3. Repeat Example 7.8, using a 100 kVA transformer and #3/0 AWG and #2 AWG cables for the SLs and SDs, respectively Show the

TABLE 7.1 Single-Phase 7200-120/240-V Distribution Transformer Data at 65°C Core Loss (kW Copper Loss (kW) Excitation Current

Solution a. Assuming a diversity factor of 100%, the total load on the transfomer is S(3+2+8+ 6)+(5+6+7+ 4)+(6+7+8+10 -19+ 22

what information needed?

3. Repeat Example 7.8, using a 100 kVA transformer and #3/0 AWG and #2 AWG cables for the SLs and SDs, respectively Show the procedure to arrive at the following answers (a) 0.72 pu A (b) 0.050 pu V Example 7.8 residential secondary distribution system. Assume that the distribution trans- Figure 7.11 shows former capacity is 75 kVA (use Table 7.1), all secondaries and services are single-phase three wire, nominally 120/240 V, and all SLs are of #2/0 A1/Cu XLPE cable, and SDs are of #1/0 AI/Cu XLPE cable (use Table 7.2). All SDs are 100 ft long, and all SLs are 200 ft long. Assume an average lagging-load power factor of 0.9 and 100% load diversity factors and determine the following: a a. Find the total load on the transformer in kilovoltamperes and in per units. b. Find the total steady-state voltage drop in per units at the most remote and severe tomer's meter for the given annual maximum system loads. cus- 3 kVA 2 kVA 5 kVA 6 kVA 6 kVA 7KVA 100 ft SL SL 6 kVA 7 kVA 4 kVA 8 kVA 10 kVA 8kVA 200 ft 200 ft A residential secondary distribution system FIGURE 7.11
TABLE 7.1 Single-Phase 7200-120/240-V Distribution Transformer Data at 65°C Core Loss (kW Copper Loss (kW) Excitation Current (A) Rated (kVA, kW) R (pu)X(pu) 0.0130 15 0.083 0.194 0.0094 0.014 0.115 25 0.309 0.015 0.0123 0,0138 0.170 37.5 0.400 0.0107 0.0126 0.014 50 0.178 0.537 0.0107 0,0139 0.014 0.755 0.014 75 0.280 0.0101 0.0143 100 0.335 0.975 0.0098 0.0145 0.014 At rated voltage and frequency. At rated voltage and kilovoltampere load. TABLE 7.2 Twin Concentric Al/Cu XLPE 600 V Cable Data R (0/1000 ft) per Conductor Direct Burial Ka X (Q/1000 ft) per Phase Neutral Size Conductor 80°C Phase Conductor Ampacity (A) Conductor 90°C 90% PF 50% PF 2 AWG 0.334 0.56 0.0299 180 0,02613 0.01608 0.0305 1 AWG 0.265 0.419 205 0.02098 0.01324 1/0 AWG 0.210 0.337 0.0297 230 0,01683 0.01089 2/0 AWG 0,167 0.259 0,0290 265 0.01360 0.00905 3/0 AWG 0.132 0.211 0,0280 300 0,01092 0.00752 4/0 AWG 0.105 0.168 0.0275 340 0.00888 0.00636 250 kcmil 0.089 0.133 0.0280 370 0.00769 0.00573 0,0270 350 kcmil 0.063 0.085 445 0.00571 0,00458 0.044 500 kemil 0,066 0.0260 540 0,00424 0,00371 Per unit voltage drop per 104 A ft (amperes per conductor times feet of cable) based on 120 V line-to-neutral or 240 V -wire loading lne line. Valid for the two power factors shown and for perfectly balanced thre
Solution a. Assuming a diversity factor of 100%, the total load on the transfomer is S(3+2+8+ 6)+(5+6+7+ 4)+(6+7+8+10 -19+ 22+31 -72 kVA or, in per units S Sa 72kVA 75KVA 0.96puA b. To find the total voltage drop in per units at the most remote and severe customer's meter, calculate the per unit voltage drops in the transformer, the service line, and the SD of the most remote and severe customer. Therefore VD NR cnse+ X sin) 0,9610.0101x 0.90+0,0143x0.4359 =0.0147puV VDg-K 10t 129.17A 200 10 0.0136 0.03513puV IxI VDan K 10 41.67 Ax100ft 683 0.0168) 10 = 0.0070puV Therefore, the total voltage drop is VD- VD +Dy VDn 0.0147+0.03513+0.0070 -0.0568puV
0 0
Add a comment Improve this question Transcribed image text
Answer #1

kv A Ran TranformeooekVA 1-et the hver si aedor be (ao%. 1V <u D &L uo ppOl op ST 3 r tat 6J + 31617+45 + 66f748+) e0v4. 72KV

Add a comment
Know the answer?
Add Answer to:
what information needed? 3. Repeat Example 7.8, using a 100 kVA transformer and #3/0 AWG and...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio...

    A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...

  • 0% 0 pts) A 100 kVA. I 3 8 2.4 kV step down transformer has the...

    0% 0 pts) A 100 kVA. I 3 8 2.4 kV step down transformer has the following parameters (referred to the secondary): Rop-0.08 04m Tn the transformer is 100 ad KVA at 09 pf lagging at 2160 V. Find the voltage applied to the primary side of the transtormer Find the voltage regulation and efficiency 216D Q니 10.3-2400 1002 042to V(52 467 oo62 06 (10 pts) Solve the previous problem using the PU system. Use the rating of the transformer...

  • 3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8...

    3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of thr...

    please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...

  • A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited...

    A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...

  • Q No.1: A 14,000/130-V, three-phase, ∆-Y transformer bank consists of three identical 100-kVA, 83l4/130-V transformers. It...

    Q No.1: A 14,000/130-V, three-phase, ∆-Y transformer bank consists of three identical 100-kVA, 83l4/130-V transformers. It is supplied with power directly from a large constant voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Vsc = 510V,     Isc = 12.6 A,        Psc = 3000 W (a) If this bank delivers a rated load at 0.8 PF lagging and rated Voltage, what is the line-to-line voltage on the primary of the...

  • Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open-...

    Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.

  • A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the...

    A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the open, and short circuit tests, yielding the following results: OPEN CIRCUIT TEST SHORT CIRCUIT TEST Vsupply = 3.3 kV Vsupply = 650 V Io = 7.3 A Isc = 54.4A Po = 6.71 kW Psc = 8.89 kW Determine: 1.1 The no load current per phase, in RECTANGULAR form, referred to the H.V. side. (5) 1.2 How would you know, without being told, that...

  • 1- A 25-kVA, 3-phase, wye-connected, 400-V alternator has a synchronous reactance of 1.6 ohms per phase....

    1- A 25-kVA, 3-phase, wye-connected, 400-V alternator has a synchronous reactance of 1.6 ohms per phase. The alternator is to have zero voltage regulation at half-load. Neglecting the armature resistance, find the operating power factor and the developed power 2. A 500-kVA, 3600-V, 3-phase, 60-Hz alternator has an effective armature resistance per phase of 0.40 ohm Mechanical and iron losses is 10 kW, field current at full load unity power factor is 70 A. The exciter voltage is constant at...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT