Question

PROBLEM 5 a Discuss the consequences of short circuit faults on electric power systems [5 Points Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. [5 Points] Consider the system shown in the single-line diagram of Figure (4 per unit to the same base. Assume that the voltage at both sources is 1 p.u .) All reactances are shown in ind the fault current due to a bolted- three-phase short circuit in the middle of line B. [5 Points] d Find the voltages at buses 4 and 5 under the fault conditions of part c above [10 Points] 3 0.2 p.u ( 1 0.2 p.u 0.2. Pu. Llne A 0.1 p.u 4 0.2. P.u. Line B 0.1 P.u. - circuit breaker a.c. generator 38 0.1 p.u transformer 0.2 p.u Figure (4) Single-line diagram for Problem (5)

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Solutio for Question A

Short Circuit Occur as a result of breakdown in the insulation of current Carrying Conductors relative to earth or insulation between phases

Different types of short circuit fault occur in the power systam are

1 Single phase to Ground

2 Phase to phase

3 Two phase to ground

4 phase to phase and third phase to ground

5 All Three phases to ground

6 All 3 phases short circuited

Faults 1 to 4 are classified as unsymmetrical faults

Faults 5 to 6 are classified as symmetrical faults

Consequence of Short circuit Faults

1 Heavy currents due to short circuits cause excessive heating which results in fire or explosion

2 Stability of power system may be adversely affected even leading to shutdown of entire plant

3 Damage will be caused to other apparatus in the system due to overheating

4 Reduction in voltage will be so large that relays having high pressure coils tend to fails

5 Interruption in power supply to consumers when power circuits or generating units are switched off

6 Considerable reduction in voltage on healthy feeders connected to the system having faults which lead to abnormally high current drawn by the motors

B Transformer Protctive Schemes

1 Buchloz Protection

When Internal faults occur in an oil immersed power transformer gas is usually generated slowly for an incipient fault and violently for heavy faults.most short circuit caused either by impulse breakdown between adjacent turns at the end turns of the winding or as a poor initial point contact which will immediately heat to arcing temperature.The heat generated by large local currents causes the transformer oil to decompose and generate gases which may be used in detection of winding faults.The relays based on this principle are gas accumulated relays known as Buchhloz relay This type of protection is mainly used for oil immersed transformer

2 Core Balance leakage protection

Due to earth faults there will be partial break down of winding insulation to ground.this leakage current will be very small compred to short circuit currents.If this earth faults persisits for a long time and causes considerable damage before it ultimately devlops in to short circuit faults.An earth faults relay used for this is an overcurrent relay of lower setting and operates when earth faults develops.

3 Combined leakage and overeload protection

Used for protection against phase to phase and earth faults.The overload relays are used to provide protection against phase to phase faults while earth faults relay has low current setting and operates under leakage or earth faults only

4 Differential Protection

The Differential protection used in power transformers provied protection against internal phase to phase and phase to earth faults and is generally used for transformers of rating exceeding 2 MVA.This protection is based on Merz-price circulating current principle.

  

Add a comment
Know the answer?
Add Answer to:
PROBLEM 5 a Discuss the consequences of short circuit faults on electric power systems [5 Points...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Discuss the consequences of short circuit faults on electric power systems.

    a- Discuss the consequences of short circuit faults on an electric power systems (5 points)  b- Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. (5 points)  Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u.  c- Find...

  • Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in...

    Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u. a- Find the fault current due to a bolted- three-phase short circuit at bus 3. [10 points] b- Find the fault current supplied by each generator and the voltage at each of the buses 1 and 2 under fault conditions. [10 points] 0.1 p.u 0.06 ?.u. 0.25 p.11....

  • Question3 3000 kVA / 0.09 p.u. Alternators 2 40004VA 0.12 p.u 6kV Busbars 4000 LVA 0.05 p.. Transmission Lines Lin...

