feel free to ask if any doubt regarding the solution and concept thank you
Name: ID# Q.2 A single phase, 100kVA, 1000/100 V transformer is to be tested to determine...
Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.
Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp 322 X,-45 Ω R,-0.05 Ω X,-0.06 Ω The excitation branch impedances are given referred to the high-voltage side of the transformer. (a) Find the equivalent circuit of this transformer referred to the high-voltage side. (b) Assume that this transformer is supplying rated load (20kVA) at 480 V and 0.8 PF lagging. What is this transformer's input voltage? What is its voltage regulation? (c) What is the transformer's...
A three phase power transformer of 100 (KVA), 22 / 12.7 (kV) and Δ-Y has a resistance of 0.15 (pu) and a reactance of 0.6 (pu). The elements of the excitation branch are R_m = 100 (pu) and X_m = 20 (pu) a) If this transformer supplies a load of 80 (KVA) with an FP = 0.8 delay, draw the phasor diagram of one phase of the transformer. b) What is the voltage regulation of the transformer bank in these...
The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...
3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...
SOLVE: In a factory there is a three-phase transformer with the following characteristics: -S = 100 kVA, 22 / 12.7 kV - D-Y - Resistance of 0.15 pu and a reactance of 0.6 pu. -Ram of excitation Rm = 100 pu and Xm = 20 pu. a) If this transformer supplies an 80 kVA load with an FP = 0.8 lag, draw the phasor diagram of one phase of the transformer. b) What is the regulation of the transformer bank...
(a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters and explain how each parameter is determined based on the test results. (b) A 2200/220 V, 15 kVA, single phase transformer has the following equivalent circuit parameters: The HV winding resistance and leakage reactance are 0.2Ω and 0.3Ω respectively. The LV winding resistance and leakage reactance are 0.012Ω and 0.03 Ω respectively. The magnetic circuit resistance and reactance referred to the HV side are...
lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. Determine the approximate equivalent circuit referred to the HV side. b. Find the voltage regulation at full-rated current delivering rated voltage and PF of 0.8 lagging. c. Calculate efficiency of transformer d. Assume that, voltage at HV side is 2000 V. Calculate the voltage at...
Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...
A 2.2KVA 600/120 V, transformer has the following data for its OC test and SC test: OC Test: Voc: 120V Ioc: 0.6A Poc: 16W SC Test Vsc = 12V Isc = 3.67A Psc= 30W (a) Find the equivalent circuit referred to its HV and LV side. (b) If it operating as a step-down transformer, and delivering its rated current at the rated voltage and 0.85 pf lagging, find what will be the input voltage. (c) Find the Voltage regulation of...