A)Take base MVA=20, Base KVA=20. As all the elements are rated to base levels, there will be no change in per unit impedance values. So take x'=j0.15 p.u, t/f x=j0.1p.u and Z=j0.1 p.u. Now E is given by. E=V+I(x'+x+z). Where I= (p/v cos), given v &cos =1 and given power p= 10MW , So P.u power delivered P=10/20= 0.5. So I=0.5. Now E=1+0.5(j0.15+j0.1+j0.1), on solving we get E=1.0159.926. B) If fault occur on 4th bus , the network looks like star connected network. So use star- delta rule, the effective x between E & V given by Xeff= j0.25+j0.1+(j0.25*j0.1)/j0.1 =j0.6. So we know power angle equation P=( EVsin)/Xeff . so [P =1.69sin]
PLEASE COMPLETE ALL PARTS AND SHOW ALL WORK. 6. Consider the system shown below. The generator...
2. nBase MVA 100p LI Base KV G1 20kV Base KV Lines 220kv G13 phase 20 kv, 100 MVA Xd-1, Xd-0.3, Xd"-0.2, Xo-0.8 H-1s T1 3 phase 100 MVA20kv -220kv, DY,X-0.1 L1, L2 Ro X1-0.2 pu on given base Y ignored L2 The infinite bus voltage is 1 PU The generator supplies 0.6 pu real power at 0.8 pf lagging to the infinite bus a. Sketch an impedance diagram appropriate for transient stability analysis b. Calculate the internal transient voltage...
A 3-phase, 1000-MVA, \(20-\mathrm{kV}, 60-\mathrm{Hz}\) synchronous generator is connected to an infinite bus as shown below. All impedances are given in pu values. The generator delivers \(0.9\) pu power at unity power factor to the infinite bus whose voltage is at 1 pu.If phase 'A' of circuit 2 (CCT 2) between buses H1 and H2 is suddenly opened at point ' \(\mathrm{F}\) ' near bus H1 due to the opening of a circuit breaker, determine:(a) [10 marks] The internal voltage...
Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the generator side. The rated line-to-line terminal voltage of the generator (BUS 1) is 38 kV. A single-circuit three-phase transposed overhead line composed by one ACSR Partridge conductor per phase with vertical configuration. The transmission line length is 50 km and the distance between phases a-b, b-c...
The component parameters for the power system shown in Figure 2 are given in Table 1. The pre-fault voltage is 120° pu and Zx-j0.1 pu. Table 1 Ratings X2-Xi (pu)Xo (pu) 0.05 0.10 0.20 0.20 Components G1, G2 200 MVA, 20 kV 0.10 0.10 0.10 0.10 T1, T2, T3200 MVA, 20/200 kV L1 200 MVA, 200 kV し2 200 MVA, 20 kV (a) Draw the three sequence networks and determine the per-unit Thevenin impedance of each sequence network seen from...
Problem 2 (50 points): The generator in the figure generates and delivers 150 MW to the power system below. At steady state the generator regulates the generating station voltage (bus 1) to pu. The system voltage at bus 3 is 1.05 pu. 1. Compute the internal voltage and rotor angle of the generator under the above conditions. 2. The fault sequence for a solid three-phase fault on any of the line circuits consists of a delayed tripping of both circuit...
3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and its internal (excitation) voltage is adjusted to 1.2 PU. The generator is connected to a 19 kV (line) infinite-bus. If the voltage angle (d) between the infinite-bus and the generator internal voltage is 20°, calculate, The generator active power output. The generator line current. Draw the phasor diagram for one phase.
A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...
can you calculating this question and explain why? thanks The ratings and sequence reactances of the components for the power system shown in Figure 2 are given in Table 1. The pre-fault voltage is 1/0° per unit (pu). Bus 8 L3 Bus 1 T1 Bus 4 T2 Bus 2 Bus 5 L1 L2 G1 Bus 3 T3 Bus 7 Bus 6 D.6975 Figure Draw the per unit impedance sequence networks and determine the per unit (a) Thevenin impedances of the...
A 7-bus power system with three generators, six transformers, and seven transmission lines is shown in Figure Q1. The per-unit reactances for the generators and transfomers are based on their rated voltage and expressed in percentage. When a three-phase fault occurs at bus 5; three transmission lines, namely L4, L5, and L6, are disconnected from the power system. By taking the base apparent power of 100 MVA and the rated voltage of generator G1 as the reference, determine the per-unit...
Consider the single-line diagram of the three-phase power system shown in Figure 1. Component ratings are as follows: Generator G1: 750 MVA, 18 kV, X0.2 per unit Generator G2: 750 MVA, 18 kV, X 0.2 per unit Synchronous Motor M: 1,500 MVA, 20 kV, X-20% A-Y Transformers Ti, T2, T's, & T.: 750 MVA, 500 kV Y/20 kV A, X = 10% Y-Y Transformer T's 1,500 MVA, 500 kV Y/20 kV Y, X-10% ne L:X (a) Using bases of 100...