Exercise 3.3: Refrigerant R 134a leaves the compressor at 1.2 Mpa, 80°C and enters the condenser...
A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at by The refrigerant enters the condenser at compressor consumes 3.3 kW of power, determine (a) the mass flow rate of the refrigerant, (b) the refrigeration load, (e) the COP, and (d) the g waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. 1.2 MPa and 50°C and leaves at the same...
1. Refrigerant 134a enters the compressor of a refrigerator as superheated vapor at 0.20 MPa and -10 °C at a rate of 0.07 kg/s, and it leaves at 1.2 MPa and 70 °C. The refrigerant is cooled in the condenser to 44 °C and 1.130 MPa and it is throttled to 0.20 MPa. Disregarding heat transfer and pressure drop in the connecting lines between the components, show the cycle on a T-s diagram with respect to the saturation line. Determine...
Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C at a rate of 0.025 kg/s and leaves at 1000 kPa as saturated liquid. If the compressor consumes 2 kW of power, determine: a) The COP of the heat pump (as heating device). b) The rate of heat absorption from the outside air. тан Condenser Throttling valve Compressor Evaporator To
Refrigerant-134a enters the compressor of a refrigerator as superheated vapor at 0.14 MPa and -10°C at a rate of 0.124 kg/s, and it leaves at 0.7 MPa and 50°C. The refrigerant is cooled in the condenser to 24°C and 0.65 MPa, and it is throttled to 0.15 MPa. Disregarding any heat transfer and pressure drops in the connecting lines between the components, determine (a) the rate of heat removal from the refrigerated space and the power input to the compressor...
Refrigerant-134a enters the condenser of a residential heat pump at 800 kPa and 35°C at a rate of 0.018 kg/s and leaves at 800 kPa as a saturated liquid. If the compressor consumes 1.2 kW of power, determine (a) the COP of the heat pump and (b) the rate of heat absorption from the outside air.
Problem #2 Refrigerant 134a enters an adiabatic compressor at 0.1 MPa and -20 oC while it leaves at 1 MPa and 110 oC. The mass flow rate of the compressor is 0.3 kg/s. Determine: a) The power input to the compressor, in kW. b) The volume flow rate of the refrigerant at the compressor inlet.
A vapor compression refrigeration cycle utilizes R-134a as the working fluid. The refrigerant flow rate is 50 g/s. Vapor at 150 kPa and -10 0C enters the compressor and leaves at 1.2 MPa and 75 0C. The power input to the non-adiabatic compressor is measured and found to be 2.4 kW. The refrigerant enters the expansion valve at 1.15 MPa and 40 0C and leaves the evaporator at 160 kPa and -15 0C. Determine the entropy generation in the compression...
6-17 Refrigerant-134a enters the compressor of a refrig- cration system as saturated vapor at 0.14 MPa and leaves as superheated vapor at 0.8 MPa and 60°C at a rate of 0.06 kg/s. Determine the rates of energy transfers by mass into and out of the compressor. Assume the kinetic and potential cncrgics to be negligible.
A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at −25°C by rejecting waste heat to cooling water that enters the condenser at 20°C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 50°C and leaves at the same pressure subcooled by 5°C. If the compressor consumes 3.3 kW of power, determine (a) the mass flow rate of the refrigerant, (b) the refrigeration...
1 MPa Isentropic Efficiency of a Compressor Refrigerant-134a enters an adiabatic compressor as a saturated vapor at 100kPa at a rate of 0.7 m/min and exits at 1-MPa pressure. The isentropic efficiency of the compressor is 87%. R-134a Compressor Isentropic Compressor Work hs-h 100 kPa sat. vapor Actual Compressor Work Determine the refrigerant properties at the inlet and outlet for an isentropic process. Actual 2s entropic procEss Inlet state Determine the actual isentropic enthalpy from the efficiency. (Ans: 289.71 J/kg)...