Question

wers with necessary diagrams and equations b) 15 Two balanced loads are connected to a 240 V, 50-H line as shown in Fig. 7(b)

(Appropriate and detailed solution will certailny help a lot. Thaanks for your support.)

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Ans)

Given

For load 1

Vine 240 kV

P 30 kW pf cosp0.6 lagging

now

30k P1 2-cos 10.6 2- cos pfi COs V3 240k0.6 line negative sign in angle because power factor is lagging current lags behind voltage

0.122 53.13 A

======

For load 2

45 kV AR, pf2= COsp2=0.8 lagging

P2 Qcotp2 45k* cot(cos 0.8) 60 kW

260 kW

now

Р2 60k 2-cos 10.8 2- cos pf2 COs V3 240k 0.8 line

I20.18Z- 36.87° A

===========

now

Ia Ia1 Ia2 = 0.122-53.1300.182-36.87

\mathbf{I_{a}=0.298\angle -43.36^{o}\: \: A}

as the given circuit is balanced all the line currents are same in magnitude with phase difference of 120 degrees as below

II-120 0.298Z- 43.36- 1200

Lb0.298-163.360 A

I_{c}=I_{a}\angle +120^{o}=0.298\angle -43.36^{o}+120^{o}

\mathbf{I_{c}=0.298\angle 76.64^{o}\: \: A}

Add a comment
Know the answer?
Add Answer to:
(Appropriate and detailed solution will certailny help a lot. Thaanks for your support.) wers with necessary...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from...

    10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...

  • Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation...

    Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation bus supplies three wye-connected three phase loads that are connected in parallel through a three-phase feeder with an impedance of 0.3 30 per phase Load 1 draws 75kVA at 0.866 lagging power factor, load 2 draws 45 kW at 0.70 leading power factor and load 3 draws 20 kVAR at 0.85 lagging power factor. The line-line voltage at the load is 460V Take the...

  • 508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an...

    508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...

  • 1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF...

    1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF lagging Load 2 draws 20 kVA at 0.6 PF leading a. b. The loads are supplied by a balanced three-phase 480 Vu source. (a) Draw the power triangle for the combined load. (b) Determine PF of the combined load. (c) Determine the magnitude of the line current from the source. (d) Y-connected inductors are now installed in parallel with the combined load. What value...

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • Problem 7 Three three-phase wye-connected loads are in parallel across a three-phase supply. The first load draws a cur...

    Problem 7 Three three-phase wye-connected loads are in parallel across a three-phase supply. The first load draws a current of 10 A at pf- 0.93 (leading), and the second and third loads (each) draw a current of 20 A at pf= 0.85 (lagging). Suppose the line-to-line voltage is 240 V. Compute the following: a) The transmission line current b) The load power factor c) The complex power supplied by the source Problem 7 Three three-phase wye-connected loads are in parallel...

  • EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT...

    EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT I CAN EASILY UNDERSTAND WHAT WE ARE FINDING AND HOW WE ARE FINDING THE REQUIRED THINGS .I AM POSTING MY QUESTION 4TH TIME PLEASE DONOT WASTE IT AND PLEASE DO ALL STEPS I NEED MY ANSWER STEP BY STEP by the line Two balanced Y-connected loads, one drawing 10 kW at 0.8 power factor lagging and the other 15 kW at 0.9 power factor...

  • 1. A 480 V (rms) source supplies power to two loads connected in parallel. The first...

    1. A 480 V (rms) source supplies power to two loads connected in parallel. The first load draws 80 kW and 30 kVAR. The second load draws 100 kVA at a power factor of 0.6 lagging. a) Draw the power triangle for the first load and determine its power factor; b) Determine the current (both magnitude and phase, using the source voltage as the phase reference) drawn by the first load; c) Draw the power triangle for the second load...

  • 1.2 kW 0.8 kVAR (cap) (a) In the circuit shown in Fig. Qla, find: Construct the...

    1.2 kW 0.8 kVAR (cap) (a) In the circuit shown in Fig. Qla, find: Construct the power triangles for the loads. (ii) Find the overall complex power consumed in the loads. (iii) Find the current lo. 100/90° v (rms) 2 kVA 0.707 pf leading 4 kW 0.9 pf lagging Fig. Qla (b) [This part has no connection to part (a)] Find the value of the parallel capacitance needed to correct a load of 140 kVAR at 0.85 lagging pf to...

  • A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line...

    A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase supply. A bank of power factor capacitors is delta connected. (a) Draw neat schematic diagram showing the connection of the capacitor bank in Delta connection. (b) Determine the KVAR rating of each individual capacitor needed to bring power factor to 0.9. (c) Determine the capacitance of each capacitor in uF.

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT