Question

Consider the office building shown below. The building is located in New Orleans, LA, at ground level near the coast. The str

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Dead load from slab=Ws=70 lb/ft? Self weight of beam=Wb=45 lb/ft Self weight of columns=Wc=70 lb/ft Live load W1=30 lb/ft? Fl

12.5 12.5 ...... 3@ 30 ft = 90 ft an 12.5 12.5 D4E 15 4@25 ft = 100 ft Plan View

Tributary area for column 1)B3 and C3 AT=(15+15)*(12.5+12.5)=750 ft? Length of beam =(12.5+12.5+15+15)=55 ft 2)D4 Ar=15*(12.5

Since the load on each storey and storey height are same let us analyze a typical storey first

TYPICAL STOREY(along B3,C3) DEAD LOAD OF SLAB SELF WEIGHT OF BEAM SELF WEGHT OF COLUMN TOTAL DEAD LOAD 750X70 52500 45+55 247

Total load at bottom of column =No stories above* typical load for storey A) D4 -First floor(have 5 stories above) 1) Dead lo

Add a comment
Know the answer?
Add Answer to:
Consider the office building shown below. The building is located in New Orleans, LA, at ground...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Assignment #1 A three-story office building, determine the total dead & live loads by columns A1...

    Assignment #1 A three-story office building, determine the total dead & live loads by columns A1 and C3 and beams. The precast exterior wall supported by the perimeter beams weighs 600 lb/ft. The floor system consists of a 6 in-thick reinforced concrete slab. 25 5-0 BEAM -0 12 14 Beam 12" Column Framing Plan

  • is the second floor of a four-story building. a flat Consider the floor framing plan shown...

    is the second floor of a four-story building. a flat Consider the floor framing plan shown below. Thi The design floor live load is 90 psf. The design roof live load is 20 psf. The structure has roof G1 G4 /2 G2 GS 2o G3 FLOOR FRAMING PLAN Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The...

  • 4. A two story office building has interior columns spaced 25 ft apart in two perpendicular...

    4. A two story office building has interior columns spaced 25 ft apart in two perpendicular directions. The columns are fixed at the roof, the second floor and the ground floor in both directions. Consider the dead load (4 inch-thick reinforced concrete slab at the roof and 6 inch thick reinforced concrete slab at the floor) as well as appropriate live load. Ignore other dead weight other than shown. Determine the following using A992 steel: (20 points) 1) Dead load...

  • Question 4 5 pts The building has beams along building lines A through E and one-way slabs spanning between building li...

    Question 4 5 pts The building has beams along building lines A through E and one-way slabs spanning between building lines A through E. A central stalrwell/elevator shaft between bulding lines 5 and 6 provides the lateral support, so only gravity loads need to be calculated The building is used for general affice space. The slab is 8 in. thick. The beams are 12 in. wide and have a total depth of 18 in., the bay dimensions are 18.5 ft...

  • REINFORCED CONCRETE DESIGN CLASS PROJECT The structural floor plan of a three-story (ground floor, two suspended...

    REINFORCED CONCRETE DESIGN CLASS PROJECT The structural floor plan of a three-story (ground floor, two suspended floors, and a roof office building is shown on the next page. The floor includes one and two way solid slabs. The new building will be located in Sharjah, UAE. The floor systems consist of one-way and two-way solid slabs supported by beams running in both directions as shown in the floor plan. The design loads for the floor (in addition to the self-weight)...

  • 2. A roof plan for a small building is shown below. The roof is composed of...

    2. A roof plan for a small building is shown below. The roof is composed of joists which frame beams or girders, which frame into into columns A, B, C, and D. The joists support a dead load 200 lb/ft2 and live load - 500 lb,/ft?. In Area ABEF there are 4 joists evenly spaced at 6 ft O.C. In Area FGHD there are 3 joists evenly spaced at 5 ft OC. Joists 5 ft 15 ft typ. typ. 6...

  • *please solve ALL questions Assume that the floor between Beams B7 and B8 is supported directly...

    *please solve ALL questions Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The floor slab consists of a 4-in.-thick, normal-weight, reinforced concrete slab (unit weight = 150 pcf). An additional floor dead load of 15 psf is specified to account for the weight of suspended utilities and fixtures. As an exterior beam, B7 must also support one...

  • A six-storey office building consists of a basement, ground floor (1t floor), five upper floor levels...

    A six-storey office building consists of a basement, ground floor (1t floor), five upper floor levels (levels 2 through 6), and a roof. The typical layout of the floor system is shown below, in which each floor girder spans 6 m and floor joists span 4 m. The total plan area of the building is therefore 12 m x 8 m. The roofsystem is similar to the floor system. All of the floors support a uniformly distributed dead load of...

  • The plan view of a typical floor of a four-story heavy storage facility is shown below. The floor and roof live load is...

    The plan view of a typical floor of a four-story heavy storage facility is shown below. The floor and roof live load is 250 psf, and the dead load on all foors and the roof consists of the structure self-weight plus 10 psf for utilities. W 12:96 beams are spaced at 12 ft; w 18x106 reinforced one-way concrete floor/roof slab is 8" thick, each story is 12' high, and the reinforced concrete columns have a 14" x 14" cross-section girders...

  • Problem #2 (33%) Design the T-beam for the floor system shown below. The floor has a...

    Problem #2 (33%) Design the T-beam for the floor system shown below. The floor has a 4-in. slab suspoted by 22-ft-span-length beams cast monolithically with the slab. Beams are 8 ft- 0 in. on center and have a web width of 12 22 in.; fe' 3000 psi in. and a total depth and fy 60,000 psi. Service loads are 0.125- ksf live load and 0.200-ksf dead load. The given dead load does not include the weight of the floor system....