Question

can you calculate this question and explain why? thanks

1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Salutiong Camtileve Appodximate crrwit feed Suggested TEEE Side Voltage to Loco R0.052 R O05A Xjo18 Xzjo.16 roso : .72 kn 220Percentage voogeRegulatio E-V2 2230.49-- 2200 Reg 7. Volt foo 22 0 -22 6220-49) C2) Corre Loss Mnn-nig 209 Maxi-m efficiency3- Tamsfoomr Rating 3 x 4- Foams forre Rating 3 x 250k vA +50 kv A for Wewye Coeion Ratio Coit emair) Same Toams forme ie 1-

Add a comment
Know the answer?
Add Answer to:
can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20...

    A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load 120 KVA, 90KW (lagging power factor) at rated terminal voltage of 208V Determine a) b) c) The approximate equivalent circuit referred to the low-voltage side The primary voltage The transformer efficiency Please show the following: Circuit with the values given & found Equations used A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • 1) A single-phase 50-kVA, 2400/240 volt, 60 Hz distribution transformer is used as a step-down tr...

    1) A single-phase 50-kVA, 2400/240 volt, 60 Hz distribution transformer is used as a step-down transformer at the load end of a 2400-volt feeder whose series impedance is (1.0+2.0) Ω. The equivalent series impedance of the transformer is (10+j25) Ω referred to the high voltage (primary) side. The transformer is delivering rated load at 0.8 power factor lagging and at rated secondary volitage. Neglect the transformer exciting curent. Using the transtormer raltings as base quantities work this problem in per...

  • Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open-...

    Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.

  • single phase transformer with open circuit test and short circuit test

    A 20 kVA, 12,000/380 V, single-phase transformer has the following test results:open circuit (low voltage side): V = 380, I = 2, P = 250short circuit (high voltage side): V = 200, I = 2.5, P = 250a)Determine the approximate equivalent circuit parameters of the transformer in per-unit values.b) the transformer is working at 80% full load with 0.85 power factor lagging. what is the secondary current at this working condition in both actual and per-unit values. 

  • Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the...

    Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...

  • 3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2...

    3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2 and Xeais 0.0433 12. The transformer is operating in the step-down mode and is delivering rated current at rated voltage to a 0.840 power-factor lagging load. Determine (a) the no- load voltage; (b) the actual input voltage at the high side; (c) the high-side current; (d) the input impedance; (e) the voltage regulation; the voltage regulation if the power factor of the load is...

  • Could you please help with solving the following question. Note answers are attached below: please show...

    Could you please help with solving the following question. Note answers are attached below: please show how these answers were obtained: Q4. A single phase 50-Hz, 100 kVA, 11000/400 V-rms transformer is connected with the grid supply (Vi) as shown in Figure 3 15Ω j100 Ω j0.12 Ω 0.016 Ω Wll j50k 2 Load V240P 300k Ideal Transformer Figure 3 The load is connected on the secondary terminal to operate at 75% of its rated kVA at 0.8 lagging power...

  • The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617...

    The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...