Question

QUESTION 1 [25 MARKS] The data in the Table 1 were obtained when open and short circuit test were performed on a single phase

0 0
Add a comment Improve this question Transcribed image text
Answer #1


Que 1-0 , 50kVA 2400 / 240, 60Hz ohen araut test 240 V 4,85 A 173W so Zo = > (coste Р VI T 240 17 3 Cort (! La 4.85 240X485 Z a hom (1:5+12,0) T les 1 v2 load Zo = 49.484/81-45°, to ad side. b a load of o-spf. is connected to coor ji wo 0.75 j K 0.75c two wads are Connents so Ig 50X0.5 X 1000 50X65X100 (Costo 8 t (lost 0.85 २५० Ia = 172.04 ) -2.54* Amy so Up Vat (x + R₂ )

Add a comment
Know the answer?
Add Answer to:
QUESTION 1 [25 MARKS] The data in the Table 1 were obtained when open and short...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • QUESTION 1 125 MARKS] The data in the Table 1 were obtained when open and short...

    QUESTION 1 125 MARKS] The data in the Table 1 were obtained when open and short circuit test were performed on a single phase 50 kVA, 2400/240 V, 60 Hz transformer. Table 1 Voltage Current Power (V) (A) (Watt) 240 4.85 173 52 20.83 650 Test A Test B (a) Determine tests A, B and the sides the tests were done. Calculate the non-ideal transformer parameters referred to the low voltage side. Draw the equivalent circuit by labeling the parameters...

  • The following data was obtained when open circuit and short circuit tests were performed on a...

    The following data was obtained when open circuit and short circuit tests were performed on a single phase, 50 KVA, 2,400:240 V, 60 Hz distribution transformer: With high voltage winding open circuited: Voc = 240 V, Ioc = 4.85 A, Poc = 173 W With low voltage winding short circuited: Vsc = 52 V, Isc = 20.8 A, Psc = 650 W a) Determine the equivalent circuit of the transformer referred to its high voltage side and to its low...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617...

    The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...

  • Electric Machines Problem 1 (40 points) The following data were obtained for a 20 kVA,60 H...

    Electric Machines Problem 1 (40 points) The following data were obtained for a 20 kVA,60 H z, 2400/240 V distribution transformer tested at 60 Hz: HV open circuited: Voc 240 V, loc 1.038 A, Poc 122 W LV short circuited: Vc 61.3 V,Is8.33 A, Pc 257 W 1) Find the parameters of the transformer and equivalent circuit referred to LV side 2) Find voltage regulation when the transformer oper ates as step down and delivers its rated kVA at rated...

  • can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer...

    can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...

  • 4.41 Consider ạ 25 kVA, 240°/240 V, 60 Hz transformer with Z,-2.533 +J2.995 Ω and Z, = (2.5333 + ...

    4.41 Consider ạ 25 kVA, 240°/240 V, 60 Hz transformer with Z,-2.533 +J2.995 Ω and Z, = (2.5333 + )2.995) 10-2 S2, referred to the primary and secondary sides, respectively. b) The transformer is connected at the receiving end of a feeder that has an impedance of 0.3 +j 1.8 Ω. Let the sending end-voltage magnitude of the feeder be 2400 V. Also there is a load connected to the secondary side of the transformer that draws rated current from...

  • Q8. The following data are obtained when open circuit and short circuit tests are performed on...

    Q8. The following data are obtained when open circuit and short circuit tests are performed on a single phase, 50 kVA, 2400/240 Volt 50 HZ distribution transformer. VOLTAGE(volts)CURRENT (amperes) POWER (watts) 213 Measurement in low voltage side with high voltage winding open Measurement on high voltage side with low voltage winding shorted 240 5.97 60 20.8 750 (a) Neglecting the series impedance, determine the exciting admittance referred to the high voltage side. (b) Neglecting the exciting admittance, determine the equivalent...

  • single phase transformer with open circuit test and short circuit test

    A 20 kVA, 12,000/380 V, single-phase transformer has the following test results:open circuit (low voltage side): V = 380, I = 2, P = 250short circuit (high voltage side): V = 200, I = 2.5, P = 250a)Determine the approximate equivalent circuit parameters of the transformer in per-unit values.b) the transformer is working at 80% full load with 0.85 power factor lagging. what is the secondary current at this working condition in both actual and per-unit values. 

  • a) Discuss the main role of per-unit systems. (CO3:P01 - 3 marks) b) A single phase...

    a) Discuss the main role of per-unit systems. (CO3:P01 - 3 marks) b) A single phase two winding transformer rated at 20 kVA, 415/230 volts 50 Hz is subjected to open and short circuit test. Table Q3 (a) summarize the results of the test; Table Q3 (a) Open Circuit Test 12 = 12 A P2 = 200 W Short Circuit Test V1 = 35 V P1 = 300 W I. Based on the short circuit test, determine the equivalent series...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT