.0.5 kg/s of refrigerant R-134a undergoes a series of steady-state operations as indicated in the figure below: 12: Isobaric
0 0
Add a comment Improve this question Transcribed image text
Answer #1

The saturated thermodynamic property of R 134a available in literature is shown below (Table 1)

TABLE 1

D m/kg Ugm/kg h, k]/kg | hg, kJ/kg | $4, kJ/(kg-K) | sp, kJ/(kg-K) Pressure, bar Temp, K Cafs kJ/(kg-K)H, 10* Pa-sk W/(m-K) P

Flow of refirgerant is 0.5 kg/s

At position 1

Refrigerant is a saturated liquid at 2 bar a

The specific enthalpy (of saturated liquid) of the refrigerant is 38.13 kJ/kg (from the table 1)

Total Enthalpy at 1 (AH1 = specific enthalpy * flow rate = 38.13 * 0.5 =19.065 kJ/s

At position 2

The refrigerant evaporates isobarically, hence the pressure at position 2 is 2 bar a

Refrigerant is a saturated vapor at 2 bar a (given)

The specific enthalpy (of saturated vapor) of the refrigerant is 244.14 kJ/kg (from the Table 1)

The specific entropy (of saturated vapor) of the refrigerant is 0.9364 kJ/kg (from the table 1)

Total Enthalpy at 2 (AH2 = specific enthalpy * flow rate = 244.14 * 0.5 =122.07 kJ/s

The amount of heat required to in evaporation process = (ДН2) - (ДН1) (АH) = 122.07-19.065 = 103.005 kJ/s

At position 3

The refrigerant gets compressed to 5 bar (given) in a reversible and adiabatical manner (which is termed as isentropic process)

In a isentropic process, the entopy of the process remains the same.

We will have to use a superheated table for R 134a where the pressure is 5 bar and the entropy is same as position 2 i.e 0.9364 kJ/kg from the following table:

TABLE 2
P=0.50 MPa (15.7°C) |Temp volumeenthalpy entropy °C V(m 3/kg) h(kJ/kg) s(kJ/kg.K) 259.3 263.5 273.0 282.5 292.0 301.5 0.924 0

The specific enthalpy of the refrigerant is 263.5 kJ/kg (from the table 2)

Total Enthalpy at 3 (AH3 = specific enthalpy * flow rate = 263.5 * 0.5 =131.75 kJ/s

The power input to the compressor = [ΔΗ)- ΔΗ = 131.75 - 122.07 = 9.68 kJ/s

At position 4

The refrigerant losses heat in the condenser isobarically to form saturated liquid at 5 bar a

The specific enthalpy (of saturated liquid) of the refrigerant is 72.87 kJ/kg (from the table 1)

Total Enthalpy at 4 ΔΗ 4 = specific enthalpy * flow rate = 72.87 * 0.5 =36.435 kJ/s

The amount of heat extracted in condenser = [ΔΗ-ΔΗ) = 36.435 - 131.75 = -95.315 kJ/s

Note: Negative sign means heat to be removed

At position 5

In a throttling process, the high pressre liquid is converted to low pressure liquid without any change in the total enthalpy (same as position 4). The temperature of refrigerant will be the saturation temperature at that pressure (from table 2). Temperature = 266.88 K

Total Enthalpy at 5 (AH5 =36.435 kJ/s

The specific enthalpy of saturated liquid of the refrigerant is 45.75 kJ/kg (from the table 1)

The specific enthalpy of saturated vapor of the refrigerant is 247.60 kJ/kg (from the table 1)

Let x be the flow of vapor present at positon 5

Therefore flow of liquid present at position 5 = total refrigerant flow - vapor flow = 0.5 - x

Total enthalpy at 5 (AH5 = Total enthalpy of vapor at 5 + Total enthalpy of liquid at 5

36.435 = x * 247.60 + (0.5-x) * 45.75

x = 0.0672 kg/s

Vapor quality = Vapor flow / Total flow = 0.0672 / 0.5 *100 = 13.44 %

Vapor quality =13.44 %

Add a comment
Know the answer?
Add Answer to:
.0.5 kg/s of refrigerant R-134a undergoes a series of steady-state operations as indicated in the figure below: 12:...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A Refrigeration System Using R-134A In a refrigeration system, the refrigerant R-134A begins as s...

    A Refrigeration System Using R-134A In a refrigeration system, the refrigerant R-134A begins as saturated vapor at -15°(State 1). It then goes through a reversible adiabatic compressor to reach State 2. After flowing through the condenser (a heat exchanger), the refrigerant exits as saturated liquid at 70°C (State 3). It is then throttled by going through an expansion valve, to reach State 4. It finishes the cycle by going through another heat exchanger (the evaporator), to return to State 1....

  • An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at -10°C, and saturated liquid leaves the condenser at 28°C. The mass flow rate of refrigerant is 5 kg/min. Determine (a) The compressor power, in kW (b) The refrigerating capacity, in tons. (c) The coefficient of performance. Sketch the system on a T-s diagram with full label. A vapor-compression heat pump with a heating capacity of 500 kJ/min is...

  • Problem 4.067 SI The figure below provides steady-state data for a throttling valve in series with...

    Problem 4.067 SI The figure below provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of P = 2 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10°C with no significant decrease in pressure. In a separate stream, liquid water at 1 bar enters the heat exchanger at a temperature of 25°C...

  • The figure below provides steady-state data for a throttling valve in series with a heat exchanger.

    The figure below provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of p2 2 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10°C with no significant decrease in pressure. In a separate stream, liquid water at 1 bar enters the heat exchanger at a temperature of 25°C with a mass flow...

  • An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at 1.25 bar, and saturated liquid exits the condenser at 5 bar. The mass flow rate of refrigerant is 8.5 kg/min. A. Determine the magnitude of the compressor power input required, in kW (report as a positive number). B. Determine the refrigerating capacity, in tons. C. Determine the coefficient of performance. Please answer all parts of the question. Thanks!

  • A vapor compression refrigeration system operates at steady state with refrigerant 134a as the working fluid....

    A vapor compression refrigeration system operates at steady state with refrigerant 134a as the working fluid. Superheated vapor enters the compressor at 10 lbf/in2 , 0 oF. The liquid leaving the condenser is at 180 lbf/in2 , 100 oF. There is no significant pressure drop in the evaporator or condenser. For compressor efficiency of 83% and refrigeration capacity of 6 tons, determine (a) the compressor power input in horsepower, and (b) the coefficient of performance. A vapor compression refrigeration system...

  • Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C...

    Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C at a rate of 0.025 kg/s and leaves at 1000 kPa as saturated liquid. If the compressor consumes 2 kW of power, determine: a) The COP of the heat pump (as heating device). b) The rate of heat absorption from the outside air. тан Condenser Throttling valve Compressor Evaporator To

  • Figure P4.96 provides steady-state data for a throttling valve in series with a heat exchanger

    4.96 Figure P4.96 provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of 2 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10℃ with no significant decrease in pressure. In a separate stream, liquid water at 1 bar enters the heat exchanger at a temperature of 25℃ with a mass flow rate of...

  • Figure 12.1 is a schematic of a heat pump operating at steady state with R-134a as...

    Figure 12.1 is a schematic of a heat pump operating at steady state with R-134a as the working fluid. The mass flow rate of the refrigerant is 7 kg/min, and the power input to the compressor is 5.17 kW. Determine a) The coefficient of performance, y b) If the valve were replaced by a turbine, what would be the maximum power generated by the turbine c) Based on your answer to b) would you recommend the replacement of a throttle...

  • refrigerator, as shown in FIGURE P 3 with the corresponding T-s diagram, uses refrigerant R-134a as...

    refrigerator, as shown in FIGURE P 3 with the corresponding T-s diagram, uses refrigerant R-134a as the working fluid and operates on the ideal vapour-compression refrigeration cycle except for the compression process. The refrigerant enters the evaporator at 120 kPa with a quality of 34.026 percent and leaves the compressor at 70 0C. If the compressor consumes 0.45 kW of power, Determine: (a) The mass flow rate of the refrigerant, in kg/s, correct to 6 dp. (b) The condenser pressure,...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT