Explain the reasons for applying system grounding in electric power systems. [4 points]
Consider the industrial plant distribution bus which is scpplied by a utility source with per-unit sequence reactances as shown in Figure (4-a). Assume that all reactances are given on a \(5,000-\mathrm{kVA}\) base, and that the plant"s bus voltage is \(4,160-\mathrm{V}\).
b- Determine the fault current for a single line to ground fault on phase A of the bus. \([4\) points]
Assume now that an ungrounded \(5,000 \mathrm{kVA}\) generator is added at the distribution bus as shown in Figure (4-b). [4 points]
c- Determine the fault current for a single line to ground foult on phase A of the bus. [4 points]
Assume now that the utility transformer is grounded through a \(8 \Omega\) grounding resistor as shown in Figure (4-c.)
d- Determine the value of the grounding resistor in per unt. [4 points]
Determine the fault current for a double line to ground fault on phases \(B\) and \(C\) of the bus. [4 points]
Explain the reasons for applying system grounding in electric power systems.
Consider the system of Figure (4) The reactances of all components in p.u. are indicated in Table (2) a- Sketch and label carefully the positive, negative, and zero sequence equivalent networks for this system including the switch S. Note that the switch is normally closed when the high voltage side of the transformer is grounded. An open switch means a broken ground connection. 15 Points) b. Assume that a double line to ground fault takes place on phases B and...
Consider the system shown in the single-line diagram of Figure (3). All reactances are shown in per unit to the same base. Assume that the voltage at both sources is \(1 \mathrm{p}\).u. a- Find the fault current due to a bolted- three-phase short circuit at bus \(3 .[10\) points \(]\) b- Find the fault current supplied by each generator and the voltage at each of the buses 1 and 2 under fault conditions. \([10\) points \(]\)
QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where negative and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance X.=0.05 per unit on the motor base. Prefault voltage is VF1.05<Oº per unit whereas prefault load current is zero. Take A-Y transformer phase shifts into consideration. M Line tool X, - X2 - 200 100 MVA X =...
2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...
The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
(10 points) For the power system shown below, sketch the sequence circuit connections for a 02, phase A to ground fault at bus B, and develop the equation for calculating the fault current in sequence coordinates. The sequence impedances of the generator and transformer are shown in the figure. T1 B (GENHH OH SLG FAULT Generator: Zs1 = Zs2, Zso, Y-grounded T1: Zy1 = Z12 = Zto, Delta-Wye Grounded Fault: Phase A to Ground, Z = 0
The positive-sequence reactances for the power system shown in Figure 10.31 are in per unit on a common MVA base. Resistances are neglected and the negative-sequence impedances are assumed to be the same as the positive-sequence impedances. A bolted line-to-line fault occurs between phases b and c at bus 2.Before the fault occurrence, all bus voltages are 1.0 per unit. Obtain the positive-sequence bus impedance matrix.Find the fault current, the three-phase bus voltages during fault, and the line currents in...
The one-line diagram of a simple power system is shown in Figure 1. The neutral of each generator is grounded through a current-limiting reactor of 0.25/3 per unit on a 100-MVA base. The system data expressed in per unit on a common 100-MVA base is tabulated below. The generators are running on no-load at their rated voltage and rated frequency with their emfs in phase. Determine the fault current for the following faults giving Zo = 0.35, Z = 0.22...
a- Discuss the consequences of short circuit faults on an electric power systems (5 points) b- Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. (5 points) Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u. c- Find...