Question

9-1 The above office requires 2,000,000 BTUH heating for exterior zones. A hot water heating system with a circulating pump i

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Amount of heat to be supplied to the exterior zones is,

Q = 2,000,000 BTUH

This heat is supplied by flow of hot water through the heating system

So, \dot{m}c_{p}\Delta T = Q

Given, Q = 2,000,000 BTUH = 586.14207732 kW

c_{p} = 4.186 kJ/kgK

\Delta T = 180 - 140 = 40

\dot{m} = 586.14207732 kW/4.186 kJ/kgK \times 40

\dot{m} = 3.5 kg/s

Volume flow rate = \dot{m}/\rho = 3.5/1000 = 0.0035 m3/s

Use conversion, 1 cubic meter/second = 13198.1549 gallon (UK)/minute

(a) Total hot water flow rate in GPM (UK gallons per minute) = 0.0035 \times 13198.1549 = 46.2 GPM

(b) BHP = TDH \times GPM/Efficiency \times 3960

where TDH is the total discharge head measured in feet (30ft in this case)

GPM flow rate in gallons per minute (46.2 GPM in this case)

Efficiency of the pump is given as 50%(0.5 in this case)

and, 3960 is the conversion number we get by dividing 8.333 (the weight, in pounds, of one gallon of water) into 33,000 ( foot pounds in one horsepower).

Therefore, BHP = 30 \times 46.2/0.5 \times 3960 = 0.7BHP

(c) Let D be the diameter of the main pipe.

Area, A = T D2/4 = 0.7857D2

Using formula, \dot{m} = \rhoAV, where V is velocity through the main pipe.

Some information is missing as there are 2 unknowns in the above equation.

Add a comment
Know the answer?
Add Answer to:
9-1 The above office requires 2,000,000 BTUH heating for exterior zones. A hot water heating system with a circulating pump is used for water circulation. Assume Heating coils have inlet temp 180 F o...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem 4.049 A pump is used to circulate hot water in a home heating system. Water...

    Problem 4.049 A pump is used to circulate hot water in a home heating system. Water enters the well-insulated pump operating at steady state at a rate of 0.42 gal/min. The inlet pressure and temperature are 14.7 lbf/in., and 180°F, respectively; at the exit the pressure is 90 lbf/in. The pump requires 1/35 hp of power input. Water can be modeled as an incompressible substance with constant density of 60.58 lb/ft and constant specific heat of 1 Btu/lb OR Neglecting...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT