Bus A Bus B R1 T1 line 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which...
Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96 X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...
Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96 X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...
Bus A Bus B R1 T1 line 1 20% 80% line 2 T2 R2 110 kV 11 kV Note TX impedance TX leakage reactance TX zero sequence impedance-TX positive Data 3 phase fault MVA Bus A 1152 MVA Single P-G level Bus A 8k T1 = T2 = 50MVA X1 0.006 RAk TX1 X2 0.0055 Rik TX2 Earthing resistance-R1-R2-2 ohm z+ sequence reactance 55j) ohm for both sequence impedance Source negative impedance -positive sequence impedance Source zero sequence impedance- purely...
The equipment ratings for a five bus system are given as Generator G1: 50 MVA, 12 kV, Xd
’’=X2=0.20, X0= 0.10 per unit Generator G2: 100 MVA, 15 kV, Xd
’’=0.2, X2=0.23, X0= 0.10 per unit Transformer T1: 50 MVA, 10 kV (Y)/138 kV (Y), X=0.10 per unit Transformer T1: 100 MVA, 15 kV (∆)/138 kV (Y), X=0.10 per unit Each 138 kV line: X1=40 Ohms, X0=100 ohms (1) Draw out the zero-, positive-, and negative- sequence reactance diagrams for the original system
using a 100-MVA,...
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
The following are the answers:
Autumn 2013 T1 G1 5 kV 50 MVA 5/20 kV 50 MVA 20 kV 50 MVA X 0.1 p.u Figure A13 In the system shown, per-unit series equivalent impedances are shown for each element. Before a balanced 3-phase fault occurs in the location shown, the pre-fault current is at its rated value at 90 % lagging power factor flowing from generator G1 The generator is operating at full voltage. How much current in kA is...
Transformer TI : 50 MVA, 10 kV Y/138 kV Y, X=0.10 per unit; Transformer T2: 100 MVA, 15 kV D/138 kV Y, X-0.10 per unit; Each 138-kV line: X1-400 A three-phase short circuit occurs at bus 5, where the prefault voltage is 15 kV. Prefault load current is neglected. (a)Draw the positive-sequence reactance diagram in per-unit on a 100-MVA, 15-kV base in the zone of generator G2. Determine: (b) the The'venin equivalent at the fault, (c) the subtransient fault current...
Styles AC Bus Local Loads T: OC Bus PV Generating DC/AC Station Zline Local Power Grid Inverter T1 T2 Figure Q2 In the microgrid in figure Q2, a solar PV station and the local power grid supply a series of local loads The PV generating station is rated at 2 MW and is operating at unity power factor. The PV station internal impedance is purely resistive equal to 50% based on its own rating of 2 MVA. The inverter DC...
I need help in matlab codes please
Single line to ground fault analysis Example 9.4 Problem 1 A three-phase, il kV, 30 MVA alternator with grounded neutral has a direct axis subtransien pu respectively based on system base. A single line to ground fault has occurred in phase a. Determine the fault current, line to ground voltages in pu. t, negative sequence and zero sequence reactances of 0.2 pu, 0.3 pu and 0.1 Solution: Phase voltage E.0 pu From equation...
2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...