3. (45) Operating data for an air-conditioning process is shown below. Air flows through a soaked...
Moist air at 24°C, 1 atm, and 35% relative humidity enters an evaporative cooling unit operating at steady state consisting of a heating section followed by a soaked pad evaporative cooler operating adiabatically. The air passing through the heating section is heated to 45°C. Next, the air passes through a soaked pad exiting with 50% relative humidity. Using data from the psychrometric chart, determine: (a) the humidity ratio of the entering moist air mixture, in kg(vapor) per kg(dry air). (b)...
Moist air at 30°C, 1 atm, and 42% relative humidity enters an evaporative cooling unit operating at steady state consisting of a heating section followed by a soaked pad evaporative cooler operating adiabatically. The air passing through the heating section is heated to 45°C. Next, the air passes through a soaked pad exiting with 50% relative humidity. A. Determine the specific humidity of the entering moist air (to the heating section). (5 of 45 points. Please input your final answer...
Atmospheric air at 32°C and 70% relative humidity passes through a cooling section in an air-conditioning duct where the air is cooled below its dew point and some of the water is removed. The air then passes over a heating section where heat is added until the final temperature is 22°C and the relative humidity is 45%. Assume the process occurs at constant pressure of 1 atm. Using the psychrometric chart, determine: (a) The amount of water removed in the...
Please DO NOT use the psychrometric chart to solve the following: An air-conditioning system operates at a total pressure of 95kPa and consists of a heating section and a humidifier that supplies wet steam (saturated water vapor) at 100°C. Air enters the heating section at 10°C and 70 percent relative humidity at a rate of 35 m3/min, and it leaves the humidifying section at 20°C and 60 percent relative humidity. Determine (a) the temperature and relative humidity of air when...
QUESTION 1 [15 marks] Due: 5 August 2020 An air conditioner operating at steady state takes in moist air at 28°C, 1 atm and 70% relative humidity. The moist air first passes over a cooling coil in the dehumidifier unit and some water vapor is condensed. The rate of heat transfer between the moist air and the cooling coil is 38.69 kW. Both saturated moist air and condensate streams exit the dehumidifier unit at the same temperature. The moist air...
Problem 4- A HVAC system is operating in heating mode with a steam humidification system, as shown below. Air enters the system at 10°C and 70% relative humidity at a rate of 35m3/min. After heating and subsequent humidification by saturated water vapor at 100°C, the air leaves the system at 20°C and 60% relative humidity. Find (1) the temperature and relative humidity of the air when it leaves the heating section, (2) the heat transferred to the air in the...
a. Calculate the dry air and water vapor mass flow rates (lb/min) if the volume flow rate is 1,000 cfm, the humidity ratio is 0.025 lbv/lba, and the dry air density is 0.072 Iba/ft3. b. Assume the above air enters an evaporator coil at 90°F where it is cooled in a constant humidity ratio process until reaching the 100 % RH curve ( the temperature at that point is the dew point. The air then keeps dropping in temperature, following...
Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 895 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. a)Determine the mass flow rate of the dry air in lb(dry air)/min....
4. Air-Conditioning Unit [20 Marks] 1 m3/s of moist air at 32 °C with a relative humidity of 70% is to be treated by a simple air condition system to produce air at 18 °C with a relative humidity of 50% The system will have two stages. In the first stage, the air will pass over cooling coils to dehumidify it, and in the second stage it will be heated electrically to the specified outlet conditions You may ignore the...
Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in lbm(dry...