Question

Find the perphase

A balanced three-phase source is supplying 60 kVA at 0.6 lagging to two balanced Y-connected parallel loads. The distribution line connecting the source to the load has negligible impedance. Load 1 is purely resistive and absorbs 30 kW. Find the per-phase impedance of Load 2 if the line voltage is and the impedance components are in series

0 0
Add a comment Improve this question Transcribed image text
Answer #1

answered by: anonymous
Add a comment
Answer #2

Load1 is pure resistive load .Load2 is unknownST=60KvA at 0.6 lagging KvA of total load                    cos0PT=60 KvA x 0.6 =36 KwQT=60KvA x sin cos-10.6=60 KvA x 0.8=48K VAR laggingP1=30 kwQ1=0 KVARS1=30 KVAR Pure resistive load

 



answered by: anonymous
Add a comment
Know the answer?
Add Answer to:
Find the perphase
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an...

    508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • 5. The line to neutral voltages of a Y-connected three phase source are given by, The...

    5. The line to neutral voltages of a Y-connected three phase source are given by, The above three phase source is directly connected to a delta connected balanced three phase resistive load. The resistance in each phase is 10 ohms. Calculate the current phasor 0. Answer- 4. Following three loads are connected in parallel across a single-phase source voltage source: Load 1 absorbs 15 kW and 6.667 kvar; Load 2 absorbs 3 kVA at 0.96PF leading; Load 3 absorbs 15...

  • of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is...

    of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is connected to the following loads via 0.5+0.25 j 0/phase line. A Y-connected 900 kVA at 0.7 pf lagging load. · A ?-connected 500 kw at 0.6 pf lagging load. A Y-connected 350 kVAR at 0.7 pf lagging load. · 4-connected 600 kW at 0.6 pf lagging load. A Part 1: If the load voltage is always kept at 11 kV a) what is the...

  • 10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from...

    10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...

  • EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT...

    EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT I CAN EASILY UNDERSTAND WHAT WE ARE FINDING AND HOW WE ARE FINDING THE REQUIRED THINGS .I AM POSTING MY QUESTION 4TH TIME PLEASE DONOT WASTE IT AND PLEASE DO ALL STEPS I NEED MY ANSWER STEP BY STEP by the line Two balanced Y-connected loads, one drawing 10 kW at 0.8 power factor lagging and the other 15 kW at 0.9 power factor...

  • The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a...

    The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a line-to-line voltage of 480 V. The loads are described below: • Load 1: ∆-connected, total three-phase apparent power is 30 kVA at 0.95 power factor lagging. • Load 2: ∆-connected, total three-phase active power is 20 kW at 0.7 power factor lagging. • Load 3: Y-connected, phase current is 30 A, and power factor is 0.9 pf leading. (a) Calculate the total complex power...

  • 1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF...

    1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF lagging Load 2 draws 20 kVA at 0.6 PF leading a. b. The loads are supplied by a balanced three-phase 480 Vu source. (a) Draw the power triangle for the combined load. (b) Determine PF of the combined load. (c) Determine the magnitude of the line current from the source. (d) Y-connected inductors are now installed in parallel with the combined load. What value...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...