Question

A service switchboard is installed in an electrical equipment room to supply a commercial building. The...

A service switchboard is installed in an electrical equipment room to supply a commercial building. The top of the switchboard is 7' above the finished floor. Determine the minimum dedicated electrical space above the switchboard per Article 408 of the NEC.
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Clearance must be 3 feet above switch board.

Here I will write statement of article 408 from National Electrical code 2017

408.18 Clearances.
(A) From Ceiling. For other than a totally enclosed switch‐
board or switchgear, a space not less than 900 mm (3 ft) shall
be provided between the top of the switchboard or switchgear
and any combustible ceiling, unless a noncombustible shield is
provided between the switchboard or switchgear and the ceil‐
ing.

So, according to article 408.18 clearances mustbe 3 feet.

Add a comment
Know the answer?
Add Answer to:
A service switchboard is installed in an electrical equipment room to supply a commercial building. The...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A building takes a three-phase supply at 400 V with a declared prospective short circuit current of 30 kA at the intake switchboard. The cable installed between the intake switchboard and a remot...

    A building takes a three-phase supply at 400 V with a declared prospective short circuit current of 30 kA at the intake switchboard. The cable installed between the intake switchboard and a remote distribution board has a circuit length of 100 m. The cable is PVC-insulated and has the following characteristics at 20 °C: 12.4 Phase conductor resistance 0.095 ma/m Phase conductor reactance 0.075 mO/m Conductor temperature coefficient of resistance 0.004 per c Connected to the remote distribution board is...

  • (1). In regard to installation of electrical conductions and equipment, who may grant exceptions to the...

    (1). In regard to installation of electrical conductions and equipment, who may grant exceptions to the requirements of the NEC? A. nfpa b. ahj c. ieee d. ul. (2). Exceptions to the Code permit alternate methods to the general (main) rule. Exceptions are permitted. A. when all of the provisions of the exception are met. B. when a written request is submitted to and approved by the NEC. C. any time the electrician deems it necessary. D. not more than...

  • O AWG copper conductor without any markings to indicate the The terminal for dh s terminal is assumed to have a min...

    O AWG copper conductor without any markings to indicate the The terminal for dh s terminal is assumed to have a minimum terminal temperature rating E. 90°C. 60°C. of: C, D. 75 C. B. 40-С. Code reference re rated branch-circuit supplies fluorescent luminaires (lighting fixtures) with a peres. All terminations are 75°C rated, there are only three current- THHW as shown in Figure 1.43 pe 10. A 20-am carrying conductors in EMT, and the conductor insulation is The minimum size...

  • pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC...

    pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...

  • The amount of available fault current at the service depends upon the ______. Method of banding...

    The amount of available fault current at the service depends upon the ______. Method of banding Method of grounding Size and impendence of the service transformer Ampere rating of the overcurrent protection device The line current for a 240/120 volt, 3-phrase system, if each phase is balanced with a 3,000-VA load and the total load is 9,000 VA, is ______ amperes. 12.5 15 21.65 37.5 Given: A dwelling unit has 3,000 sq.ft. of habitable space with laundry facilities and bathrooms,...

  • Can you please show or elaborate how you got your answers. Thank you #2-10 board on...

    Can you please show or elaborate how you got your answers. Thank you #2-10 board on Bl Refer to the plot plan for Highland Office Supply to answer queslD Local ordinances require the following for commercial office buildings: Porking-hwo 200 sq t parking spaces per 1000 sq ft of office space Green space-10% minimum of total lot size Maximum building size-40% of total lot size Selbock-400-from front street curb; 250" on each side; 200" on back ETER STREET NORTH FL...

  • Answer all 13. On e of your equipment operators tests positive for a controlled dangerous substance....

    Answer all 13. On e of your equipment operators tests positive for a controlled dangerous substance. Do you (algive him an oral warning (b) give him an oral warning (c) issue a minor discipline (d) terminate him (e) none of the above. 14. Public bids have been received. In reviewing the bids, you discover that the low bidder's numbers don't add up correctly. Do you (a) let him fix the number (b) correct the number and award the contract to...

  • Answer all please e of your equipment operators tests positive for a controlled dangerous substance. Do...

    Answer all please e of your equipment operators tests positive for a controlled dangerous substance. Do you (algive him an oral warning (b) give him an oral warning (c) issue a minor discipline (d) terminate him (e) none of the above. 13. On 14. Public bids have been received. In reviewing the bids, you discover that the low bidder's numbers don't add up correctly. Do you (a) let him fix the number (b) correct the number and award the contract...

  • can you please answer question 1 and 3 please ABC General Contractors ABC General Contractors was...

    can you please answer question 1 and 3 please ABC General Contractors ABC General Contractors was an established construction company handling small-to medium- sized commercial and industrial construction projects. Some recent projects that the company had completed were a 20,000-square-foot factory building, a four-story office building, and a water filtration plant. TELEVISION TOWER BID The company was now in the process of preparing a bid for a television station for the erection of a 225-foot-high television antenna tower and the...

  • Class: Week 7 10. Where multiple power supplies serve the same de system, the dc side...

    Class: Week 7 10. Where multiple power supplies serve the same de system, the dc side of each power su supply shall have a a. disconnecting means b. suitable ground c. removable conductor d. removable fuses 11. Generator accessories,including but not limited to, te electrically operated louver, ath altemate power accessories essential for generator operation, shall be arranged for automatic connection to source. a. transfer fuel pump c. environmental controls b. transfer circuit d. auviliary switching 12. Minimum ampacity of...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT