Please write very clearly.
Determine whether a W12x35 can work if A992 steel is used considering the conditions stated above.
Total load=6.5 kip/ft
Negative moment at support=6.5*6=39 kip-ft
Reaction at support=6.5*(6+18+6)/2=97.5 kips
Positive moment at midspan=97.5*9-(6.5*(6+9)*(6+9)/2)=146.25 kip-ft
Therefore, moment at midspan will govern the design
Moment at midspan due to Dead load=0.5*146.25=73.125 kip-ft
Moment at midspan due to live load=0.5*146.25=73.125 kip-ft
Per LRFD load combination, 1.2D+1.6L,
Design moment=1.2*73.125+1.6*73.125=204.75 kip-ft
Since both flanges are continuosly braced, beam will develop plastic moment capacity
Moment capacity of W12x35=192 kip-ft per Table 3-2 of AISC 360-10,
Since the capacity is less that demand, beam is inadequate
Please write very clearly. Determine whether a W12x35 can work if A992 steel is used considering...
Q3) A simply supported beam is subjected to a uniform service dead load of 2.3 kips/ft (excluding the weight of the beam), a uniform service live load of 3.0 kips/ft. The beam is 30 feet long, and deflection not to exceed L/360. The beam has continuous lateral support, and A992 steel is used. Is a W27 x 84 adequate?
Please refer AISC 15th edition 3. A simply supported beam (W18x97) is 50-ft long and is restrained at the supports and at midspan. It carries a uniform dead load of 0.4 kips/ft plus beam weight, and a live load of 1.0 kips/ft. The steel is A992 and the method of analysis is LRFD. Determine if this shape and length is adequate to support this load. Also determine which controls: flexural strength or deflection. The limiting maximum live load deflection is...
Could you please use 15th edition of AISC Manual for proper solution. 4. Use A992 steel and select the lightest W12-shape for the beam-column shown in the figure below. The member is part of a braced frame, and the axial load and bending moment are based on service loads consisting of 30% dead load and 70% live load (the end shears are not shown) Bending is about the strong axis, and K= Ky=1.0. The frame analysis was performed consistent with...
steel design 2-160 points] A992 steel (F, 50ksi) is used and LRFD method is to be followed. a) Through calculations determine if w14x 38 is compact or not. b) The beam shown below is laterally braced only at the ends. The applied load is a service live load. Through calculations determine if W14x38 is adequate. Note: Shear forces are of no concern. You are not allowed to use the beam design chart included at the end of the exam. 302...
Could you please use AISC steel manual for the parts needed? 15th edition. 4. The beam shown the Figure has lateral support only at the ends. The uniform load is a superimposed dead load, and the concentrated load is a live load. Use A992 steel and select an economical W shape. The live load deflection must not exceed L/360 (you may use the tables of Chapter 3). Also, calculate Fer for the selected W shape 25 k/ft A 15 15"...
The 5.5 in concrete slab (150 pcf density) is to be supported by W12X30 A992, Grade 50 simply supported steel beams spaced at 8ft c/c. The slab is spanning 20ft. The live load is 100psf. Using the LRFD and ASD procedures, check the adequacy of the beam if:(3) The beam upper flange is fully supported by the slab (4) The beam lateral bracing at the ends only (Cb=1.0) Determine the beam shear capacity and check the beam deflection for a...
2. Design Wide flange column section only of A992 steel to serve as a pinned- end main member column 30 ft long to carry an axial compression loads in a braced structure, based on AISC LRFD method. The dead load is 50 kips A992 13-0" and live load is 70 kips. The member has strong axis direction supported at 17ft height from the bottom of the column. Dead load is 20 kips and live load is 40 kips. Assume the...
Given w 14 x 145, A992 Grade 50 (Fy = 50 ksi) steel shape is used for column AC in Fig.1. Service load P = 1,000 kips (70% dead load and 30% live load). Required: Is the column safe, based on LRFD?
Please refer AISC 15th edition 2. Select the lightest W shape to carry a uniformly distributed dead load of 0.5 kips/ft and a live load of 1.0 kips/ft on a simply supported span of 42 ft. Adequate lateral support is provided. The live load deflection is limited to 360, Use A572 Grade 50 steel and LRFD. (credit weight 30)
Name beam shown in Figure is a W16 x 31 of A36 steel. It supports a reinforced concrete floor slab that provides continuous lateral support of the compression flange The service dead load is 450 lb/ft. This load is superimposed on the beam: it does n include the weight of the beam itself. The service live load is 550 lb/ft. Does this bean have adequate moment strength? (25 430 550