Question

A 1.8km distribution line has an impedance of 0.28 +j0.5 ohms/km. other information of this power...

A 1.8km distribution line has an impedance of 0.28 +j0.5 ohms/km. other information of this power system are:

Load factor =0.65 ; Load voltage =2.2kV

Empirical constant for estimating power losses of line =0.15

All loads are connected at the end of the line and are balanced

Line current at peak load = 850A; Power factor at peak load =0.76

Electricity energy charge is $0.25/kWh; there is no demand charge

Reactive power surcharge of $0.008/kVarh in excess of 62% of kWh consumption applies to consumers

a) Calculate the average demand in KW

B) Calculate the average power losses in the line.

c)How much can the utility save in $ per year if the power factor at peak load is corrected from 0.76 to 0.9? Assume the load factor remains unchanged.

Help A,B,C

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
A 1.8km distribution line has an impedance of 0.28 +j0.5 ohms/km. other information of this power...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • 1) Figure- generator is producing a line voltage of 480 V, and the line impedance is...

    1) Figure- generator is producing a line voltage of 480 V, and the line impedance is 0.09 + j0.16 . Load 1 is Y connected, with a phase impedance of 2.5236.87° 0 and load 2 is A connected, with a phase impedance of 54-20° n. shows a three-phase power system with two loads. The A-connected 2 0.09 j0.16 n w Vca= 4802-240° V + Vab = 48020 V Vhc = 480-120° V 0.09 j0.16 0.09 j0.16 Load 1 Load 2...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...

  • The load data for a primary feeder of a power company for a typical winter day...

    The load data for a primary feeder of a power company for a typical winter day are as follows Street Lighting 1 AM to 6 AM 500 kW 7 AM 300 kW 8 AM to 5 PM 0 kW 6 PM 200 kW 7 PM 300 kW 8 PMto 12 AM 500 kW Residential Load 1 AM to 5 AM 100 kW 6 AM 250 kW 7 AM to 8 AM 400 kW 9 AM 300 kW 10 AM to...

  • Can you help me calculating this question? Thank you. (6) The following table shows the readings of the kWh meter of a...

    Can you help me calculating this question? Thank you. (6) The following table shows the readings of the kWh meter of a factory for 8 hours. The ratings of all of the loads in the factory total to 1000 kVA at 0.85 lagging power factor. Time Meter reading (k Wh) Time Meter reading (kWh) 00:30 100 04:30 1850 01:00 210 05:00 2200 01:30 310 05:30 2530 02:00 1450 06:00 2850 02:30 620 06:30 3130 03:00 850 07:00 3350 03:30 11...

  • #1, A 3-phase, 60-Hz transmission line is 50 km long and has r -o20 Ohms/km and...

    #1, A 3-phase, 60-Hz transmission line is 50 km long and has r -o20 Ohms/km and x-0.50 Ohms/km. The load at the receiving end of the line is 2.5 Mw at a power factor of 0.9 leading. (i)Compute the impedance of the line, Zline * at the lad tole, the lad wi e . (ii)Find the sending end current, I, as 33nv lhe to tine Van-eerene (ii) What is the sending end voltage, V,? (iv)What is the real power, P...

  • Question: A three-phase line has an impedance of 1 + j2 Ω per phase. The line...

    Question: A three-phase line has an impedance of 1 + j2 Ω per phase. The line feeds two balanced three-phase loads that are connected in parallel. The first load is Y-connected and has an impedance of 20+j40 Ω per phase. The second load is ∆-connected and has an impedance of 30-j60 Ω per phase. The line-to-line voltage at the load end of the line is 415V. Taking the phase voltage Va as reference, determine: a) The total current per phase...

  • VO) L1 L2 Line VO LI Power Calculations Learning Goal: In this tutorial, you will practice...

    VO) L1 L2 Line VO LI Power Calculations Learning Goal: In this tutorial, you will practice the calculation of power in circuits containing loads, including the effects of non-ideal transmission lines, and practice how to improve the power factor for an entire system. Many appliances (eg., hair dryers, coffee makers, and refrigerators) and industrial loads are powered by AC sources. The ability to be able to calculate their power needs is important in a number of situations. Before completing this...

  • A three-phase transmission line is 200 km long. lt has a total series impedance of 25+j110)Ω...

    A three-phase transmission line is 200 km long. lt has a total series impedance of 25+j110)Ω Per Phase and a total shunt admittance ofj5x 10 Ω. It delivers 180 MW at 275 kV and 0.8 power factor lagging to a load connected at the receiving end. Using the medium π model of the line, determine the voltage, current, real power, reactive power and power factor at the sending end of the line.

  • Three loads are connected in parallel across a V. = 345 Z0° V (rms) line and...

    Three loads are connected in parallel across a V. = 345 Z0° V (rms) line and fed from a line having a series impedance 0.2 + 0.05 12, as shown in (Figure 1). Load 1 absorbs 3 kW at unity power factor; Load 2 absorbs 5 kVA at 0.8 leading; Load 3 absorbs 5 kW and delivers 6 kVAR. Part A Calculate the rms value of the voltage (V3) at the sending end of the line. Figure ① 1 of...