Question

Given a 31.5 MVA Single phase step down transformer.110 KV:11 KV The open circuit test values...

Given a 31.5 MVA Single phase step down transformer.110 KV:11 KV

The open circuit test values are Input voltage = 11 KV, P = 22.1 KW, I=5.85 A

The short circuit test values are.Input voltage = 5.755 KV, P=163.935 KW, I= 286.36A

If the transformer is run full load output with a power factor of 0.8 lagging

13.            Find I2 and V2     bold denotes phasor values

14.            Find the full load power P

15.            Find the voltage drop across the transformer

16.            Find the %Regulation of the transformer

17. Find the efficiency of the transformer

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
Given a 31.5 MVA Single phase step down transformer.110 KV:11 KV The open circuit test values...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit...

    A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit reactance of 5%. The open-circuit test performed on the low voltage side of the transfromer yielded the following data: VOC=13.8 kV, IOC=21.1 A, and POC=90.8 kW. (a) Find the equivalent circuit referred to the high voltage side of this transformer. (b) If the transformer is operating at full-load and at 0.8 pf lagging, find the voltage regulation of the transformer at this operating condition.

  • QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit...

    QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...

  • three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit...

    three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit parameters (referred to the primary winding where appropriate) : • primary resistance R1 = 0.03 ohms, secondary resistance R2’ = 0.04 ohms • primary leakage reactance X1 = 0.1 ohms, secondary leakage reactance X2’ = 0.1 ohms • magnetising reactance XM = 16 ohms, core-loss resistance RC = 200 ohms. In your calculations, you should use the simplified equivalent circuit. i) The transformer is...

  • single phase transformer with open circuit test and short circuit test

    A 20 kVA, 12,000/380 V, single-phase transformer has the following test results:open circuit (low voltage side): V = 380, I = 2, P = 250short circuit (high voltage side): V = 200, I = 2.5, P = 250a)Determine the approximate equivalent circuit parameters of the transformer in per-unit values.b) the transformer is working at 80% full load with 0.85 power factor lagging. what is the secondary current at this working condition in both actual and per-unit values. 

  • 2) A 50kVA, 2400/240V single phase transformer has the test measurements: (20) Open circuit test: 240V,...

    2) A 50kVA, 2400/240V single phase transformer has the test measurements: (20) Open circuit test: 240V, 5.0A, 450W (HV open) Short circuit test: 55V, 20.8A, 600W (LV short) a Caleulate the transformer equivalent circuit parameters and draw the transformer equivalent circuit. b) Find the voltage regulation and efficiency when the transformer is connected to a load that is 75% of the rated load current at 0.8 pf lagging. c) Find the voltage regulation and efficiency when the transformer is full...

  • A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the...

    A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the open, and short circuit tests, yielding the following results: OPEN CIRCUIT TEST SHORT CIRCUIT TEST Vsupply = 3.3 kV Vsupply = 650 V Io = 7.3 A Isc = 54.4A Po = 6.71 kW Psc = 8.89 kW Determine: 1.1 The no load current per phase, in RECTANGULAR form, referred to the H.V. side. (5) 1.2 How would you know, without being told, that...

  • 4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a...

    4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a feeder with impedance of 100/60° Ω Load 90 kw 0.85 PF lagging Feeder transmission line) Source Transformer Load The transformer has been tested to determine its equivalent circuit. The results of the tests are: Open-circuit test Voc = 14 kV oc 0.1 A Рос-800 w Short-circuit test Vsc 800 V Isc = 7A Psc 2 kW The load on the transformer is 90 kW...

  • can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has...

    can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has a full-load efficiency of 98% at 0.8 lagging power factor. The transformer core loss is 80 kW. The transformer supplies an industrial load that has a constant demand of 5000 kW at 0.65 lagging power factor. The cost of energy is $0.1 per kWh. 1. In the following questions, assume that the voltage at the load terminal is maintained constant at 22 kV. calculations....

  • A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012...

    A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...

  • Question 31 (17 points) 120/120 single-phase transformer. Calculate the values for the equivalent circuit for the single-phase transformer for the given short and open circuit test shown below. (2 po...

    Question 31 (17 points) 120/120 single-phase transformer. Calculate the values for the equivalent circuit for the single-phase transformer for the given short and open circuit test shown below. (2 points) Draw the equivalent circuit. (1 point each) Find Ssc, QSC, Soc, Qoc, R1, R2, XI, X2, Rc, Xm, PFsc, PFoc, (esc θ。c) phase angel between V and I. What is the power rating of this transformer? Short circuit test (performed at High Voltage side) Vsc 16.20V rms, Isc 5.00 A...