Question

Consider the system Shown in the single-line diagram of Figure (3). All reactance are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u.

Question.PNG

Consider the system shown in the single-line diagram of Figure (3). All reactances are shown in per unit to the same base. Assume that the voltage at both sources is \(1 \mathrm{p}\).u.

a- Find the fault current due to a bolted- three-phase short circuit at bus \(3 .[10\) points \(]\)

b- Find the fault current supplied by each generator and the voltage at each of the buses 1 and 2 under fault conditions. \([10\) points \(]\)

0 0
Add a comment Improve this question Transcribed image text
Answer #1

In order to find the short cirant fault Current and voltage at each bus, we have to find the Bus impedence matrix for the GivAdding But 6 to Bus : 6.204 0.204 Cool 10.204 6 Bus Adding to Bus 6: hy Steps & 10.20t 3- 8,404 0.204 1 12 13ez lorot stot orCoiners rule : U 24-214741 24A Z122 Zi2- Zia Z42 & soon. АА 71 2 0.264 0.204 0.337 0.204 0.27 0.264 0.204 0. 27 0-337 1313 44 stopper Adding Band on the regione Adding Bus to referencer NA 8.204 cond 0.18 0.139 0.139 0.097 4X4 0.097 0.129 8.097 0.16o.oar 0.066 0.066 0.081 0.14 0.103 0.103 0.13 0.103 0.14 0.103 (+3140.14) 0.066 0.14 4. . 10.085 0.045 0.065 Z Bus = i 10.045Uz - o - Ct213 Up 2 = ush. Plgtes 0 Given that Prefaut voltages to a Eq③ Vg3 vs 3 - Itz zuz faut voltages vo a Vo² = 10²-160-17723 o.11 394 (7) 0-204 Tell 10.2 ruer 02 30.31 - 90.004 &= 120.17923 J j 4033 l supplied by a ha !~ 012223 - [3 2.654] su

Add a comment
Know the answer?
Add Answer to:
Consider the system Shown in the single-line diagram of Figure (3). All reactance are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u.
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in...

    Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u. a- Find the fault current due to a bolted- three-phase short circuit at bus 3. [10 points] b- Find the fault current supplied by each generator and the voltage at each of the buses 1 and 2 under fault conditions. [10 points] 0.1 p.u 0.06 ?.u. 0.25 p.11....

  • Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in...

    Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u. c- Find the fault current due to a bolted-three-phase short circuit in the middle of line 1- 3. [5 points d- Find the voltages at buses 1 and 2 under the fault conditions of part c above [5 points] 0.225 pu. 0.035 pu. 0.2p.u ? 0.15 p.u. 0.215...

  • The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows

    The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence  reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...

  • PROBLEM 5 a Discuss the consequences of short circuit faults on electric power systems [5 Points...

    PROBLEM 5 a Discuss the consequences of short circuit faults on electric power systems [5 Points Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. [5 Points] Consider the system shown in the single-line diagram of Figure (4 per unit to the same base. Assume that the voltage at both sources is 1 p.u .) All reactances are shown in ind...

  • Discuss the consequences of short circuit faults on electric power systems.

    a- Discuss the consequences of short circuit faults on an electric power systems (5 points)  b- Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. (5 points)  Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u.  c- Find...

  • 2. A single-line diagram of the power system considered is shown in Figure P2a, where negative-...

    2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...

  • The reactance data for the power system shown in figure 10.30 in per unit on a...

    The reactance data for the power system shown in figure 10.30 in per unit on a common base is as follows: *************Remember calculations are needed at bus 2 **************** 10.15. The reactance data for the power system shown in Figure 10.30 in per unit on a common base is as follows Item X1 G1 0.10 0.10 0.05 G2 0.10 0.10 0.05 T, 0.25 0.25 0.25 T 0.25 0.25 0.25 Line 1-2 0.30 0.30 0.50 Ti 1 3 2 FIGURE 10.30...

  • A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y...

    A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...

  • Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown...

    Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown in Figure 1. The single line diagram shows a synchronous generator G connected to a large 50 Hz grid via its unit transformer T and a network of three transmission lines. Relevant details of the grid, transformer, generator and overhead lines are provided in Tables I,II,II & IV respectively. A double line to ground fault occurs at bus 3 Questions....

  • Explain the reasons for applying system grounding in electric power systems.

    Explain the reasons for applying system grounding in electric power systems. [4 points] Consider the industrial plant distribution bus which is scpplied by a utility source with per-unit sequence reactances as shown in Figure (4-a). Assume that all reactances are given on a \(5,000-\mathrm{kVA}\) base, and that the plant"s bus voltage is \(4,160-\mathrm{V}\). b- Determine the fault current for a single line to ground fault on phase A of the bus. \([4\) points] Assume now that an ungrounded \(5,000 \mathrm{kVA}\)...