Amount of heat to be supplied to the exterior zones is,
Q = 2,000,000 BTUH
This heat is supplied by flow of hot water through the heating system
So, =
Q
Given, Q = 2,000,000 BTUH = 586.14207732 kW
= 4.186
kJ/kgK
= 180 - 140
= 40
=
586.14207732 kW/4.186 kJ/kgK
40
= 3.5
kg/s
Volume flow rate = /
=
3.5/1000 = 0.0035 m3/s
Use conversion, 1 cubic meter/second = 13198.1549 gallon (UK)/minute
(a) Total hot water flow rate in GPM (UK gallons per minute) =
0.0035 13198.1549 =
46.2 GPM
(b) BHP = TDH GPM/Efficiency
3960
where TDH is the total discharge head measured in feet (30ft in this case)
GPM flow rate in gallons per minute (46.2 GPM in this case)
Efficiency of the pump is given as 50%(0.5 in this case)
and, 3960 is the conversion number we get by dividing 8.333 (the weight, in pounds, of one gallon of water) into 33,000 ( foot pounds in one horsepower).
Therefore, BHP = 30 46.2/0.5
3960 =
0.7BHP
(c) Let D be the diameter of the main pipe.
Area, A = =
0.7857D2
Using formula, =
AV,
where V is velocity through the main pipe.
Some information is missing as there are 2 unknowns in the above equation.
9-1 The above office requires 2,000,000 BTUH heating for exterior zones. A hot water heating system with a circulating pump is used for water circulation. Assume Heating coils have inlet temp 180 F o...
Problem 4.049 A pump is used to circulate hot water in a home heating system. Water enters the well-insulated pump operating at steady state at a rate of 0.42 gal/min. The inlet pressure and temperature are 14.7 lbf/in., and 180°F, respectively; at the exit the pressure is 90 lbf/in. The pump requires 1/35 hp of power input. Water can be modeled as an incompressible substance with constant density of 60.58 lb/ft and constant specific heat of 1 Btu/lb OR Neglecting...