Question

A three phase distribution substation transformer has a nameplate rating of 7250 kVA and a thermal...

A three phase distribution substation transformer has a nameplate rating of 7250 kVA and a thermal capability of 120% of nameplate rating. If the connected load on the transformer is 8816 kVA at a power factor of 0.85 lagging, determine the following:
The kilovar rating of the shunt capacitor bank required to decrease the kilovoltampere load on the transformer to its thermal capability level.
The power factor of the corrected load.
The kilovar rating of the capacitor bank to correct the power factor of the load to 0.95 and unity.
Sketch a graph of capacitor requirement (kVar) against power factor and comment on the fact that power factor correction is seldom brought to unity.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

one thumbs up please.

Thank you.

Add a comment
Know the answer?
Add Answer to:
A three phase distribution substation transformer has a nameplate rating of 7250 kVA and a thermal...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation...

    Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation bus supplies three wye-connected three phase loads that are connected in parallel through a three-phase feeder with an impedance of 0.3 30 per phase Load 1 draws 75kVA at 0.866 lagging power factor, load 2 draws 45 kW at 0.70 leading power factor and load 3 draws 20 kVAR at 0.85 lagging power factor. The line-line voltage at the load is 460V Take the...

  • can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has...

    can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has a full-load efficiency of 98% at 0.8 lagging power factor. The transformer core loss is 80 kW. The transformer supplies an industrial load that has a constant demand of 5000 kW at 0.65 lagging power factor. The cost of energy is $0.1 per kWh. 1. In the following questions, assume that the voltage at the load terminal is maintained constant at 22 kV. calculations....

  • A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at...

    A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at power factor of 0.8 lagging. Find: The feeder current in A, real power in kW and Reactive power in kVAr. The capacitor size in kVAr to improve the power factor to 0.98. The feeder power in kW and kVA and current in A, after installing the capacitor bank.

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Please show full working Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and power efficiency...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Help me answer c and d Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • (a) A 240 V 50 Hz factory electrical system has the following loads connected in parallel:...

    (a) A 240 V 50 Hz factory electrical system has the following loads connected in parallel: Load 1: 4 kW at a power factor of 0.8 lag Load 2: 6 kVA at a power factor of 0.6 lag Load3: 6.5 kVA with 2.5 kVAr of leading reactive power Determine: (C) the overall system power factor, (ii) the value of a power-factor correction capacitor to improve the power factor to unity, and (ii) the value of a power-factor correction capacitor to...

  • A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel...

    A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?

  • 2.14 The resistances and leakage reactances of a 40-kVA 60-Hz 7.97-kV-V:240-V single-phase distribution transformer are where...

    2.14 The resistances and leakage reactances of a 40-kVA 60-Hz 7.97-kV-V:240-V single-phase distribution transformer are where subscript 1 denotes the 7.97-kV winding and subscript 2 denotes the 240-V winding. Each quantity is referred to its own side of the transformer. Consider a rated-kVA load connected at the low-voltage terminals. Assuming the load voltage to remain constant at 240 V use MATLAB to plot the high-side terminal voltage as a function of the power-factor angle as the load power factor varies...