The low pressure side of the 3,300v/220v transformer was opened and the high pressure side was applied with 3,300v. In this case, current 1A flows and the power factor is 0.12.
What would the current flow be if the high pressure side of the transformer was opened and 220v applied to the low pressure side? Also, what is the effective and reactive power?
Real power when LV side is opened
P=VI*pf
P=3300*1*0.12
P=396W
Reactive power
Q=3300*1*0.992
Q=3276.1 Var
Now HV side opened
S=VI
220*I=3300*1
I=15A
P=396W
Q=3276.1 Var
The low pressure side of the 3,300v/220v transformer was opened and the high pressure side was...
For 3,300V/220V transformer, open the low pressure side and input voltage of high pressure side was 3,300V and the current was 1A P.F. was 0.12 lagging. With this condition, connect load to low pressure side wich P.F. is 0.8 and it current flows 150A. In this moment what are the current and new P.F. of high pressure side?? Also draw phasor diagram before and after of connecting load.
3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2 and Xeais 0.0433 12. The transformer is operating in the step-down mode and is delivering rated current at rated voltage to a 0.840 power-factor lagging load. Determine (a) the no- load voltage; (b) the actual input voltage at the high side; (c) the high-side current; (d) the input impedance; (e) the voltage regulation; the voltage regulation if the power factor of the load is...
5. Consider the one-ine diagram shown below. The three-phase transformer bank is made up of three identical single-phase transformer, each specified by X1-0.004 Ω (on the high-voltage side), negligible resistance and magnetizing current, and turns ratio N2/N,-10. The transformer bank is delivering is delivering 110MW at 0.9 power factor leading to a substation bus voltage is 230kV. Determine the reactive power supplied by the source. (3.47) whose To rest of the system Generator ΔΥ 230-kV substation bus Step-up transformer bank...
EMM2802 MAYIJUNE 2016 QUESTION B A single phase transformer has a high voltage to low voltage ratio of 10. The following parameters are referred to low voltage side, with a supply of 200V. Equvalent Impedance referred to low woltage side Zev 0.1+jo.s a Load impedance referred to low voltage side R-4000 X-2310 Magnetizing Branch referred to low voltage side Draw an approximate equivalent circut with the given parameters and determine the following: 81 The magnetizing current (), the core loss...
3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...
4. The figure below shows the equivalent circuit of a 2400/240-V, 60-Hz transformer. The high-side leakage impedance is (1.2+j 2.0) 2. the low-side leakage impedance is (0.012 ti 0.02) S2, and Xm at the high-side is 1800 2. Neglect the Hysteresis and Eddy current loss resistance Rhe Calculate the input voltage if the output voltage is 240 V (rms). Given the load resistance is 1.5 12 and the power factor is 0.8 (lagging). ཉིས་པ་དེ། དེ་ | ༼ ། ༼། །
Problem # 2-A single phase, 60 Hz, 10 KVA, 440110 V has the following parameters: R1=0.15 R2=0.0086 X1=0.5 X2-0.0286 Re and Xmare 1500 and 1000 referred to the high voltage side. Using the approximate equivalent circuit, Calculate the transformer no load current, power factor and power when terminal voltage is 470 a- V. What would these values be if the transformer were ideal? Calculate the transformer output power and efficiency when load of 1.6+j1.2 ohms is connected b- to its...
Problem # 2-A single phase, 60 Hz, 10 KVA, 440/ 110 V has the following R1 0.15 R 0.0086X 0.5 X 0.0286 Re and Xnare 1500 and 1000 referred to the high voltage side Using the approximate equivalent circuit, Calculate the transformer no load power a- current, power factor and power when terminal voltage is 470 V. What would these values be if the transformer were ideal? b Calculate the transformeroutput power and eficiency when load of 1.6+j1.2 ohms is...
The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...
Problem 3 A 50-Hz transformer is operated from a 60 Hz supply. Assume that the load does not change. Discuss the corresponding effects on its flux, reactive power requirements, losses, and efficiency. а- [5 Points] A 50-kVA, 2400/240 V, 60-Hz, single-phase distribution transformer has the following equivalent circuit parameters referred to the high-voltage side Xea 3.0 Req= 0.5 Xm 4,500 S2 Use the equivalent Cantilever model circuit shown in Figure (1). Assume that the load on the secondary of the...