Question

A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the...

A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the open,
and short circuit tests, yielding the following results:
OPEN CIRCUIT TEST SHORT CIRCUIT TEST
Vsupply = 3.3 kV Vsupply = 650 V
Io = 7.3 A Isc = 54.4A
Po = 6.71 kW Psc = 8.89 kW
Determine:
1.1 The no load current per phase, in RECTANGULAR form, referred to the H.V. side.
(5)
1.2 How would you know, without being told, that the short circuit test was probably supplied
on the H.V. side? Support your argument with calculations. (6)
1.3 Was the SCT carried out at rated full load currents? (Note: You must ALWAYS check
this, even if it is not asked!). (1)
1.4 The percentage impedance (or “Impedance Voltage”). (4)
1.5 The full load copper loss, and from this, the %R. (4)
1.6 The equivalent impedance per phase, referred to the l.v. side. (3)
1.7 The efficiency of this transformer under the following conditions:
1.7.1 Full load, at a power factor of 0.9 (2)
1.7.2 40% of full load, at a power factor of 0.75 (3)
1.7.3 The maximum efficiency at a power factor of 0.96 (3)
1.8 The full load terminal voltage on the l.v. side when the transformer load power factor is
0.8 lagging. (5)
1.9 Show how you would connect this transformer according to its designated vector group.
Use Figure 1 to help you. (

0 0
Add a comment Improve this question Transcribed image text
Request Professional Answer

Request Answer!

We need at least 10 more requests to produce the answer.

0 / 10 have requested this problem solution

The more requests, the faster the answer.

Request! (Login Required)


All students who have requested the answer will be notified once they are available.
Know the answer?
Add Answer to:
A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Similar Homework Help Questions
  • [29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If...

    [29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If the no load current and iron loss of this e transformer supplies a load of 10 ampere at a ampere and 12-watt respectively, calculate the total current supplied and the powe oad current and iron loss of this transformer are factor. (7) KVA, 50-Hz, 1200:230-volt single phase transformer has the following series impedance values: Z1 = (0.047 +0.112) Z2 = (0.00172 +0.00411)2 Calculate: 2.2.1...

  • Given a 31.5 MVA Single phase step down transformer.110 KV:11 KV The open circuit test values...

    Given a 31.5 MVA Single phase step down transformer.110 KV:11 KV The open circuit test values are Input voltage = 11 KV, P = 22.1 KW, I=5.85 A The short circuit test values are.Input voltage = 5.755 KV, P=163.935 KW, I= 286.36A If the transformer is run full load output with a power factor of 0.8 lagging 13.            Find I2 and V2     bold denotes phasor values 14.            Find the full load power P 15.            Find the voltage drop across the...

  • The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617...

    The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...

  • QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit...

    QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...

  • 3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8...

    3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...

  • A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit...

    A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit reactance of 5%. The open-circuit test performed on the low voltage side of the transfromer yielded the following data: VOC=13.8 kV, IOC=21.1 A, and POC=90.8 kW. (a) Find the equivalent circuit referred to the high voltage side of this transformer. (b) If the transformer is operating at full-load and at 0.8 pf lagging, find the voltage regulation of the transformer at this operating condition.

  • A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012...

    A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...

  • 4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a...

    4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a feeder with impedance of 100/60° Ω Load 90 kw 0.85 PF lagging Feeder transmission line) Source Transformer Load The transformer has been tested to determine its equivalent circuit. The results of the tests are: Open-circuit test Voc = 14 kV oc 0.1 A Рос-800 w Short-circuit test Vsc 800 V Isc = 7A Psc 2 kW The load on the transformer is 90 kW...

  • A three phase power transformer of 100 (KVA), 22 / 12.7 (kV) and Δ-Y has a...

    A three phase power transformer of 100 (KVA), 22 / 12.7 (kV) and Δ-Y has a resistance of 0.15 (pu) and a reactance of 0.6 (pu). The elements of the excitation branch are R_m = 100 (pu) and X_m = 20 (pu) a) If this transformer supplies a load of 80 (KVA) with an FP = 0.8 delay, draw the phasor diagram of one phase of the transformer. b) What is the voltage regulation of the transformer bank in these...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT