Question

15 (c) Consider the single-line diagram of the power system shown in Figure. Neglect all resistances, transformer phase shift

0 0
Add a comment Improve this question Transcribed image text
Answer #1

(111) Three b fault at bugs. by positive sequence dagram For Ren. 0.46 + arross 0.35 La 0.211 2 By Strmetry, Folding 0.281 0

Add a comment
Know the answer?
Add Answer to:
15 (c) Consider the single-line diagram of the power system shown in Figure. Neglect all resistances,...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 2. A single-line diagram of the power system considered is shown in Figure P2a, where negative-...

    2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...

  • QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where...

    QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where negative and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance X.=0.05 per unit on the motor base. Prefault voltage is VF1.05<Oº per unit whereas prefault load current is zero. Take A-Y transformer phase shifts into consideration. M Line tool X, - X2 - 200 100 MVA X =...

  • A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y...

    A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...

  • 03 Consider the following one line diagram. The generator is rated at 25 MVA, IN has...

    03 Consider the following one line diagram. The generator is rated at 25 MVA, IN has subtransient reactance of 20 %. The transmission line has a reactance of 10 The subtransient reactance of motorlis 0.345 pu where is that ol second more pu. Each motor has the following ratings. 10 MVA and 11 kV. Both transformers are rated at 25 MVA and have a reactance of 8.05% each; the transformers 1 and 2 have voltage ratio of 11/121 KV and...

  • the single-line diagram of a three-phase power system is shown in figure 9.17. equipment ratings are...

    the single-line diagram of a three-phase power system is shown in figure 9.17. equipment ratings are given as follows: The inductor connected to Generator 3 neutral has a reactance of 0.05 per unit using generator 3 ratings as a base. Draw the zero-, positive-, and negative-sequence reactance diagrams using a 1000-MVA, 765-kV base in the zone of line 1-2. Neglect the Δ—Y. transformer phase shifts.

  • Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in...

    Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u. a- Find the fault current due to a bolted- three-phase short circuit at bus 3. [10 points] b- Find the fault current supplied by each generator and the voltage at each of the buses 1 and 2 under fault conditions. [10 points] 0.1 p.u 0.06 ?.u. 0.25 p.11....

  • Consider the system Shown in the single-line diagram of Figure 4. The required sequence reactances in per unit to the same base are as follows.

    Consider the system shown in the single-line diagram of Figure 4. The required sequence reactances in per unit to the same base are as follows: G1 X1 = X2 = 0.12  G2 X1 = X2 = 0.24  G3 X1 = X2 = 0.12  Transformers X11=X12= 0.12  Lines: Positive and X13=X12= 0.20 Negative Sequence  a. Draw the positive-, and negative- sequence reactance diagrams. [6 Points]  b- Determine the The'venin's equivalent of each sequence network as viewed from a fault in the...

  • Power system operation and control

    The positive-sequence reactances for the power system shown in Figure 10.31 are in per unit on a common MVA base. Resistances are neglected and the negative-sequence impedances are assumed to be the same as the positive-sequence impedances. A bolted line-to-line fault occurs between phases b and c at bus 2.Before the fault occurrence, all bus voltages are 1.0 per unit. Obtain the positive-sequence bus impedance matrix.Find the fault current, the three-phase bus voltages during fault, and the line currents in...

  • Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown...

    Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown in Figure 1. The single line diagram shows a synchronous generator G connected to a large 50 Hz grid via its unit transformer T and a network of three transmission lines. Relevant details of the grid, transformer, generator and overhead lines are provided in Tables I,II,II & IV respectively. A double line to ground fault occurs at bus 3 Questions....

  • The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows

    The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence  reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT