12). B.
Covered is not same as Insulated. If a conductor is covered, it is
covered in the material of composition or thickness not recognised
by codes as Electrcial Insulation. If a conductor is insulated, it
is encased with the material of composition or thickness recognised
by the codes as electrcial insulation.
13). C
Installation of these open motors with commutators is permitted on
the wooden floors.
14). B.
Per the specification, the branch circuit conductors supplying a
motor that draws 40 A must have an ampacity of not less than 125 %
of the motor marked rating i.e, 40x 1.25 = 50 A
15). A.
The overload device should be rated atmost 125 percent of the
continuous duty motor rating. i.e, 125 Amperes in the
above case.Though, such overload protection is not required for the
motors having capacity less than 1 Hp.
16). D.
This is a electrical specification to be followed.
17). After power factor correction capacitor the line current gets
reduced to 80 Amp. Now, as per the codes the overload protection
device should not be more than 125 percent of the motor rating.
Following this the overload device is based on the current equal to
80x 1.25 = 100 Amperes.
18). None Answer is 125% based on NEC Codes.
Conductors supplying more than two or more motors must have an
ampacity not less than 125% of the rating of the highest rated
motor plus the sum of full load current of all the other
motors.
19). C.
General Rule
20). B.
This is by NEC Codes.
Several motors, each not exceeding 1 horsepower, are permitted on a
branch circuit protected at not more than 20 amperes at 120 volts
or less, or at 600 volts or less protected at not over 15 amperes
if all of the following conditions can be met:
The rating of the branch-circuit short-circuit and ground-fault
protective device marked on the controllers is not exceeded.
The full-load rating of each motor does not exceed 6 amperes.
Individual overload protection conforms with section 430-32 of the
NEC
(12 If a conductor is covered, it is: A) Encased with an insulation recognized by the Code 8) Encased with an outer...
Name HW Due 530/19 ART 430, 440 1. The motor disconnecting means is not required to be in sight from the motor and the driven machinery location, provided_ (a) the (b) the provisions for locking are permanently installed on, or at, the switch or circuit breaker used as the controller disconnecting means (c) locating the motor disconnecting means within sight of the motor is impractical or introduces additional or increased hazards to people or property (d) all of these controller...
1. Transformer with three legs A, B and C in case of homogenous
the first leg A has coil with 3 Henry, what is the Henry at leg
C
a. 0.5 H
b. 1 H
c. 2 H
d. 2.5 H
2. If a carrier wave of 10MHz is amplitude modulated by an audio
signal of 1 kHz, the resultant signal to be broadcast contains only
the:
(A) 10,001,000-Hz component
(B) 10,001,000-Hz and 9,999,000-Hz components
(C) 10,001,000-Hz, 10,000,000-Hz, and 9,999,000-Hz...
Class: Week 7 10. Where multiple power supplies serve the same de system, the dc side of each power su supply shall have a a. disconnecting means b. suitable ground c. removable conductor d. removable fuses 11. Generator accessories,including but not limited to, te electrically operated louver, ath altemate power accessories essential for generator operation, shall be arranged for automatic connection to source. a. transfer fuel pump c. environmental controls b. transfer circuit d. auviliary switching 12. Minimum ampacity of...
A) select the appropriate overcurrent protection device
size,
B) conductor size(s) (including equipment grounding
conductor),
C) conduit size(s)
D) Draw a schematic representation of the circuit (conduit and
tick marks)
Please dont skip steps and label which tables you used!
thanks
240V-іф branch circuit to an electric range with a continuous load of 8700 VA. Copper conductors, TW insulation, and ENT conduit. Use Chapter 9, Tables 4 and 5 for sizing the conduit. 4,
1. The color of the outer finish of the insulation or tape marking a grounded conductor must be A. black B. green. C. white or gray D. yellow finish. 2. When the main bonding jumper in a residential el ectrical system is a screw only, the screw must be identified with a A. white B. red C. green D. black The grounding electrode conductor should be installed without a splice, unless the splice is made using exothermic welding or by...
The equivalent circuit of a 440 V, 3-phase, 8 pole, and 50 Hz star-connected induction motor is shown in figure 1. The short-circuit test is conducted with a locked rotor and a line current of 80 A. The open-circuit test is conducted by supplying the stator winding at rated voltage and at the rotor is rotating freely without any mechanical load.a) Determine the line voltage and power factor on the short circuit test;b) We need to apply a low...
Question: The equivalent circuit of a 440 V, 3-phase, 8 pole, and 50 Hz star-connected induction motor is shown in figure 1. The short-circuit test is conducted with a locked rotor and a line current of 80 A. The open-circuit test is conducted by supplying the stator winding at rated voltage and at the rotor is rotating freely without any mechanical load. Fig. 1 The per-phase equivalent circuit of a 3-phase induction motora) Determine the line voltage and power factor on the...
3. An electric motor draws 2238 W and 12 A when operating on a 240 V source. Determine the (a) Power factor of the motor. (b) Apparent power input to motor. (c) True power input to motor. (d) Horsepower output of the motor if it is 75% efficient. 4 The follwing s found on the nameplate of a motor. 3 hp 60 Hz 1 phase 120/240 V 34/17 A 1,740 RPM irthe power factor of the motor is 0.30, what...
Question: The equivalent circuit parameters of a 440 V, 3-phase, 8-poles, and 50 Hz star connected motor are given below. The short-circuit test is conducted with a locked rotor and a line current of 80 A. The open-circuit test is conducted by supplying the stator winding at rated voltage and at the same time driving the rotor in the same direction as the rotating field, at synchronous speed; s=0.R1 = 0.1, X1 = 0.5, RI2 = 0.1, XI2 = 0.5, Xm = 20, Rm = 100...
Question: The equivalent circuit parameters of a 440 V, 3-phase, 8-poles, and 50 Hz star connected motor are given below. The short-circuit test is conducted with a locked rotor and a line current of 80 A. The open-circuit test is conducted by supplying the stator winding at rated voltage and at the same time driving the rotor in the same direction as the rotating field, at synchronous speed; s=0.R1 = 0.1, X1 = 0.5, RI2 = 0.1, XI2 = 0.5,...