Question

It is found that 40 kJ.s- of heat energy is lost from a building when the internal air temperature is maintained at 22°C and

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Please refer to the attached images where i have shown the entropy generation calculation and other answers asked in the question. Do comment in case of any query and please up-vote this answer if you find it to be usefuk.

P.s We are provided a stipulated time period for solving a question, as per HOMEWORKLIB POLICY it is mandatory to attempt atleast first four sub questions. I have answered the first five. Sorry, for the inconvinience caused.

Ik Data provided: Temperature of outside air Ta= 66 =2494 Temperature of inade aur To = 22°c= 295k Heat energy lost ☺ - 40kh* Ph diagram of heat pomp. P Qout 1 N Qin 3-2 2-1 (compresion procen) (Heat out) (4-3) (expansion Valve) (9-4) (Heat Inpot) Cthe red Rigua is going to be used worlling eisid Compresor prewore and temperature Coutlet) P2- 7.5bar T2 = 39°c. Condenser P

Add a comment
Know the answer?
Add Answer to:
It is found that 40 kJ.s- of heat energy is lost from a building when the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 6. An office building requires a heat transfer rate of 20 kW to maintain the inside temperature a...

    6. An office building requires a heat transfer rate of 20 kW to maintain the inside temperature at 21°C when the outside temperature is 0°C. A vapor-compression heat pump with Refrigerant 134a as the working fluid is to be used to provide the necessary heating. The compressor operates adiabatically with an isentropic efficiency of 82%. Specify appropriate evaporator and condenser pressures of a cycle for this purpose assuming Δ1cond-Al evap-10°C, as shown below. The states are numbered as shown below....

  • The heat-pump system shown is designed to provide water-heating and space-cooling. The system includes a heat...

    The heat-pump system shown is designed to provide water-heating and space-cooling. The system includes a heat exchanger to subcool the R134a refrigerant at the outlet of the water heater while heating the refrigerant at the outlet of the evaporator. Given the following data, determine the enthalpy at each station, 1 through 6, using the R134a property tables (click here). Type your answers hy through h6 in the space provided below, and show all your work on your paper. · At...

  • now pleassse QUESTI 20 points Save An The heat-pump system shown is designed to provide water...

    now pleassse QUESTI 20 points Save An The heat-pump system shown is designed to provide water heating and space-cooling. The system includes a heat exchanger to subcool the R134a refrigerant at the outlet of the water heater while heating the refrigerant at the outlet of the evaporator. Given the following data, determine the enthalpy at each station, 1 through 6, using the R134a property tables (click here). Type your answers hy through h6 in the space provided below, and show...

  • PLEASE ANSWER QUICKLY!! I WILL THUMBS UP! Thank you so much in advance!! The heat-pump system...

    PLEASE ANSWER QUICKLY!! I WILL THUMBS UP! Thank you so much in advance!! The heat-pump system shown is designed to provide water-heating and space-cooling. The system includes a heat exchanger to subcool the R134a refrigerant at the outlet of the water heater while heating the refrigerant at the outlet of the evaporator. Given the following data, determine the enthalpy at each station, 1 through 6, using the R134a property tables (click here). Type your answers hy through h6 in the...

  • In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a....

    In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a. A water source of 11 °C is used to heat a house with a heating load of 17 kW. Refrigerant enters the compressor as saturated steam at 100 kPa pressure and rises at 1.6 MPa, 60 ° C. The temperature of the refrigerant at the outlet of the condenser is 30°C. a) The amount of heat at the beginning of the water, b) Compressor...

  • Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C...

    Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C at a rate of 0.025 kg/s and leaves at 1000 kPa as saturated liquid. If the compressor consumes 2 kW of power, determine: a) The COP of the heat pump (as heating device). b) The rate of heat absorption from the outside air. тан Condenser Throttling valve Compressor Evaporator To

  • Refrigeration Question 1 a) A refrigerant R134a refrigerator is to maintain the refrigerated spac...

    Refrigeration Question 1 a) A refrigerant R134a refrigerator is to maintain the refrigerated space at -100C. Would you recommended an evaporator pressure of 1.6 bar or 2 bar for this system? Why? -la An automotive Air conditioner using refrigerant R134a as the working fluid and operating on ideal vapor compression refrigerant cycle is to maintain a space at 24°C while operating its condenser at 1000 kPa. Determine the COP of the system when a temperature difference of 14°C is allowed...

  • Problem I: Not applicable for 2017 Problem II: In an R-134a vapor-compression home heat pump, R-134A...

    Problem I: Not applicable for 2017 Problem II: In an R-134a vapor-compression home heat pump, R-134A enters the compressor (75% isentropic efficiency) as a saturated vapor at 200 kPa and leaves at 800 kPa. The refrigerant goes through a constant pressure condenser and leaves as a saturated liquid. The refrigerant then goes through an adiabatic expansion valve enters the evaporator as a liquid-vapor mixture. The mass flow rate of refrigerant is 0.1 kg/s. and Cod A. Write the equation for...

  • Problem: Feasibility Study of Recovering Waste Heat from Primary Process Cooling Water to Provide Heat for...

    Problem: Feasibility Study of Recovering Waste Heat from Primary Process Cooling Water to Provide Heat for a Secondary Process Primary Process Cooling Water 100 F Secondary Process Requirements: Heat Supply Rate of 330,000 BTU/hr at 150 F Recovery System Heat Pump R134a Compressor Isentropic Efficiency: 76% Design Values Evaporator Coil Design Pressure: 160 psi Condenser Coil Design Pressure: 300 psi Deliverables Design Coil Temperatures (Evaporator and Condenser) - Confirm that these will be consistent with temperatures at the heat source...

  • Refrigerant-134a enters the condenser of a residential heat pump at 800 kPa and 35°C at a...

    Refrigerant-134a enters the condenser of a residential heat pump at 800 kPa and 35°C at a rate of 0.018 kg/s and leaves at 800 kPa as a saturated liquid. If the compressor consumes 1.2 kW of power, determine (a) the COP of the heat pump and (b) the rate of heat absorption from the outside air.