Question

QUESTION 2 Calculate heat loss through square foot of construction assembly consisting of 4 in brick...

QUESTION 2 Calculate heat loss through square foot of construction assembly consisting of 4 in brick veneer, vapor barrier, ½ in plywood, insulation with 2x4 @16” stud spacing (R- value of 10) and ½” drywall DB difference in temperature of 20°F. Round off R of wall to whole number.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Ans) We know,

Heat loss, q = U A T

where, U = U-factor of wall = 1 / R-value

A = Area of wall

  T = Temperature difference

R-value = R1 + R2..................Rn

R1 = R-value of 4" brick veneer = 0.80 F ft2 hr/BTU

R2 = R-value of vapor barrier = 0

R3 = R-value of plywood = 0.62 F ft2 hr/BTU

R4 = R-value of insulation = 10 F ft2 hr/BTU

R5 = R-value of 1/2" drywall = 0.45 F ft2 hr/BTU

=> Total R -value = 0.80 + 0.62 + 10 + 0.45 = 11.87 F ft2 hr/BTU

Hence, U-value = 1/11.87 = 0.0842 BTU/ F ft2 hr

Putting values,

=> q = 0.0842 BTU/ F ft2 hr x 1 ft2 x 20 F

=> q = 1.684 BTU/hr per ft2

Hence, heat loss per square ft of given assembly is 1.684 BTU/hr

Add a comment
Know the answer?
Add Answer to:
QUESTION 2 Calculate heat loss through square foot of construction assembly consisting of 4 in brick...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • summarizr the followung info and write them in your own words and break them into different...

    summarizr the followung info and write them in your own words and break them into different key points.   6.5 Metering Chamber: 6.5.1 The minimum size of the metering box is governed by the metering area required to obtain a representative test area for the specimen (see 7.2) and for maintenance of reasonable test accuracy. For example, for specimens incorporating air spaces or stud spaces, the metering area shall span an integral number of spaces (see 5.5). The depth of...

  • summatize the following info and break them into differeng key points. write them in yojr own...

    summatize the following info and break them into differeng key points. write them in yojr own words   apartus 6.1 Introduction—The design of a successful hot box appa- ratus is influenced by many factors. Before beginning the design of an apparatus meeting this standard, the designer shall review the discussion on the limitations and accuracy, Section 13, discussions of the energy flows in a hot box, Annex A2, the metering box wall loss flow, Annex A3, and flanking loss, Annex...

  • Auge Steel Framing Details 1. Complete all light g auge steel componente ir the following wall se...

    auge Steel Framing Details 1. Complete all light g auge steel componente ir the following wall section, including floor joists, wall studs, roof rafters, and required clips angles, stiffeners, and fasteners. Label all components. Roof sheathing Wall sheathing 。 Interior wallboard Subflooring Foundation 103 Scale: l square =2" (50 mm) Name: necessity of cutting holes in m on the construction ste 12.11. 12.15). Thack etions a sed for top and bottom plates, e construction, shemperature that col tural shapes. Prers...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT