Question

use (absolute volume method). Calculate the materials (type II cement, coarse aggregate, fine aggregate, and water)...

use (absolute volume method). Calculate the materials (type II cement, coarse aggregate, fine aggregate, and water) needed to make 16 concrete cylinders (diameter = 4", height = 8") for our compression tests. Specified compressive strength = 3000 psi at 28 days.

For coarse aggregate, please choose 3/4 in max size gravel containing some crushed particles with the following assumptions: oven-dry specific gravity of 2.68; oven-dry rodded unit weight: 100 lb per cu. ft; moisture content: 1%.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Ans) We know,

For ordinary concrete, slump required = 2-4 in

First lets calculate the mix design for 1 cy (27 ft3), then we can calculate any required amount .

   According to ACI Table 6.3.3 , for slump of 4 in and 3/4 in maximum aggregate size, amount of water required is 340 lb/cy

For 3000 psi , according to Table 6.3.4(a) , water cement ratio = 0.68

Amount of cement = Amount of water/ w/c ratio = 340/0.68= 500 lb/cy

Now, according to table 6.3.6 , for 3/4 in aggregate size and 2.6 fineness modulus , volume of coarse aggregate = 0.64

Amount of coarse aggregate = oven dry weight x volume = 100 x 0.64 x 27 = 1728 lb /cy3

According to absolute volume method, volume of fine aggregate = Total volume - Volume of water , cement and coarse aggregate

Volume of materials = Weight / (Specific gravity x Unit weight)

=> Volume of fine aggregate = 27 - [ (340/62.4) + (500/3.15 x 62.4) + (1728 / 2.68 x 62.4)]

=> Volume of fine aggregate = 27 - 18.32 = 8.68 ft3

=> Amount of fine aggregate = Density x Volume = 2.68 x 62.4 x 8.68 = 1451.7 lb

Since, coarse aggregate contains moisture it will provide some water to concrete so amount of water is needed to be corrected

Amount of water provided by coarse aggregate = 0.01 x 1728 = 17.28 lb

=> Correct amount of water needed = 340 - 17.28 = 322.72 lb

Total volume = Number of cylinder x Volume of one cylinder

Volume of one cylinder, V = (/4) D2 H

=> V = (/4)(4)2 (8) = 100.48 in3 or 0.05814 ft3

Hence, volume of 16 cylinders = 16 x 0.05814 = 0.93 ft3

Following table consist of required batch weights of components :

Component Amount per cy (lb) Amount for 0.93 ft3 (lb)
Cement 500 465
Water 322.72 300.13
Coarse aggregate 1728 1607
Fine aggregate 1451.7 1350

    

Add a comment
Know the answer?
Add Answer to:
use (absolute volume method). Calculate the materials (type II cement, coarse aggregate, fine aggregate, and water)...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Design the concrete mix according to the following conditions: Design Environment Pavement slab, Bozeman, Montana (cold...

    Design the concrete mix according to the following conditions: Design Environment Pavement slab, Bozeman, Montana (cold climate) Required design strength = 3000 psi Slab thickness = 12 in. Statistical data indicate a standard deviation of compressive strength of 250 psi is expected (more than 30 samples). Only air entrainer is allowed. Available Materials Air entrainer: Manufacture specification is 0.15 fl oz/1% air/100 lb cement. Coarse aggregate: 2 in. nominal maximum size, crushed stone Bulk oven-dry specific gravity = 2.573, absorption...

  • Please show which equations you use and describe in detail. 21. concrete mix design, Design the...

    Please show which equations you use and describe in detail. 21. concrete mix design, Design the concrete mix according to the following conditions: Design Environment Unreinforced slab, Bozeman, Montana (cold climate) Required design strength = 3500 psi Slab thickness = 12 in Statistical data indicate a standard deviation of compressive strength of 250 psi is expected (more than 30 samples). Only air entrainer is allowed Available materials Air entrainer: manufacture specification is 0.15 fl oz/1%/100 lb cement Coarse aggregate: 2...

  • Problem with different moisture conditions: 5. Calculate the quantities of cement, water, fine ag...

    Problem with different moisture conditions: 5. Calculate the quantities of cement, water, fine aggregate, and coarse aggregate per trial mix of 1 m3 for the following specifications. Target mean compressive strength-30 MPa at 7 days; Cement strength class 42.5; Slump required 100 mm; Max. Aggregate size 20 mm; specific gravity of aggregates 2.65% Coarse aggregate UNCRUSHED (10, 20mm), fine aggregate CRUSHED (50% pass 600 micros); Maximum allowable free- water/cement ratio 0.40; Minimum allowable cement content 275 kg/m3; Absorption of fine...

  • Hi, can you help me do this problem, i know its a little bit long but...

    Hi, can you help me do this problem, i know its a little bit long but i really need to know how to answer it and know the answer thank you Problem 2 Concrete Mix Design. (30 points) You are planning to place concrete for a roof slab in a 3 story light commercial building located in Boston, MA (cold climate). Develop the mix proportion for this concrete. Explain your selections. Design Criteria: 290 Design strength-3.700 psi Statistical data based...

  • Question 1. A concrete mix is to be designed for use in a 250 mm thick road pavement. The desired properties are pr...

    Question 1. A concrete mix is to be designed for use in a 250 mm thick road pavement. The desired properties are provided below. Use the ACI method to calculate the required amounts per unit volume (/1m) of water, cement, course aggregate and fine aggregate. Slump 25 mm Average 28-day flexural strength of at least 4.5 MPa Coarse aggregate: nominal maximum size = 37.5 mm, dry-rodded weight 1600 kg/m3, specific gravity 2.68, moisture content 1.0 percent, absorption 0.5 percent Fine...

  • Compute the SSD mix proportions for the following mix design using the ACI method: Compressive Strength:...

    Compute the SSD mix proportions for the following mix design using the ACI method: Compressive Strength: 3,000 psi Slump: 4 inches Non-Air Entrained Concrete The materials have the following properties: | Cement: Type I, specific gravity = 3.15 | Fine Aggregate: Bulk specific gravity = 2.68; fineness modulus = 2.40 Coarse Aggregate: Maximum size aggregate = 1 inch; bulk specific gravity = 2.68; Dry-rodded unit weight = 100 lbs/ft3

  • Concrete is required for an interior building column in Burlington, VT. A specified compressive streng of...

    Concrete is required for an interior building column in Burlington, VT. A specified compressive streng of 4,000 psi is required at 28 days. Information regarding reinforcing steel spacing and sizing willb provided in class. You have contacted the local concrete batch plant and found that they have th following materials ready Coarse Aggregates: 1 inch Nominal Maximum Size; Bulk Specific Gravity (oven-dry) 2.66; Dry- Fine Aggregates: Sand-Bulk Specific Gravity (oven-dry) = 2.64; Fineness Modulus (FM.)s 2.55; Rodded Unit Weight-102.3 lb/ft:...

  • The following requirements are specified for concrete construction of a reinforced concrete jetty exposed to sea...

    The following requirements are specified for concrete construction of a reinforced concrete jetty exposed to sea water and moderate freeze and thaw environment Required Design Strength, fc Slump required Standard deviation Cement 35 MPa 25-75 mnm 4.8 MPa Ordinary portland cement with relative density 3.15 Fine Aggregate (Natural Sand) Oven-dry relative densitv SSD moisture content Moisture content of sample Fineness Modulus 2.3 0.2 % 4.3 % 2.63 Coarse aggregate (crushed stone) Nominal maximum aggregate size Oven-dry relative density SSD moisture...

  • What would be the maximum aggregate size used for the given mixture properties by using ACI...

    What would be the maximum aggregate size used for the given mixture properties by using ACI Method of Mix Design. 28-day specified concrete strength is 3b Mpa, standard deviation is choosen as 3.a Mpa and it is required that no more than 1 test result in 200 will fall below the specified strength. Project Title: Detoration of wood column of a commercial building Project summary: Wood deterioration at the lower level of a heavy timber column, which supports five floor...

  • 2. Determine the following parameters for both the coarse and fine aggregate samples (separately) based on...

    2. Determine the following parameters for both the coarse and fine aggregate samples (separately) based on the data provided in the following table: (a) (b) absorption capacity moisture content apparent specific gravity bulk specific gravity (oven dry) bulk specific gravity (SSD) Aggregate Wop (g) Wsub (g) Wpye+wi (g) Wpyetagg-w2 (g) WStock (g) 5302 CA Wssp (g) 5226 501 5220 496 3294 I FA 515 622 938

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT