Question

Moist air at 300C and 50% RH enters a dehumidifier operating at steady state with a...

Moist air at 300C and 50% RH enters a dehumidifier operating at steady state with a volumetric flowrate of 280 m3/min. the moist air passes over the refrigerating coil and water condenses. The condensate leaves at 100C. Saturated moist air leaves in a separate stream at the same temperature. There is no significant loss of energy by heat transfer to the surroundings and the pressure remains constant at 1.013 bar. What is the rate of condensation of water in kg/min? ans: 1.87

0 0
Add a comment Improve this question Transcribed image text
Answer #1

* 2 0 Dehumidifiere 10°C 100%RH 30°C 50% RH 280 m/min 1.013 bar watere wondencate min 00 Pressure = 1.013 bar = 101.3 k Pa.,of kg dry ais Amount watere condensed = (13-31 - 7.6) g watere x 326.5226 Kg min = 1864.44 Kg water min 1864.44 kg water min

Add a comment
Know the answer?
Add Answer to:
Moist air at 300C and 50% RH enters a dehumidifier operating at steady state with a...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • An air conditioner operating at steady state takes in moist air at 30 °C, 1 bar and a wet bulb temperature of 25

    An air conditioner operating at steady state takes in moist air at 30 °C, 1 bar and a wet bulb temperature of 25 °C. The moist air is cooled in the dehumidifier unit and some of the water is removed. There is 10 tons of cooling in the dehumidifier (also called the evaporator of an air conditioner). The condensate and the saturated air stream discharging the section is at 10 °C The moist air is then heated in the heater...

  • QUESTION 1 [15 marks] Due: 5 August 2020 An air conditioner operating at steady state takes...

    QUESTION 1 [15 marks] Due: 5 August 2020 An air conditioner operating at steady state takes in moist air at 28°C, 1 atm and 70% relative humidity. The moist air first passes over a cooling coil in the dehumidifier unit and some water vapor is condensed. The rate of heat transfer between the moist air and the cooling coil is 38.69 kW. Both saturated moist air and condensate streams exit the dehumidifier unit at the same temperature. The moist air...

  • Moist air at 30C, 1.0325bar and 50% relative humidity enters a heat exchanger operating at steady...

    Moist air at 30C, 1.0325bar and 50% relative humidity enters a heat exchanger operating at steady state at 1000kg/h. It is cooled at constant pressure to 20C. Ignoring kinetic and potential energy changes, determine the following: A. At approximately what temperature will the water in the moist air condense? (8 of 45 points. Please input your final answer in the box below) B.Does condensation occur? (2 of 45 points. Please input your final answer in the box below) C.Determine the...

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 895 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. a)Determine the mass flow rate of the dry air in lb(dry air)/min....

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in lbm(dry...

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in Ibm(dry...

  • Problem 2: A residential air-conditioner with an actual cooling capacity of 14.06 kJ/s (4 tons), cools and dehumidifies a steady stream of air flowing over the cooling coil. Actual states for the Ref...

    Problem 2: A residential air-conditioner with an actual cooling capacity of 14.06 kJ/s (4 tons), cools and dehumidifies a steady stream of air flowing over the cooling coil. Actual states for the Refrigerant 134a are given Notice that the compressor efficiency is less than 100% and there are small pressure drops given for the heat exchangers. The coefficient of performance is 3.51 for the actual cycle. Changes in kinetic and potential energy are negligible. The warm indoor air temperature entering...

  • Problem 12.043 SI Air enters a compressor operating at steady state at 50°C, 0.9 bar, 70%...

    Problem 12.043 SI Air enters a compressor operating at steady state at 50°C, 0.9 bar, 70% relative humidity with a volumetric flow rate of 0.8 m3/s. The molst alr exits the compressor at 155°C, 1.5 bar Assuming the compressor is well insulated, determine: (a) the relative humidity at the exit, in percent (b) the magnitude of the power input, in kVW (c) the rate of entropy production, in kW/K

  • Question 1 Moist air, saturated at 5°C, enters a heating coil at a rate of 10 m2/s. Air leaves th...

    Question 1 Moist air, saturated at 5°C, enters a heating coil at a rate of 10 m2/s. Air leaves the coil at 40°C. a) What is the nature of this transformation? Find from the psychrometric chart the required rate of heat addition. n r Tables Vertical wall in wi Horizontal wall in contact with the ground (Hoor of a heated space, buried) all adjoining to an unheated room (garage, sh Wall in contact with the outside Space category contact with...

  • Uestion 2 Moist air, saturated at 5°C, enters a heating coil at a rate of 10 m'/s. Air leaves the...

    uestion 2 Moist air, saturated at 5°C, enters a heating coil at a rate of 10 m'/s. Air leaves the coil with of h2-50 kJ/kgda. i an enthalpy a) Find each of the initial and final states the dry and wet temperatures, dew point, relative humidity, humidity ratio, specific volume. b) Imagine a simple transformation to reach a dry temperature of 25°C and a relative humidity of 50%. What is the nature of this transformation? What is the required heat...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT