Question

21. concrete mix design, Design the concrete mix according to the following conditions: Design Environment Unreinforced slab,Please show which equations you use and describe in detail.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Answer:-

Given

Let the total volume of trial mix be 1 yd3 (27 ft3) then according to ACI 211.1.8 Table 6.3.1 , slump required for slabs should be between 1 - 3 in .According to table 6.3.3 for 3 in slump and nominal aggregate size of 2 in , amount of water required per cubic yard of concrete is 285 lb/cy

=> Amount of water = 285 lb per yd3 concrete

For aggregate size 2 in, approximate air content is 0.5 % (0.135 ft3)

Now, required compressive strength as per ACI should be more of :

f'cr = f'c + 1.34 s or f'c + 2.33 s - 500

where, f'c = design compressive strength

s = standard deviation

Since, number of sample tested are more than 30 , standard deviation modification factor is 1

=> f'cr = 3000 + 1.34(250) or 3000 + 2.33(250) - 500

=> f'cr = 3335 psi or 3082.5 psi

fcr is larger of above two value,

=> fcr = 3335 psi

Now according to Table 6.3.4 (a) , for compressive strength of 3335 psi, water cement ratio is 0.64

Hence, amount of cement = 285 / 0.64 = 445.3 lb

Now, according to table 6.3.6 for nominal aggregate size of 2 in and fineness modulus of 2.68 , volume of coarse aggregate is 0.75 yd3 (20.25 ft3)

=> Amount of coarse aggregate = dry rodded weight x volume = 120 lb/ft3 x 20.25 ft3 = 2430 lb

Volume of fine aggregate = Total volume of concrete - Volume of water ,cement, coarse aggregate and air respectively

Volume of components = Weight / (Specific gravity x Water unit weight)

=> Fine aggregate volume = 27 - [(285/62.4) (445.3 / 3.15 x 62.4) + (2430/ 2.573 x 62.4) + 0.135]

=> Fine aggregate volume = 27 - 22.08 = 4.92 ft3

=> Amount of fine aggregate = Specific gravity x Water unit weight x volume = 2.54 x 62.4 x 4.92 = 779.8 lb

Admixture dose = 0.15 fl oz / 1 % air /100 lb cement

=> Admixture needed = (0.15 fl oz / 1% /100 lb) x 445.3 lb x 0.5 % = 0.334 fl oz

Now, since both aggregates has moisture and absorption capacity , amount of mixing water needs to be corrected

Water provided by coarse aggregate = (0.01 - 0.001) x 2430 lb = 21.87 lb

Water provided by fine aggregate = (0.0376 - 0.002) x 779.8 = 27.76 lb

=> Actual amount of water to be added = 285 lb -21.87 lb - 27.76 lb = 235.37 lb

Hence, final batch weight of components for 1 cy concrete are :

Component Cement Welght (lb) 445.30 235.37 Water Coarse Aggregate Fine Aggregate 2430 779.80

Admixture Dose = 0.334 fl oz

PLEASE UPVOTE IF YOU LIKE MY ANSWER.

THANK YOU

Add a comment
Know the answer?
Add Answer to:
Please show which equations you use and describe in detail. 21. concrete mix design, Design the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Design the concrete mix according to the following conditions: Design Environment Pavement slab, Bozeman, Montana (cold...

    Design the concrete mix according to the following conditions: Design Environment Pavement slab, Bozeman, Montana (cold climate) Required design strength = 3000 psi Slab thickness = 12 in. Statistical data indicate a standard deviation of compressive strength of 250 psi is expected (more than 30 samples). Only air entrainer is allowed. Available Materials Air entrainer: Manufacture specification is 0.15 fl oz/1% air/100 lb cement. Coarse aggregate: 2 in. nominal maximum size, crushed stone Bulk oven-dry specific gravity = 2.573, absorption...

  • Compute the SSD mix proportions for the following mix design using the ACI method: Compressive Strength:...

