Question

20. The voltage and current in an electrical load is given by v(t) = 100 cos(wt + 15°) and i(t) = 2 cos(wt – 15°). The reacti

0 0
Add a comment Improve this question Transcribed image text
Answer #1

- V!= 100 cos lut +150) -> V = 100.150v ilt) = 26s (wt -15°) -) is q l-15° v The reactive power Q = h vi sin 100-0) ES (100)

Add a comment
Know the answer?
Add Answer to:
20. The voltage and current in an electrical load is given by v(t) = 100 cos(wt...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Example 1 The voltage across the load is v(t) = 60 cos(wt - 10°) V and...

    Example 1 The voltage across the load is v(t) = 60 cos(wt - 10°) V and the current through the element in the direction of I voltage drop is i(t) = 1.5 sin(wt + 50°) A. Find a) The complex and apparent powers b) The real and the reactive powers c) The power factor and the load impedance.

  • A balanced three-phase source with a 208 V rms (line-to-line) is delivering power to a balanced...

    A balanced three-phase source with a 208 V rms (line-to-line) is delivering power to a balanced Y-connected load with phase impedance Z1 = 4 + j 3 Ohms in parallel with a balanced delta-connected load with phase impedance Z2 = 7.5 + j 6 Ohms. Calculate the active (real) and reactive (imaginary) powers delivered by the source. Draw the power triangle. What is the power factor of the combined load?

  • A Δ-connected source supplies power to a Y-connected load in a three-phase balanced system. Given that...

    A Δ-connected source supplies power to a Y-connected load in a three-phase balanced system. Given that the line impedance is (1 + j1) Ω per phase while the load impedance is (6 + j4) Ω per phase, find the magnitude of the line voltage at the load. Assume the source phase voltage Vab= 208 ∠0° V rms. The magnitude of the line voltage at the load is _______ Vrms.

  • Given v(t) = 60cos(wt - 10) V and i(t) = 1.5 cos(wt +50)A find a. Complex...

    Given v(t) = 60cos(wt - 10) V and i(t) = 1.5 cos(wt +50)A find a. Complex Power (S) (2 pts.) b. Apparent Power (SI)(1 pts.) C. Real Power (P) (1 pts.) d. Power factor (2 pts.) e. Reactive Power (Q) (1 pts.) f. Impedance (Z) (1 pts.) g. Capacitance (C) ((2 pts.)

  • Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a ...

    Please show how this transformers problem is done. Thanks! Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a balanced three-phase load (it doesn't matter whether the load is Y or Delta connected). The voltage and current of the source are: van (t) - 340 sin (377t + 0.5236) ia(t) 100sin (377t 0.87266) Calculate the following: (a) The rms phase voltage (Van, magnitude and phase). (b) The rms line-to-line voltage (Vab, magnitude and phase) (c) The...

  • 1) In the balanced Y-Y circuit shown below, let Van=990<0° V (rms) and the load impedance...

    1) In the balanced Y-Y circuit shown below, let Van=990<0° V (rms) and the load impedance per phase be Zy=60+j35 2. Find the complex power, apparent power, average power, and reactive power of the load (25 marks) 110 os os

  • A balanced Y-connected voltage source with a phase voltage ?௔௡ = 277∠0°? delivers to a balanced...

    A balanced Y-connected voltage source with a phase voltage ?௔௡ = 277∠0°? delivers to a balanced delta connected load with impedance ?ௗ௘௟௧௔ = 45 − ?18Ω that is in parallel with a Yconnected load with impedance ?௒ = 30 + ?15Ω. (a) Calculate the current at the source (b) Calculate the source real and reactive power

  • can I have the correct solutions, answers are given impedance of (2 + j4)n per phase,...

    can I have the correct solutions, answers are given impedance of (2 + j4)n per phase, feeds two balanced 2.7 A three-phase line, which has an three-phase loads that are connected in parallel. One of the loads is Y-connected with an impedance of (30 + (60 - impedance of j40)N per phase, and the other is A-connected with an j45) per phase. The line is energized at the sending end from a 60-Hz, three-phase, balanced voltage source of 120V3 V...

  • A three-phase line, which has an impedance of (2 + j4) Ω per phase, feeds two...

    A three-phase line, which has an impedance of (2 + j4) Ω per phase, feeds two balanced three-phase loads that are connected in parallel. One of the loads is Y- connected with an impedance of (30 + j40) Ω per phase, and the other is delta- connected with an impedance of (60 + j45) Ω per phase. The line is energized at the sending end from a 60-Hz, three phase, balanced voltage source of 120√3 V (rms, line- to-line). Determine...

  • 9. A three phase balanced Y connected source is supplying three, three phase loads that are...

    9. A three phase balanced Y connected source is supplying three, three phase loads that are connected in parallel. First load is a y connected and has an impedance of 30+j40 ohms. The second load is absorbing a total of 150kVA at 0.5 power factor lagging. The third load is absorbing 150kVA at 0.5 power factor leading. The line to line source rms voltage is 2500V. i Find the load current in each load i) Find the total real and...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT