Question

A 3-j semi-controlled bridge rectifier is fed from a delta-star transformer 66 kVA, 60 Hz, 13800...

A 3-j semi-controlled bridge rectifier is fed from a delta-star transformer 66 kVA, 60 Hz, 13800 V/? (the secondary voltage is unknown). The load of the rectifier is highly inductive. The following measurements at a specified firing angle have been recorded:
Ith RMS
70.71 A
I line RMS (transformer secondary)
76.40 A
Draw the complete circuit diagram and calculate;
i. Load current Io.
ii. Firing angle α.
iii. Transformer secondary line voltage (RMS).
iiii. Average output voltage (at the calculated firing angle in (ii)).
v. Load resistance R.
vi. Draw, to scale, vAKT2, vo, and transformer secondary phase “c” current.
0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
A 3-j semi-controlled bridge rectifier is fed from a delta-star transformer 66 kVA, 60 Hz, 13800...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 3-j semi-controlled bridge rectifier is fed from a delta-star transformer 66 kVA, 60 Hz, 13800 ...

    A 3-j semi-controlled bridge rectifier is fed from a delta-star transformer 66 kVA, 60 Hz, 13800 V/? (the secondary voltage is unknown). The load of the rectifier is highly inductive. The following measurements at a specified firing angle have been recorded: Ith RMS 70.71 A I line RMS (transformer secondary) 76.40 A Draw the complete circuit diagram and calculate; i. Load current Io. ii. Firing angle α. iii. Transformer secondary line voltage (RMS). iiii. Average output voltage (at the calculated...

  • The three-phase bridge rectifier is designed to produce 650kV of the output voltage from 450 kv/s5o kv, 50 Hz of the tr...

    The three-phase bridge rectifier is designed to produce 650kV of the output voltage from 450 kv/s5o kv, 50 Hz of the transmission transformer. Then c) determine; The firing angle α required for the rectifier's valve if no commutation ./i/ angle is involved. The new necessary line secondary voltage of the transformer, if a- and u 60 are being applied. If the new transformer reactance is 2.8 H, determine the load DC current of this rectifier (consider the firing angle same...

  • i want the answer with detales Single-Phase Controlled Rectifier Exercise Derive the expressions of the average...

    i want the answer with detales Single-Phase Controlled Rectifier Exercise Derive the expressions of the average load voltage and current in single-phase half-wave controlled rectifiers and resistive load. Draw the waveforms of supply voltage. output voltage, output current, thyristor voltage and thyristor current Exercise In a single-phase half-wave controlled rectifier and resistive kad, it is desired to get an average load voltage of 80 V. Determine the firing angle if the ac supply voltage is 230 V. If the load...

  • can you calculate and explain why? thanks A single-phase thyristor rectifier as 50 Hz source. The...

    can you calculate and explain why? thanks A single-phase thyristor rectifier as 50 Hz source. The rectifier delivers a DC voltage of 150 V to a highly inductive depicted in Figure 1 is fed from a 220 V rms, 1. load with a resistive value of 10 Q. SCR, T SCR2 + is Vo SCR3 SCR T Figure 1 (a) for a delay angle component indicating its phase shift with respect to the input voltage v, Sketch the net rectifier...

  • 1. A star connected secondary of a 60 Hz 3-phase transformer, as shown in Fig. 3, is supplying a ...

    1. A star connected secondary of a 60 Hz 3-phase transformer, as shown in Fig. 3, is supplying a 3-phase HW uncontrolled rectifier loaded with a pure 10 Ω resistor. The fuse Fy is open circuit. L. Determine the conduction periods of the diodes ii Draw the waveform of the output voltage. F1 D D and D in msec. phase A iii. Calculate the secondary line voltage if the average iv. Draw the waveforms of the supply currents i, and...

  • 4.70 A full-wave bridge-rectifier circuit with a 500-22 load operates from a 120-V (rms) 60-Hz household...

    4.70 A full-wave bridge-rectifier circuit with a 500-22 load operates from a 120-V (rms) 60-Hz household supply through a 6-to-1 step-down transformer having a single Secondary winding. It uses four diodes, each of which can be modeled to have a 0.7-V drop for any current. What is the peak value of the rectified voltage across the load? For what fraction of a cycle does each diode conduct? What is the average voltage across the load? What is the average current...

  • 4.41 Consider ạ 25 kVA, 240°/240 V, 60 Hz transformer with Z,-2.533 +J2.995 Ω and Z, = (2.5333 + ...

    4.41 Consider ạ 25 kVA, 240°/240 V, 60 Hz transformer with Z,-2.533 +J2.995 Ω and Z, = (2.5333 + )2.995) 10-2 S2, referred to the primary and secondary sides, respectively. b) The transformer is connected at the receiving end of a feeder that has an impedance of 0.3 +j 1.8 Ω. Let the sending end-voltage magnitude of the feeder be 2400 V. Also there is a load connected to the secondary side of the transformer that draws rated current from...

  • Design a FULL WAVE BRIDGE RECTIFIER circuit that will: Take 120volts ac, 60 hz, sinusoidal waveform...

    Design a FULL WAVE BRIDGE RECTIFIER circuit that will: Take 120volts ac, 60 hz, sinusoidal waveform and convert it to a “regulated “dc value giving 12 volts +, - 1 volt across a 2000-ohm output load resistor with no more than 2% ripple voltage. You may assume: a. An ideal power transformer as discussed in class. b. For hand computations, you must assume a diode given by Figure 4.8 page 185. c. A filter capacitor sized per the textbook equation...

  • 3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2...

    3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2 and Xeais 0.0433 12. The transformer is operating in the step-down mode and is delivering rated current at rated voltage to a 0.840 power-factor lagging load. Determine (a) the no- load voltage; (b) the actual input voltage at the high side; (c) the high-side current; (d) the input impedance; (e) the voltage regulation; the voltage regulation if the power factor of the load is...

  • Problem 3 A 50-Hz transformer is operated from a 60 Hz supply. Assume that the load...

    Problem 3 A 50-Hz transformer is operated from a 60 Hz supply. Assume that the load does not change. Discuss the corresponding effects on its flux, reactive power requirements, losses, and efficiency. а- [5 Points] A 50-kVA, 2400/240 V, 60-Hz, single-phase distribution transformer has the following equivalent circuit parameters referred to the high-voltage side Xea 3.0 Req= 0.5 Xm 4,500 S2 Use the equivalent Cantilever model circuit shown in Figure (1). Assume that the load on the secondary of the...