A 20 kVA, 12,000/380 V, single-phase transformer has the following test results:
open circuit (low voltage side): V = 380, I = 2, P = 250
short circuit (high voltage side): V = 200, I = 2.5, P = 250
a)Determine the approximate equivalent circuit parameters of the transformer in per-unit values.
b) the transformer is working at 80% full load with 0.85 power factor lagging. what is the secondary current at this working condition in both actual and per-unit values.
We need at least 9 more requests to produce the answer.
1 / 10 have requested this problem solution
The more requests, the faster the answer.
single phase transformer with open circuit test and short circuit test
can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...
A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...
The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...
A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load 120 KVA, 90KW (lagging power factor) at rated terminal voltage of 208V Determine a) b) c) The approximate equivalent circuit referred to the low-voltage side The primary voltage The transformer efficiency Please show the following: Circuit with the values given & found Equations used A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load...
please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...
lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. Determine the approximate equivalent circuit referred to the HV side. b. Find the voltage regulation at full-rated current delivering rated voltage and PF of 0.8 lagging. c. Calculate efficiency of transformer d. Assume that, voltage at HV side is 2000 V. Calculate the voltage at...
(a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters and explain how each parameter is determined based on the test results. (b) A 2200/220 V, 15 kVA, single phase transformer has the following equivalent circuit parameters: The HV winding resistance and leakage reactance are 0.2Ω and 0.3Ω respectively. The LV winding resistance and leakage reactance are 0.012Ω and 0.03 Ω respectively. The magnetic circuit resistance and reactance referred to the HV side are...
Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...
Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.
Question 31 (17 points) 120/120 single-phase transformer. Calculate the values for the equivalent circuit for the single-phase transformer for the given short and open circuit test shown below. (2 points) Draw the equivalent circuit. (1 point each) Find Ssc, QSC, Soc, Qoc, R1, R2, XI, X2, Rc, Xm, PFsc, PFoc, (esc θ。c) phase angel between V and I. What is the power rating of this transformer? Short circuit test (performed at High Voltage side) Vsc 16.20V rms, Isc 5.00 A...