Question

What application for heat exchanger that use cold fluid in shell side and hot fluid in...

What application for heat exchanger that use cold fluid in shell side and hot fluid in tube, and also what application that use hot fluid in shell side and cold fluid in tube side, and what is the reason?
0 0
Add a comment Improve this question Transcribed image text
Answer #1

A condensing fluid most often goes on the shell side but the choice demands careful evaluation. If the shell-side velocity is low enough, the vapor and liquid can separate inside the exchanger. The liquid dropping out makes the vapor leaner, reducing the temperature required to get more liquid to condense from the remaining vapor.

A viscous fluid on the tube side tends to have high pressure drop and low heat transfer. That favors shell-side allocation. However, high pressure drop on the shell side can prompt significant flow bypassing around baffles, reducing heat transfer.

Because a vapor normally has a higher volume and lower heat transfer coefficient than a liquid, allocate it to the shell side. This reduces pressure drop for a given volume and typically provides a higher heat-transfer coefficient.

Add a comment
Know the answer?
Add Answer to:
What application for heat exchanger that use cold fluid in shell side and hot fluid in...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • why is the hot fluid often put on the tube side rather than the shell side?...

    why is the hot fluid often put on the tube side rather than the shell side? Is there any reason you may want to pass a cold fluid through the tubes rather than the shell? (This is a shell and tube heat exchanger question)

  • 1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold strea...

    1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold stream Hot stream Crude Oil Fluid Cooling water Tube side Stream allocation Shell side Mass flow rate (kg/s) 110 30 Inlet temperature (C) 90 Outlet temperature (C) Heat capacity (J/kg K) Density (kg/m2) Viscosity (Pa-s) Thermal conductivity (W/m-K) Fouling factor (m2 CW) 40 50 2177 4187 787 995 0.72-10 1.89-103 0.122 0.59 0.0002 0.0004 The shell and tube heat exchanger has the following...

  • 1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold strea...

    1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold stream Hot stream Crude Oil Fluid Cooling water Tube side Stream allocation Shell side Mass flow rate (kg/s) 110 30 Inlet temperature (C) 90 Outlet temperature (C) Heat capacity (J/kg K) Density (kg/m2) Viscosity (Pa-s) Thermal conductivity (W/m-K) Fouling factor (m2 CW) 40 50 2177 4187 787 995 0.72-10 1.89-103 0.122 0.59 0.0002 0.0004 The shell and tube heat exchanger has the following...

  • Determine the effectiveness of the concentric tube heat exchanger. The working fluid through the heat exchanger...

    Determine the effectiveness of the concentric tube heat exchanger. The working fluid through the heat exchanger is water and is flowing at 1 m/min for both cold and hot pipes. The hot water temperature at the tube inlet is 90°C and the temperature at the tube outlet is 60°C. The cold water temperature at the tube inlet is 50°C and the temperature at the tube outlet is 80°C. Assume the density and the specific heat of water are 988.1 kg/m3...

  • 11.20 Heat exchanger of counter flow arrangement with temperatures at inlet of hot and cold fluids...

    11.20 Heat exchanger of counter flow arrangement with temperatures at inlet of hot and cold fluids are (200°C) and (60°C) gave outlet temperature of (110°C) for both sides as the surfaces were clean. After long time of use for same the inlet temperatures and flow rate, the hot fluid outlet was (130°C). Find the change in the overall heat transfer coefficient and the heat transfer values by percentage. Ans.: -37.4%, -22.2% 11.21 A liquid with a specific heat of (3200J/kg....

  • Hot air enters a heat exchanger at 350°C and exits at (149°C. The heat extracted is...

    Hot air enters a heat exchanger at 350°C and exits at (149°C. The heat extracted is used to boil (0.263) kg/s of 100°C water (from saturated liquid to saturated steam). The heat exchanger is a single-shell shell-and-tube heat exchanger with two tube passes. The overall heat transfer coefficient for the hot side is 240 W/(m2°C). Assume a constant specific heat for air of Cp = 1.005 kJ/(kgC). The pressure of the hot air and the boiling water is P =...

  • Question Completion Status: [CLO-4) Consider the 2-shell pass and 4-tube passes heat exchanger shown in the...

    Question Completion Status: [CLO-4) Consider the 2-shell pass and 4-tube passes heat exchanger shown in the fure, cold water enters the tube at 10 °C and leaves at 70°C. Hotoletters the shell. The mass flow rate of water is 5 kg/s and of oil is 20 kg/s. if needed, you may take the specific heat Cp of liquid water to be 4.18 kuand of the oil is 20 kk.. Shell-side fluid Out Tube Image 016-new.pdf side fluid le Our The...

  • 2) Hot air enters a heat exchanger at 350°C and exits at 153°C. The heat extracted...

    2) Hot air enters a heat exchanger at 350°C and exits at 153°C. The heat extracted is used to boil 0.277 kg/s of 100°C water (from saturated liquid to saturated steam). The heat exchanger is a single-shell shell-and-tube heat exchanger with two tube passes. The overall heat transfer coefficient for the hot side is 240 W/(m2). Assume a constant specific heat for air of cp = 1.005 kJ/(kg°C). The pressure of the hot air and the boiling water is P...

  • 2) Hot air enters a heat exchanger at 350°C and exits at 155°C. The heat extracted...

    2) Hot air enters a heat exchanger at 350°C and exits at 155°C. The heat extracted is used to boil 0.283 kg/s of 100°C water (from saturated liquid to saturated steam). The heat exchanger is a single-shell shell-and-tube heat exchanger with two tube passes. The overall heat transfer coefficient for the hot side is 240 W/(m²°C). Assume a constant specific heat for air of Cp = 1.005 kJ/(kg °C). The pressure of the hot air and the boiling water is...

  • Hot and cold water streams exchange heat in a double pipe heat exchanger in counter current...

    Hot and cold water streams exchange heat in a double pipe heat exchanger in counter current flow. The pipes are 3 ft long. The inside pipe is a 5/8 inch BWG 12 copper tube. The outside pipe is a 1 inch Sch 40 steel pipe. The outside pipe is insulated to minimize heat loss to the surroundings. The hot water enters the inside tube at 180F with a flow rate such that Re = 10000 The cold water flows through...