Question 1: Consider a 3 phase hydropower generator feeding power into the grid bus, which is held at line voltage of 26kV. The internal reactance is 0.8pu for a rated power of 30MVA. (a) Choose...
Question 5 (Svnchronous machines) a. A synchronous generator connected to an infinite grid has its frequency and terminal b. A six-pole, Y-connected three-phase synchronous machine rated 208 V (line-to- voltage fixed. What is the effect of increasing the excitation current in this case? line), 5500 VA has a synchronous reactance of 8 2 per phase at rated terminal voltage. It is operating as a generator connected to an infinite grid Determine the excitation voltage and the power angle if the...
A 3-phase, 1000-MVA, \(20-\mathrm{kV}, 60-\mathrm{Hz}\) synchronous generator is connected to an infinite bus as shown below. All impedances are given in pu values. The generator delivers \(0.9\) pu power at unity power factor to the infinite bus whose voltage is at 1 pu.If phase 'A' of circuit 2 (CCT 2) between buses H1 and H2 is suddenly opened at point ' \(\mathrm{F}\) ' near bus H1 due to the opening of a circuit breaker, determine:(a) [10 marks] The internal voltage...
please show steps. Thank you. (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utility) bus to deliver power to a 2000 kw plant load at 0.866 lagging power factor. The synchronous generator is wye-connected and rated 3750 kva, 13.2 kv, and 0.8 power factor lagging with 1.0 per unit synchronous reactance and negligible armature resistance. 13.2 kVI 60 Hz I infinite bus utility) rated: 3750 kva 0.8 lag load: 2000 kW...
Problem #2: A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (5), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained...
Problem 2. A 3-phase star-connected turbo-generator feeds power to 11 kV infinite bus, through two parallel transmission lines each having a reactance of452. The generator synchronous reactance is 3 Ω. (a) The mechanical input to alternator and its excitation are adjusted as that the operating power factor at alternator terminals is unity and rated current of 500 A is delivered. Calculate the alternator terminal and excitation voltages. Also determine the active and reactive powers delivered to the infinite bus. (b)...
Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the generator side. The rated line-to-line terminal voltage of the generator (BUS 1) is 38 kV. A single-circuit three-phase transposed overhead line composed by one ACSR Partridge conductor per phase with vertical configuration. The transmission line length is 50 km and the distance between phases a-b, b-c...
The six-bus system shown in Figure 1 will be simulated using MATLAB. Transmission line data and bus data are given in Tables 1 and 2 respectively. The transmission line data are calculated on 100 MVA base and 230 (line-to-line) kV base for generator. Tasks: 1. Determine the network admittance matrix Y 2. Find the load flow solution using Gauss-Seidel/Newton Raphson method until first iteration by manual calculation. Use Maltab software to solve power flow problem using Gauss-Seidel method. Find the...
I need help to solve this questions about Generator Governor Droop and Transmission Line. A complete solutions with answers would be great. Thank you Generation Question 1 to 5 relate to the following grid connected generator. A governor-controlled, steam-driven 450 MW synchronous generator with 5% droop is synchronized to the 60 Hz grid and its load set-point adjusted to deliver 300 MW to the grid. Q1. (a) 000 What is the actual droop of the generating unit? 0.0225 Hz/MW (b)...
solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...