1. A building air-condition unit is designed to cool 2500 ft3/min of outside air (95°F, 740 mmHG, 82% relative humidity) to 50°F, thereby condensing a portion of the water vapor. The system then heats the air and sends it to a building at 68°F
a) Calculate the rate of water condensation.
b) Calculate the volumetric flow rate of air delivered to the building.
Basis: 1 min of operation
2500 ft3 of air at 95 o F ( 308 K) 740 mm Hg contains = 1*(273/308)*(740/760)*(2500/359)= 6.01 lb moles
( we know at std conditions - 1 lb mole of gas at 273 K, 760 mm Hg occupy 359 ft3 )
Total moles entering the unit = n=6.01 lb moles
Relative humidity= partial pressure of water/vapor pressure of water at95 oF= 0.82
Vapor pressure at 95 oF =41.526 mm Hg
Therefore partial pressure of water vapor in the inlet air= 0.82* 41.526=34.05 mm Hg
Mole of water vapor = na = Partial pressure/total pressure =34.05/740=0.046 lb moles
Moles of dry air = n-na= 6.01-0.046=5.550 lb mole
Since the moles of dry air do not change during the process, can be considered as tie substance.
Partial pressure of water vapor leaving the unit = vapor pressure of water at 50 oF )since it is condensing) = 8.899 mm Hg
Moles of water vapor leaving the unit = Partial pressure/total pressure =8.899/740=0.012 lb mole
a) water vapor condensed = lb moles =0.046-0.012 =0.034 lb moles=0.612 lb per minute
b) Total moles leaving the unit= 5.55 + 0.012= 5.67 lb moles.
These moles leave the building after heating to 68 oF (293 K) ,740 mm Hg and therefore
The volumetric flow rate of gases at these conditions is = (5.67/1)*(293/273)*(760/740)*359= 2243 ft3 per minute
1. A building air-condition unit is designed to cool 2500 ft3/min of outside air (95°F, 740...
Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 895 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. a)Determine the mass flow rate of the dry air in lb(dry air)/min....
Problem2 (a) Suppose outside temperature is 55 °F while the temperature inside a building is 72 F. The building is heated but not air conditioned, so the partial pressure of water vapor is the same both inside and outside the building. Finally, suppose the dew point outside is 40°F What is the dew point inside? What are the relative humidities inside and outside the building? (We are most comfortable if relative humidity is between 30% and 50%-This question shows why...
a. Calculate the dry air and water vapor mass flow rates (lb/min) if the volume flow rate is 1,000 cfm, the humidity ratio is 0.025 lbv/lba, and the dry air density is 0.072 Iba/ft3. b. Assume the above air enters an evaporator coil at 90°F where it is cooled in a constant humidity ratio process until reaching the 100 % RH curve ( the temperature at that point is the dew point. The air then keeps dropping in temperature, following...
Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in lbm(dry...
Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in Ibm(dry...
A manufacturing building is being ventilated to maintain air temperature, air moisture levels and air quality. The following is known about the situation: • The desired inside conditions are 68°F db with a maximum of 60% RH. • The average outside conditions are 42°F db and 35°F wb. • The building has an overall heat loss factor of 454 BTU/(h·ºF) with a total volume of 76,000 ft3. • Inside the building, people and equipment generate sensible heat at a rate...
Q.3 Outside air at 90°F, 1 atm, and 95% relative humidity with a flow rate of 4000 cfm is blown over an evaporator of a refrigeration system and exits at 75°F and 60% relative humidity. The refrigeration system has operating with the COP of 2.5. Determine (a) the amount of cooling provided by the evaporator Btu/hr (b) the amount of water condensed in the evaporator, lbm/hr and (c) the power required by the compressor of the refrigerator in kW. 1...