A three-phase delta-connected synchronous induction motor is connected to a 415 volt, 50 Hz supply. The winding resistance is negligible and the synchronous reactance per phase is 5 ohms. The input power is 20 kW and the motor has a leading power factor of 0.8.
Draw the phasor diagram for this machine:
ii) use the IXs phasor and the V phasor to construct the phasor for E.
iii) measure or calculate the magnitude of E
iv) By construction and/or by calculation find the load angle
c) If the excitation and, as a consequence the generated emf, is reduced by 10%:
i) Calculate the new value of the generated emf E’
ii) Construct the new phasor for E’’ on the same diagram, using the same value for reactive volt drop
iii) Calculate or measure the load angle iv) Draw the new stator current phasor from the phasor diagram, measure or calculate the new power factor
We need at least 10 more requests to produce the answer.
0 / 10 have requested this problem solution
The more requests, the faster the answer.
A three-phase delta-connected synchronous induction motor is connected to a 415 volt, 50 Hz supply. The...
Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...
Problem 2 A 15 HP, 96% efficient, three-phase Wye-connected synchronous motor is connected to a 480 VAC, 60 Hz power supply. The field excitation is set such that the power factor is 0.97 leading. The machine draws 9 kW from the supplv. The per-phase armature reactance is 9500. Find the internally generated voltage, E, Calculate the motor torque angle, δ. Draw the phasor diagram, showing Vn E, XsL, IA ,Θ and δ. a. b. c. Problem 2 A 15 HP,...
Be detailed please A three-phase y-connected 2300 V, 60 Hz round-rotor synchronous motor has a synchronous reactance of 2 ohms/ phase and negligible armature resistance. 2. If the motor takes a line current of 350 A operating at a leading pf of 0.8. calculate the armature voltage and the power angle. If the motor is operating on load with a load angle of-20%, and the excitation is adjusted so that the armature voltage is equal in magnitude to the terminal...
A three phase 10-pole synchronous motor has per phase synchronous resistance of 4.3 ohm. It is connected to a 4160V (line to line) 60Hz line and generates an excitation voltage Eo of 1790V (line to neutral) when the dc exciting current is 30A. The Torque angle between E and Eo is 30 degrees. Calculate a) The mechanical angle between the center of rotor and stator poles b) The voltage across the synchronous reactance c) The power delivered to the motor...
b) A 1MW, 3300 V, 50 Hz, wye-connected, 3-ф, twenty four-pole, synchronous motor has a synchronous reactance of 3.24 2 per phase. Assume armature resistance is negligible. This machine is connected to an infinite bus-bars at 3300 V. Its field excitation is adjusted to provide P.F-1 at rated load Calculate: 0 the internal generated voltage EA and armature current la at rated conditions (S marks) ii) the maximum power and torqu e that the motor can deliver with its Ir...
Electric Machines - Synchronous Motors 4. A 150 kVA, 460-V, four pole, 60 Hz, three phase, Y-connected synchronous motor operatingat rated load has a synchronous reactance of 1.20 ohms/phase, determine: Excitation voltage Power angle Pull-out torque Draw a phasor diagram a. b. c. d. 4. A 150 kVA, 460-V, four pole, 60 Hz, three phase, Y-connected synchronous motor operatingat rated load has a synchronous reactance of 1.20 ohms/phase, determine: Excitation voltage Power angle Pull-out torque Draw a phasor diagram a....
Q2 (a) A star connected 6.6kV, 8MVA synchronous generator operating at 7MW and a 0.88 lagging power factor is connected to the Grid. The synchronous reactance is 1.5Ω (i) Calculate the phase current, excitation voltage and load angle. [10] (ii) What is the maximum theoretical power at this excitation? Draw a phasor diagram (to scale) and from this estimate the phase current and power factor when operating at this point. 151 Q2 (a) A star connected 6.6kV, 8MVA synchronous generator...
e connected, 60 Hz, 2300 volt, sik pole, cylindrical rotor synchronous motor is 8 leading, neglect losses, the synchronous reactance is 2.5 sand Fp ohm/phase. Determine: (a) Synchronous speed-n, (b) Developed torque in Horsepower Tmec (c) Active Power-P (d) Apparent Power-S (e) Reactive Power-Q (f) Draw the Power Triangle (g) Armature current-1 (h) Excitation voltage-Et (i) Power Angle-8 U) Draw the phasor diagram e connected, 60 Hz, 2300 volt, sik pole, cylindrical rotor synchronous motor is 8 leading, neglect losses,...
A 2200Vrms (line-to-line), 30Hz, Y-connected, 3-phase synchronous motor has a synchronous reactance of 10Ω per phase. The motor draws 163kW at a power angle of 15°. Determine: a) The excitation voltage per phase. b) The supply current and the supply power factor. c) Draw the phasor diagram for the above condition. d) Suppose the mechanical load is now disconnected, with all the losses are negligible. Determine the new supply current and the supply power factor.
(Question 1): (4pts) A three-phase, 2300-V, 60-Hz, 10-pole, A-connected cylindrical rotor synchronous motor has a synchronous reactance of 4.0 82/phase. The armature resistance may be neglected. It is connected to 2300-V source and drives a system with its excitation set to give a PF of 0.9-leading when the power is 500-kW. (a) Sketch the phasor diagram of this motor. (b) Calculate the armature current. (c) Calculate the excitation voltage and torque angle. (d) If the load torque is increased by...