    Compute the SSD mix proportions for the following mix design using the ACI method: Compressive Strength: 3,000 psi Slump: 4 inches Non-Air Entrained Concrete The materials have the following properties: | Cement: Type I, specific gravity = 3.15 | Fine Aggregate: Bulk specific gravity = 2.68; fineness modulus = 2.40 Coarse Aggregate: Maximum size aggregate = 1 inch; bulk specific gravity = 2.68; Dry-rodded unit weight = 100 lbs/ft3

  • The question is as follows:- Q) Design the concrete mixture for the slab

    The question is as follows:- Q) Design the concrete mixture for the slab 2. A reinforced slab concrete foundation is to be poured for a building. The building is to be constructed near Edmonton. The slab will be in direct contact with the soil, and the soil typically has a sulphate content of 0.3 percent by mass. The minimum rebar spacing in the slab is 100 mm. The contractor is certain that his workers can place a concrete with a...

  • Q1// Use the ACI method to design a concrete mix which is required to obtain f'c28=...

    Q1// Use the ACI method to design a concrete mix which is required to obtain f'c28= 34.5MPa and a slump of 75mm. the fineness modulus of the aggregate is 3.0, the bulk density of coarse aggregate is 1600 kg/m' and the maximum size is 25. Both the specific gravity of fine and coarse aggregate are 2.68. neglect the absorption and total moisture content.

  • Hi, can you help me do this problem, i know its a little bit long but...

    Hi, can you help me do this problem, i know its a little bit long but i really need to know how to answer it and know the answer thank you Problem 2 Concrete Mix Design. (30 points) You are planning to place concrete for a roof slab in a 3 story light commercial building located in Boston, MA (cold climate). Develop the mix proportion for this concrete. Explain your selections. Design Criteria: 290 Design strength-3.700 psi Statistical data based...

  • Question 1. A concrete mix is to be designed for use in a 250 mm thick road pavement. The desired properties are pr...

    Question 1. A concrete mix is to be designed for use in a 250 mm thick road pavement. The desired properties are provided below. Use the ACI method to calculate the required amounts per unit volume (/1m) of water, cement, course aggregate and fine aggregate. Slump 25 mm Average 28-day flexural strength of at least 4.5 MPa Coarse aggregate: nominal maximum size = 37.5 mm, dry-rodded weight 1600 kg/m3, specific gravity 2.68, moisture content 1.0 percent, absorption 0.5 percent Fine...

  • please help with this concrete design mix problem (40 points) Design the concrete mix according to...

    please help with this concrete design mix problem (40 points) Design the concrete mix according to the following conditions. Perform the necessary computations to determine all ingredients in (kg) per unit volume of mix, and state resources and cite references used for each step. Summarize your design in the table at the bottom, and answer the questions beneath the table. Application Environment Area 52, airport location Idaho, (150m x 50m) runway test section Exposures: freeze-thaw, deicers Design Environment Concrete Requirements:...

  • Design a concrete mixture using the following data when the mixture design strength is 3000psi (20.7...

    Design a concrete mixture using the following data when the mixture design strength is 3000psi (20.7 MPa): Required strength = 5000 psi (34.5 MPa) type of structure: beam Maximum size of aggregate = 1in (18mm) Fineness Modulus of sand =2.6 Dry rodded weight of coarse aggregate = 100 lb/ft^3 Moisture absourption: 2% for Coarse and Fine aggregate

  • use (absolute volume method). Calculate the materials (type II cement, coarse aggregate, fine aggregate, and water)...

    use (absolute volume method). Calculate the materials (type II cement, coarse aggregate, fine aggregate, and water) needed to make 16 concrete cylinders (diameter = 4", height = 8") for our compression tests. Specified compressive strength = 3000 psi at 28 days. For coarse aggregate, please choose 3/4 in max size gravel containing some crushed particles with the following assumptions: oven-dry specific gravity of 2.68; oven-dry rodded unit weight: 100 lb per cu. ft; moisture content: 1%.

  • The following requirements are specified for concrete construction of a reinforced concrete jetty exposed to sea...

    The following requirements are specified for concrete construction of a reinforced concrete jetty exposed to sea water and moderate freeze and thaw environment Required Design Strength, fc Slump required Standard deviation Cement 35 MPa 25-75 mnm 4.8 MPa Ordinary portland cement with relative density 3.15 Fine Aggregate (Natural Sand) Oven-dry relative densitv SSD moisture content Moisture content of sample Fineness Modulus 2.3 0.2 % 4.3 % 2.63 Coarse aggregate (crushed stone) Nominal maximum aggregate size Oven-dry relative density SSD moisture...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT