Question

e. A three phase generator turning at 1500 rpm has a terminal voltage of 15 kV, 50 Hz. If the synchronous reactance is 5 per

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Sol Given data Termenal voltage Vt=15KV f=50143 ! Resistive Lood 12mW. I j5 Eg Load 13 I Vit Cosp=P P.f. criting for ResistivOMALIA 1SX103 + (461-9190/15) 6.35kv Ege EJ = 13x6.35X/03 = 11kV D In Each Cose Generator Induced voltage is different for al1) Capacitive Load of 0-8 Pf [leading) Ef 13686 IS jIXS b) In. ( cose magnitude of terminal voltage less than Generated volt

Add a comment
Know the answer?
Add Answer to:
e. A three phase generator turning at 1500 rpm has a terminal voltage of 15 kV,...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature...

    A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter

  • A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of...

    A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of 12 2 and negligible stator resistance. a. The generator is connected to an infinite bus and delivers 80 MW at 0.8 leading power factor. Determine the power angle and excitation voltage EA. Draw the phasor diagram. b. The field current of the generator is now slowly reduced until the generator reaches its static stability limit (5=0). For this condition, determine the power angle, excitation...

  • A 36 MVA, 20.8 kV, 3-phase alternator has a synchronous reactance of 9 Q and a...

    A 36 MVA, 20.8 kV, 3-phase alternator has a synchronous reactance of 9 Q and a nominal current of 1 kA. The no-load saturation curve giving the relationship between Eo and I, is given in Fig. 13b. If the excitation is adjusted so that the terminal voltage remains fixed at 12 kV, calculate the exciting current required and draw the phasor diagram for the following conditions: No-load а. b. Resistive load or 36 MW Capacitive load of 12 Mvar C....

  • Discussion: Determine the synchronous reactance by neglecting the armature resistance ? How does the phase voltage...

    Discussion: Determine the synchronous reactance by neglecting the armature resistance ? How does the phase voltage behave in case of ohms load, inductive load and capacitive load of synchronous generator? How can be control the terminal voltage to the rated voltage of synchronous generator?

  • Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a...

    Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...

  • A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a...

    A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...

  • Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and...

    Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and armature resistance, Ra-005Ω. The terminal voltage in all working conditions is assumed constant and equal to the rated voltage. The generator is delivering a load current of 2000A at 0.8 PF leading a. Draw the per-phase equivalent circuit of the generator. b. Calculate the induced EMF, EA. c. Calculate the real and reactive power delivered at the generator terminals. d. Sketch the phasor diagram...

  • Question 5 (Svnchronous machines) a. A synchronous generator connected to an infinite grid has its frequency and terminal b. A six-pole, Y-connected three-phase synchronous machine rated 208 V (line-...

    Question 5 (Svnchronous machines) a. A synchronous generator connected to an infinite grid has its frequency and terminal b. A six-pole, Y-connected three-phase synchronous machine rated 208 V (line-to- voltage fixed. What is the effect of increasing the excitation current in this case? line), 5500 VA has a synchronous reactance of 8 2 per phase at rated terminal voltage. It is operating as a generator connected to an infinite grid Determine the excitation voltage and the power angle if the...

  • Please show all the clearly step A 500 MVA, 24 kV, 60 Hz three-phase synchronous generator...

    Please show all the clearly step A 500 MVA, 24 kV, 60 Hz three-phase synchronous generator is operating at rated voltage and frequency with a terminal power factor of 0.8 lagging. The synchronous reactance X 0.8. Stator coil resistance is negligible. The internally generated voltage E,-18 kv a) Draw the per phase equivalent circuit. b) Determine the torque (power) angle 5, c) the total output power, d) the line current.

  • A 100MVA synchronous generator is connected to a 25kV infinite bus through two parallel transmission lines....

    A 100MVA synchronous generator is connected to a 25kV infinite bus through two parallel transmission lines. The synchronous reactance of the generator is 2.5Ω. Each transmission line has inductive reactance of 2Ω and 0.2Ω resistance. The generator delivers 90MVA to the infinite bus at 0.8 power factor lagging.    For the above conditions, calculate: a. The terminal voltage of the generator      b. The equivalent field voltage and power angle      c. The real power output at the generator terminals    d. The reactive...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT