what information needed?
what information needed? 3. Repeat Example 7.8, using a 100 kVA transformer and #3/0 AWG and...
A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...
0% 0 pts) A 100 kVA. I 3 8 2.4 kV step down transformer has the following parameters (referred to the secondary): Rop-0.08 04m Tn the transformer is 100 ad KVA at 09 pf lagging at 2160 V. Find the voltage applied to the primary side of the transtormer Find the voltage regulation and efficiency 216D Q니 10.3-2400 1002 042to V(52 467 oo62 06 (10 pts) Solve the previous problem using the PU system. Use the rating of the transformer...
3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...
Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...
please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...
A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...
Q No.1: A 14,000/130-V, three-phase, ∆-Y transformer bank consists of three identical 100-kVA, 83l4/130-V transformers. It is supplied with power directly from a large constant voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Vsc = 510V, Isc = 12.6 A, Psc = 3000 W (a) If this bank delivers a rated load at 0.8 PF lagging and rated Voltage, what is the line-to-line voltage on the primary of the...
Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.
A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the open, and short circuit tests, yielding the following results: OPEN CIRCUIT TEST SHORT CIRCUIT TEST Vsupply = 3.3 kV Vsupply = 650 V Io = 7.3 A Isc = 54.4A Po = 6.71 kW Psc = 8.89 kW Determine: 1.1 The no load current per phase, in RECTANGULAR form, referred to the H.V. side. (5) 1.2 How would you know, without being told, that...
1- A 25-kVA, 3-phase, wye-connected, 400-V alternator has a synchronous reactance of 1.6 ohms per phase. The alternator is to have zero voltage regulation at half-load. Neglecting the armature resistance, find the operating power factor and the developed power 2. A 500-kVA, 3600-V, 3-phase, 60-Hz alternator has an effective armature resistance per phase of 0.40 ohm Mechanical and iron losses is 10 kW, field current at full load unity power factor is 70 A. The exciter voltage is constant at...