Question




4-13. The no-load test on a certain transformer with its secondary terminals open yields this data: 400 V, 2.5 A. 150 W. Negl
0 0
Add a comment Improve this question Transcribed image text
Answer #1

PqoL ५००० open To No-Load ckt Goov Ro Im jxm w (Equivalent) Nagleting the winding resistanca leakage flux. I = 2.5A 7 Vs= 400RC = Us 50 Pg. 2 400² 10 67 2 (approx.) 150 Now 1 150 = 1,² x 1067 0.374 A magnetizing Current (Im) = Is sind Io. sind 2.5X SAll the three parts has been solved..!!!

Add a comment
Know the answer?
Add Answer to:
4-13. The no-load test on a certain transformer with its secondary terminals open yields this data:...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited...

    A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...

  • A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table...

    A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table below, a) For the rated load having a lagging power factor of 0.8, find the magnitude of the load current in Amperes. 15 Primary resistance 0.02 econdary resistance 120 Primary leakage reactance X2wL2 0.15 Secondary leakage reactance Xm=wLm Magnetizing reactance 30 k Re 200 k Core-loss resistance Answer: Check b) Find the phase of he load current in degrees (note: sign is important). Answer:...

  • PLEASE SO PART C, THANK YOU WILL RATE. A single-phase transformer with a 5:1 turns ratio...

    PLEASE SO PART C, THANK YOU WILL RATE. A single-phase transformer with a 5:1 turns ratio is connected to a 600 V voltage source on the primary side, and a 5 Ω resistor on the secondary. A current of 22 amps of current is measured to flow through the 5 Ω resistor on the secondary side. The real power flowing into the transformer primary is measured at 2500 W. You can neglect Lm and Rc (the magnetizing inductance and core...

  • The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied...

    The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied to the secondary gave a wattmeter reading of 60 W and secondary current of 10 A. II the normal applied primary voltage is 200 V, the transformation ratio 1:2 and the full-load secondary current 10 A, calculate the secondary p.d. at full-load current for (a) unity power factor (b) power factor 0.8 lagging. these are the answers [ 394 V; 377.6 V ]

  • An autotransformer with a total of 600 turns has its secondary embracing 200 turns. The 600...

    An autotransformer with a total of 600 turns has its secondary embracing 200 turns. The 600 turns is connected to a 60 Hz, 2400 V driving voltage. A load connected to the Secondary draws 4.8 kVA at 0.6 power factor lagging. Neglecting losses and leakage effects, determine: (a) secondary voltage; (b) secondary current; (c) primary current; (d) KVA conducted; (e) KVA transformed; (0) the instantaneous maximum value of the core flux.

  • single phase transformer with open circuit test and short circuit test

    A 20 kVA, 12,000/380 V, single-phase transformer has the following test results:open circuit (low voltage side): V = 380, I = 2, P = 250short circuit (high voltage side): V = 200, I = 2.5, P = 250a)Determine the approximate equivalent circuit parameters of the transformer in per-unit values.b) the transformer is working at 80% full load with 0.85 power factor lagging. what is the secondary current at this working condition in both actual and per-unit values. 

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Please show full working Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and power efficiency...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Help me answer c and d Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and...

  • step by step please The following data were obtained for a 20-kVA, 60-Hz, 2400:240-V distribution transformer...

    step by step please The following data were obtained for a 20-kVA, 60-Hz, 2400:240-V distribution transformer tested 5. at 60 Hz Power Voltage V Current, A 240 61.3 1038 8.33 With high-voltage winding open-circuited With low-voltage terminals short-circuited 122 257 Compute the efficiency at full-load current and the rated terminal voltage at 0.8 power factor. a. Assume that the load power factor is varied while the load current and secondary terminal voltage are b. held constant. Use a phasor diagram...

  • Q-1 A 60Hz, 480V/240V,960V A transformer is supplying a 960W passive load at 240V. The resistances...

    Q-1 A 60Hz, 480V/240V,960V A transformer is supplying a 960W passive load at 240V. The resistances of the primary side and secondary side of the transformer are 1.092 and 0.252 respectively. If the no load losses of the transfomer is given by P-Vã 4800 W where Vn is the input voltage of the transformer in Volt. Answer the following: a) Calculate transformer efficiency b) Do you allow this transformer to be connected to 240V 50Hz distribution system? Explain. c What...