Answer for the Question-2(i)
Rating of transformer = 60KVA = 60000VA
From the open circuit test, we get constant losses = Wi = 430 Watts
From the short circuit test, we get full load copper loss = Wc = 525 Watts
If we assume x is the ratio of the amount of load connected to the rated load and pf is the power factor,
The efficiency of the transformer is given as,
(i)-(a) x = 1 and pf = 0.7
(i)-(b) x = 0.5 and pf = 0.7
Answer for the Question-2(ii)
Given,
Primary Voltage = V1 = 240 V
Secondary Voltage = V2 =12 V
Power at Secondary side = P2 = 150 W
(ii)-(a)
Turns Ratio = V1 / V2 = 240 / 12 = 20
(ii)-(b)
Secondary Current = I2 = P2 / V2 = 150 / 12 = 12.5 Amps
Primary Current = I2 / Turns Ratio = 12.5 / 20 = 0.625 Amps
Answer for the Question-4
Given data,
Load Power = PL = 22000 Watts
Since it is a Shunt generator, Terminal Voltage at field = Terminal Voltage at Load = VL = 220 V
Efficiency = n = 0.88
Shunt field resistance = Rsh = 110 Ohms
Armature resistance = Ra = 0.05 Ohms
Load current = IL = PL / VL = 22000 / 220 = 100 Amps
Shunt field Current = If = VL / Rsh = 220 / 110 = 2 Amps
Armature Current = Ia = IL - If = 100 - 2 = 98 Amps
(a)-answer
Shunt field copper loss = If2 * Rsh = 22 * 110 = 4 * 110 = 440 Watts
Armature copper loss = Ia2 * Ra = 982 * 0.05 = 480.2 Watts
Total Copper Loss = 440 + 480.2 = 920.2 Watts
(b)-answer
Efficiency = n = ( Load Power ) / (Load Power + Total Losses)
0.88 = ( 22000 ) / (22000+ Total Losses)
22000+ Total Losses = ( 22000 ) / 0.88
Total Losses = 25000 - 22000
Total Losses = 3000 Watts
Iron and Friction Loss = Total Losses - Total Copper Loss = 3000 - 920.2 = 2079.8 Watts
Q2.) A 60KVA, Single phase 3300/400 V transformer gave the following test results. Table 2.1 Open...
A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...
Electric Machinery
Problem 2: [50 points] A 15-KVA, 230/2300-V transformer is considered. The following test data have been taken: | OC Test (on Primary) Voc = 230 V loc = 2.8 A Poc = 100 W SC Test (on Secondary) Vsc = 47 V Isc = 9.5 A Psc = 350 W (a) Find the equivalent circuit of this transformer referred to the high- voltage side. [10 points] (b) Find the equivalent circuit of this transformer referred to the low-...
Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...
Q1 A single-phase 11/2.2 kV, 22 kVA transformer has the following parameters all referred to the HV side RI 0.4, X 0.602, R2 7.5 , X2 22 , Re 2500 , and Xm - 20002 The transformer is supplying 80% of its rated load at a power factor of 0.87 power factor lagging and at its rated voltage. Calculate (a) the efficiency of the transformer, (b) the power losses on the primary side (the copper loss and core loss), and...
Given a 31.5 MVA Single phase step down transformer.110 KV:11 KV The open circuit test values are Input voltage = 11 KV, P = 22.1 KW, I=5.85 A The short circuit test values are.Input voltage = 5.755 KV, P=163.935 KW, I= 286.36A If the transformer is run full load output with a power factor of 0.8 lagging 13. Find I2 and V2 bold denotes phasor values 14. Find the full load power P 15. Find the voltage drop across the...
A single-phase transformer rated 1.2kV/120V, 7.2kVA yields the following results: Open circuit test (performed on secondary side): V2=120V I2=1.2A W2=40W Short circuit test (performed on primary side): V1=20V I1=6A W1=36W Determine: i. ii. iii. The equivalent circuit referred to primary side The equivalent circuit referred to secondary side Efficiency of transformer when it delivers 6kVA at 120V and 0.9pf
Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.
lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. Determine the approximate equivalent circuit referred to the HV side. b. Find the voltage regulation at full-rated current delivering rated voltage and PF of 0.8 lagging. c. Calculate efficiency of transformer d. Assume that, voltage at HV side is 2000 V. Calculate the voltage at...