the following a) The required sending end voltage b) The required sending end power factor c) The percent voltage regulation at the receiving end SHOW ALL YOUR CALCUALTIONS feet long. 470 eU steel conduit hase dietribution transformer with voltage 2400/240VAC (center I Table 9 Alternating-Curreat Resistunce und Reactance for 600-Volt...
The three figures below show a balanced three phase Delta, its Wye equivalent and the single phase equivalent of the three phase Wye. All three representations have a complex load ZALD or ZYLD and a complex line impedance ZLINE Refer to these diagrams when answering questions 1-4. ZLINE Vab= 679 L 30° ZLINE ZALD ZLINE = 2+1 DELTA ZALD= 18+24j2 LINE ZLINE ZLINE ZYLD 7yun WYE WYE ZYLD ZLINE ZLINE Van Complex Load ZYLD Single Line WYE 1) In the...
The ratings of the components shown in the one-line diagram are G1: 25 MVA, 13.8 kV, x-0.15 pu G2:15MVA, 13 kV, x = 0.1 5 pu. TI : 25 MVA, 13.2/69 kV, x-0. I 1 pu T2: 25 MVA, 69/13.2 kV,x-0.220 pu Transmission line: j65 ohms/pha bus 2 BE 165Ω ISMVA e ratings of generator 1 as base valu 25MVA 13.8 kV 1 5% 69113.2 kV13kV 1 1% 13.2169k 1 1% 1- Draw the reactance diagram. 2- Find the Y-bus...
pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...
Please do exercise 129: Exercise 128: Define r:N + N by r(n) = next(next(n)). Let f:N → N be the unique function that satisfies f(0) = 2 and f(next(n)) =r(f(n)) for all n E N. 102 1. Prove that f(3) = 8. 2. Prove that 2 <f(n) for all n E N. Exercise 129: Define r and f as in Exercise 128. Assume that x + y. Define r' = {(x,y),(y,x)}. Let g:N + {x,y} be the unique function that...
3. For each reagent Q, R, W, X, Y, and Z in the list below, provide one correct function and the two correct reasons for your choice. .. Na O: S: Na Ho KI Na : Q RW > The options are: FUNCTIONS 1 - strong nucleophile + strong base; (choose one) 2 - strong nucleophile + weak base; 3 - weak nucleophile + strong base; 4 - weak nucleophile + weak base REASONS (choose two) A - conjugate acid...
3. Implement the following gates using only one TTLİCİ (1 point) TEL EL (a) Example: One 4-input OR gate (b) One 2-input NAND gate and one 2-input OR gate (c) One inverter, one 2-input NAND and one 3-input NAND (d) One 2-input XOR gate and one 2-input XNOR (e) One 4-input XNOR gate 2346 GND 2-input OR 7432 1 Porcuits Simplify the following expressions, and implement them with two-level NAND gate circuits: 4. Minterms, K-map and two-level NAND/NAND logic: F...