Condenser Temperature (T) = 30 °C = 303 K

Evaporator Temperature (TE)--20 °C = 253 K

Part A

Calculation of refrigerant effect (RE

Consider Refrigerant medium is ammonia

h_{1}=h_{g}\textup{ at -20}\: \: ^{o}\textup{C}=1437.23\textup{ kJ/Kg}

h4- hf at 30 °C314.769 kJ/Kg

\textup{RE}=\left ( h_{1}-h_{4} \right )

RE = 1437.23-314.769= 1122.461 kJ/Kg

Consider Refrigerant medium is R-12

h_{1}=h_{g}\textup{ at -20}\: \: ^{o}\textup{C}=342.682\textup{ kJ/Kg}

h4- hf at 30 °C228.540 kJ/Kg

\textup{RE}=\left ( h_{1}-h_{4} \right )

\textup{RE}=342.682-228.540=114.142\textup{ kJ/Kg}

Based on the above calculation RE of Ammonia is greater than RE of R-12

\textup{Part B -- calculation of COP}

Consider Refrigerant medium is ammonia

h_{1}=h_{g}\textup{ at -20}\: \: ^{o}\textup{C}=1437.23\textup{ kJ/Kg}

h4- hf at 30 °C314.769 kJ/Kg

h_{2}=h_{g}\textup{ at 30}\: \: ^{o}\textup{C}=1486.14\textup{ kJ/Kg}

\textup{COP}=\frac{h_{1}-h_{4}}{h_{2}-h_{1}}

\textup{COP}=\frac{1437.23-314.769}{1486.14-1437.23}=22.94

Consider Refrigerant medium is R-12

h_{1}=h_{g}\textup{ at -20}\: \: ^{o}\textup{C}=342.682\textup{ kJ/Kg}

h4- hf at 30 °C228.540 kJ/Kg

h_{2}=h_{g}\textup{ at 30}\: \: ^{o}\textup{C}=363.566\textup{ kJ/Kg}

\textup{COP}=\frac{h_{1}-h_{4}}{h_{2}-h_{1}}

\textup{COP}=\frac{342.682-228.540}{363.566-342.682}=5.46

Based on the above calculation COP of Ammonia is greater than COP of R-12

\textup{Part C-- Carnot efficiency}\left ( \eta \right )

Condenser Temperature (T) = 30 °C = 303 K

Evaporator Temperature (TE)--20 °C = 253 K

\textup{Carnot efficiency}\left ( \eta \right )=\frac{T_{C}-T_{E}}{T_{C}}

\textup{Carnot efficiency}\left ( \eta \right )=\frac{303-253}{303}=0.165=16.5 %

\textup{carnot efficiency is same for both cases}

Add a comment
Know the answer?
Add Answer to:
Two refrigeration systems, one using Refrigerant 717 (Ammonia) and the other using Refrigerant 12 (Dichlorodifluoromethane). The...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT