Question

(a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters...

(a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters and explain how each parameter is determined based on the test results.

(b) A 2200/220 V, 15 kVA, single phase transformer has the following equivalent circuit parameters:

The HV winding resistance and leakage reactance are 0.2Ω and 0.3Ω respectively. The LV winding resistance and leakage reactance are 0.012Ω and 0.03 Ω respectively. The magnetic circuit resistance and reactance referred to the HV side are I.2 kΩ and I.8 kΩ respectively.

Determine the efficiency and voltage regulation, when the transformer is supplying rated load at rated voltage and at 0.9 power factor lagging.
0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
(a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit...

    three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit parameters (referred to the primary winding where appropriate) : • primary resistance R1 = 0.03 ohms, secondary resistance R2’ = 0.04 ohms • primary leakage reactance X1 = 0.1 ohms, secondary leakage reactance X2’ = 0.1 ohms • magnetising reactance XM = 16 ohms, core-loss resistance RC = 200 ohms. In your calculations, you should use the simplified equivalent circuit. i) The transformer is...

  • lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. De...

    lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. Determine the approximate equivalent circuit referred to the HV side. b. Find the voltage regulation at full-rated current delivering rated voltage and PF of 0.8 lagging. c. Calculate efficiency of transformer d. Assume that, voltage at HV side is 2000 V. Calculate the voltage at...

  • A single-phase 50-kVA, 2400/240-volt, 60-Hz distribution transformer has a 1-ohm equivalent leakage reactance and a 5000-ohm...

    A single-phase 50-kVA, 2400/240-volt, 60-Hz distribution transformer has a 1-ohm equivalent leakage reactance and a 5000-ohm magnetizing reactance referred to the high-voltage side. If rated voltage is applied to the high-voltage winding, calculate the open-circuit secondary voltage. Neglect 'R and G^V losses. Assume equal series leakage reactances for the primary and the referred secondary

  • 2) A 50kVA, 2400/240V single phase transformer has the test measurements: (20) Open circuit test: 240V,...

    2) A 50kVA, 2400/240V single phase transformer has the test measurements: (20) Open circuit test: 240V, 5.0A, 450W (HV open) Short circuit test: 55V, 20.8A, 600W (LV short) a Caleulate the transformer equivalent circuit parameters and draw the transformer equivalent circuit. b) Find the voltage regulation and efficiency when the transformer is connected to a load that is 75% of the rated load current at 0.8 pf lagging. c) Find the voltage regulation and efficiency when the transformer is full...

  • can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer...

    can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...

  • A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table...

    A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table below, a) For the rated load having a lagging power factor of 0.8, find the magnitude of the load current in Amperes. 15 Primary resistance 0.02 econdary resistance 120 Primary leakage reactance X2wL2 0.15 Secondary leakage reactance Xm=wLm Magnetizing reactance 30 k Re 200 k Core-loss resistance Answer: Check b) Find the phase of he load current in degrees (note: sign is important). Answer:...

  • Q1 A single-phase 11/2.2 kV, 22 kVA transformer has the following parameters all referred to the HV side RI 0.4, X 0...

    Q1 A single-phase 11/2.2 kV, 22 kVA transformer has the following parameters all referred to the HV side RI 0.4, X 0.602, R2 7.5 , X2 22 , Re 2500 , and Xm - 20002 The transformer is supplying 80% of its rated load at a power factor of 0.87 power factor lagging and at its rated voltage. Calculate (a) the efficiency of the transformer, (b) the power losses on the primary side (the copper loss and core loss), and...

  • JUST PART E VOLTAGE REGULATION PLEASE!! 2) The series impedance referred to the HV side of...

    JUST PART E VOLTAGE REGULATION PLEASE!! 2) The series impedance referred to the HV side of a 30 kVA, 8800/220 V distribution transformer is Zeq = 20 + j80 N. The components of the excitation branch referred to the HV side are Rc = 200 kN and XM = 20 kN. Suppose the transformer is supplying the load connected to the LV winding with the rated apparent power and the rated voltage (220 V) at a 0.8 lagging P.F. Use...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Please show full working Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and power efficiency...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Help me answer c and d Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and...