Please help me to answer those question and answer with PHASOR MAGNITUDE and PHASE ANGLE
Part 1:
Taking the rated power of generator G1 as the base power, and
the transformer T1 low-voltage
side rated voltage as the base voltage, calculate the Thevanin’s
equivalent zero-sequence
impedance, positive sequence impedance and the negative sequence
impedance viewed from
Bus-2. Specify your answers in per-unit.
Part 2:
Assuming the pre-fault bus voltages are at 1.02 pu, calculate the
fault currents in each phase for a
three-phase balanced fault at Bus-2. Specify your answers in
per-unit.
Part 3:
Assuming the pre-fault bus voltages are at 1.02 pu, calculate the
fault currents in each phase for a
single-line to ground fault at Bus-2. Specify your answers in
per-unit.
EEET2202 - Assignment-2 2018 page 3 of 3
Part 4:
Assuming the pre-fault bus voltages are at 1.02 pu, calculate the
fault currents in each phase for a line-to-line fault at Bus-2.
Specify your answers in per-unit
.
Part 5:
Assuming the pre-fault bus voltages are at 1.02 pu, calculate the
fault currents in each phase for a line-to-line-to-ground fault at
Bus-2. Specify your answers in per-unit.
Please help me to answer those question and answer with PHASOR MAGNITUDE and PHASE ANGLE
Please help me to answer those question and answer with PHASOR MAGNITUDE and PHASE ANGLE Part...
Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96 X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...
Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96 X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...
The component parameters for the power system shown in Figure 2 are given in Table 1. The pre-fault voltage is 120° pu and Zx-j0.1 pu. Table 1 Ratings X2-Xi (pu)Xo (pu) 0.05 0.10 0.20 0.20 Components G1, G2 200 MVA, 20 kV 0.10 0.10 0.10 0.10 T1, T2, T3200 MVA, 20/200 kV L1 200 MVA, 200 kV し2 200 MVA, 20 kV (a) Draw the three sequence networks and determine the per-unit Thevenin impedance of each sequence network seen from...
BUS 1 BUS 2 LINE 1 T1 L1 T2 G1 G2 R = 0,6 pu LINE 2 L2 T3 G3 BUS 3 a) For the above network, draw positive, negative and zero sequence networks (60 marks) b) Provide the main mathematical steps that will allow you to calculate the magnitude (in ampere) of the phase to phase fault current at BUS 1. As part of your answer you should show clearly, on a diagram, how the networks of part (a)...
can you calculating this question and explain why? thanks The ratings and sequence reactances of the components for the power system shown in Figure 2 are given in Table 1. The pre-fault voltage is 1/0° per unit (pu). Bus 8 L3 Bus 1 T1 Bus 4 T2 Bus 2 Bus 5 L1 L2 G1 Bus 3 T3 Bus 7 Bus 6 D.6975 Figure Draw the per unit impedance sequence networks and determine the per unit (a) Thevenin impedances of the...
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
Bus A Bus B R1 T1 line 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96) X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...
No calculations needed, just use written labels given. BUS 1 BUS 2 LINE 1 T1 L1 T2. G1 G2 R= 0.6 pu LINE 2 L2 T3 G3 BUS 3 a) For the above network, draw positive, negative and zero sequence networks (40 marks) b) Provide the main mathematical steps that will allow you to calculate the magnitude (in ampere) of the phase to ground fault at the midpoint of line 1 As part of your answer you should show clearly,...
The equipment ratings for a five bus system are given as Generator G1: 50 MVA, 12 kV, Xd ’’=X2=0.20, X0= 0.10 per unit Generator G2: 100 MVA, 15 kV, Xd ’’=0.2, X2=0.23, X0= 0.10 per unit Transformer T1: 50 MVA, 10 kV (Y)/138 kV (Y), X=0.10 per unit Transformer T1: 100 MVA, 15 kV (∆)/138 kV (Y), X=0.10 per unit Each 138 kV line: X1=40 Ohms, X0=100 ohms (1) Draw out the zero-, positive-, and negative- sequence reactance diagrams for the original system using a 100-MVA,...
For the network shown below, the pu reactance data are equivalent sequence circuit and calculate the fault current in per unit for a bolted single line- to-ground fault at bus 2. The pre-fault bus voltages are assumed to be 1 pu given in the table. Draw the Ti T2 1 2 3 G1 G2 5 X2 Item G1 0.10 0.10 0.05 0.05 G2 0.10 0.10 0.01 T1 0.01 0.01 0.01 T2 0.01 0.01 Line 2-3 0.10 0.10 0.20 Line 3-5...