According to the NEC Table 220.55, what would the demand load be for two 14 kW ranges?
According to NEC Table 220.55 ==>
Demand load for 2, 12 kW range = D2,12 = 11 kW (See column - C)
Therefore, Demand load for 2, 14 kW range = (1+0.05*(14-12))*D2,12 = (1+0.10)*11 = 1.1*11 = 12.1 kW ==> ANSWER
According to the NEC Table 220.55, what would the demand load be for two 14 kW...
According to NEC Table 220.55, what would the demand load be for two ranges - one 14 kW and one 16 kW?
According to the NEC, what article would typically be used to calculate the 50 amps circuit breaker
What is the feeder neutral load for two 4.4-kW wall ovens and one 8-kW counter-mounted cooking unit in the kitchen of a one-family dwelling? a. 16.8 kW b. 9.24 kW c. 5.04 kW d. 6.47 kW
Two shunt generators running in parallel share a load of 100 kW equally at a terminal voltage of 230 V. On no-load, their voltages rise to 240 V and 245 V respectively. Assuming that their volt-ampere characteristics are rectilinear, find how would they share the load when the total current is reduced to half its original value? Also, find the new terminal voltage. Answers: 20 kW 30 kW and 236V. Complete solution please.
For the following problems assume the cost of electrical demand is $14 /kW-mo, the cost of electrical energy is $0.02/kWh and the power factor charge is $0.60/kVAr-month 3) The measured current, voltage and power factor of a premium-efficient, three- phase, 125-hp air compressor motor are shown in the table below. Assume motor is 95.3% efficient at all loads. Loaded 127 476 92 Unloaded 63 476 .81 Current (Amps) Voltage (Volts) Power Factor (kw/kvA) A) Calculate the power draw of the...
ELECTRIC SYSTEM DESIGNEo TEST NAME ID# pute the dermand load for a 12 kW cooktop and two okW ovens for dwelting umit 2) Compute the load in a dwelling unit for the following Heating unit system totaling 8 0 kW A/C units: 1-24,000 btu, 2-15.000 btu (assurme 0000 btu -1300 VA) tandard calculation method, determine the demand load for the gencral lightm load of a 3500 sq ft dwelling unit shown in the figure ?- Rt(Tr tArt t irmrt. ??,.tv
What is the current flow in the line supplying a three-phase load of 2 kW at 208-V three phase? (Assuming the load is 100% resistance.) a. None of these b. 7kW c. 6.25A d. 6 kW e. 5.55A
What pH would be neutral if Kw = 6.40 x 10-14? Please show all work. Thanks!
Two 25A thyristors are connected in parallel to switch a 25 kW heater load. The ratings of the heater and the on-state characteristic for the two thyristors are as follows; Power: 25 kW Element resistance: 12 Ω Rated Voltage: 600 V
Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...