    Question3 3000 kVA / 0.09 p.u. Alternators 2 40004VA 0.12 p.u 6kV Busbars 4000 LVA 0.05 p.. Transmission Lines Lines 4000 kV 0.05 p.ย. Step-Up Transformers 5000 kVA 5000 kVA 0.06 р.u. 0.06 p.u. 11 kV Basbars -150 kVA 0.05 pu. Secondary feeder line Step-Down 1500 kVA 0.03 p.u 415 V Busbars Fault Point Figure Q3 Figure Q3 shows a power system comprising two three phase alternators supplying 6 kV busbars. I wo paralilel transmission lines fed from these busbars...

  • Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in...

    Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u. c- Find the fault current due to a bolted-three-phase short circuit in the middle of line 1- 3. [5 points d- Find the voltages at buses 1 and 2 under the fault conditions of part c above [5 points] 0.225 pu. 0.035 pu. 0.2p.u ? 0.15 p.u. 0.215...

  • Explain the reasons for applying system grounding in electric power systems.

    Explain the reasons for applying system grounding in electric power systems. [4 points] Consider the industrial plant distribution bus which is scpplied by a utility source with per-unit sequence reactances as shown in Figure (4-a). Assume that all reactances are given on a \(5,000-\mathrm{kVA}\) base, and that the plant"s bus voltage is \(4,160-\mathrm{V}\). b- Determine the fault current for a single line to ground fault on phase A of the bus. \([4\) points] Assume now that an ungrounded \(5,000 \mathrm{kVA}\)...

  • 15 (c) Consider the single-line diagram of the power system shown in Figure. Neglect all resistances,...

    15 (c) Consider the single-line diagram of the power system shown in Figure. Neglect all resistances, transformer phase shift, and magnetizing reactances. The given positive, negative and zero sequence reactances are based on common base. i. Sketch the positive, negative and zero sequence reactance diagrams for the given system. ii. Calculate the fault current for a line-line fault (b-c fault) at bus 5. iii. Calculate the three phase voltages at the fault of part (ii). AE AE 0.2) X.=X=0.06 X=0.17j...

  • A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y...

    A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...

  • Zone 1 Zone 3 Zone 2 Xice j1002 BE SO MW 0.8 pf lagging Vload =...

    Zone 1 Zone 3 Zone 2 Xice j1002 BE SO MW 0.8 pf lagging Vload = 30 kV Ti 50 MVA 11/132 kV X= 10% Tz 50 MVA 132/33 kV X=12% Figure 1 2. A 500 MVA, 20 kV, 50 Hz synchronous generator with reactances Xd" = 0.15, Xá = 0.24, Xo = 1.1 p.u. and time constant To = 0.035, Tó' = 2.0, TA = 0.2 seconds is connected to a circuit breaker. The generator is operating at 5%...

  • PLEASE SOLVE THIS POWER / LOAD FLOW 07-Elec-B December 2016 Page 7 of 7 Problem 7...

    PLEASE SOLVE THIS POWER / LOAD FLOW 07-Elec-B December 2016 Page 7 of 7 Problem 7 Consider the system shown in the single-line diagram of Figure (5). Here, a 60-Hz synchronous generator having a transient reactance of 0.15 pu. is connected to an infinite bus through a transformer whose reactance is 0.1 p. u. and a double circuit transmission line with circuits having a reactance of 0.6 p.u each as indicated in the figurc. The generator delivers a real power...

  • Problem 7 Consider the circuit shown in Figure (4.) Assume that E 1.2 p.u. and V 1.00 p.u. where a three-phase fault takes place at the point F as shown. The fault is cleared by opening the faulted l...

    Problem 7 Consider the circuit shown in Figure (4.) Assume that E 1.2 p.u. and V 1.00 p.u. where a three-phase fault takes place at the point F as shown. The fault is cleared by opening the faulted line. a Find the initial power angle when the active component of the load on the circuit is 1 p.u. b Find the power angle curve, during the fault. [5 points] c Find the post fault power angle curve. [5 points] [5...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT