Consider a 2-generator power system feeding a load through transmission network as shown in Figure below. The impedance data of the network is given in pu values on 100 MVA base. Using NR method find the bus voltages after two i terations. The scheduled power and nominal bus pu bus voltages are indicated in Figure below.
Consider a 2-generator power system feeding a load through transmission network as shown in Figure below....
(POWER SYSTEM ANALYSIS) Load + Load Figure 1. One line diagram of a three bus power transmission system. In Figure 1, the power flows in the transmission lines are to be found. In this system, 100 MVA and 154 kV are the base values. The generator bus, which is shown as Bus 1, is considered to be an infinite bus and the voltage magnitude and the angle are 1 and 0°, respectively. The voltages of Bus 2 and Bus 3...
Exercise 3 Consider a 2 generator 4 bus power system shown in Figure E3. The impedance data of the network in p.u. are given in Figure E3. A bolted symmetrical three phase fault occurs at bus 4. Assuming the prefault bus voltages as I p.u., calculate the fault current and the current delivered by the generators during the fault and the bus voltages during the fault. j0.12 0.05 0.16 j0.18 j0.12 0.15 0.05 j0.12 j0.1 j0.14 4 (2 Figure E3:...
2. Three generators feed a 2-transmission line network (see below). Each component of the network is expressed in per-unit on its own power and voltage rating 100 MVA 138 kV 14 0.03 Bus 1 Bus 4 100 MVA 138 kV XL24 = j0.02 Bus 2 2 50 MVA 13.2 KV G10.1 pu XT0.2 pu 50 MVA 132/13.2 kV 100 MVA 138/20 kV XT2uX2 0.1 pu 100 MVA 18 kV 35 MVA 132/13.2 kV XT3 = 0.2 pu Bus 3 20...
A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...
Answer part D The single line diagram of a power network is shown in the figure. Bus#1 is a slack bus. The scheduled powers for bus#2 and bus#3 are given. The impedances shown in the figure are all in per-unit considering a power base of 100 MVA. 30 400 MW 320 MVAr Slack V-140 j0.0125 jo.0s 00 MW 270 MVAr A. Use the Gauss Seidel technique to determine voltages at bus#2 & bus#3. (Start with an initial guess 140 for...
Assume a round-rotor generator delivering power in the steady state to a load bus through two transformers and a transmission line. The topology of the system is shown as below XL Хо Xi/2 XP Figure Q5 Parameters are as follows: G: Xgi -0.10 TI: Х,1-0, 10 12: XT2-0.20 0.40 Initial state: E1-1 .6 ,見= 1.6 (a) Please determine the maximal real power that can be delivered through the transmission system. (b) Please determine 6 at the steady state. (c) Assume...
Qustion 2.120 marks) a) Figure I below shows a system with plant-I and plant-2 connected to bus-1 and bus-2 respectively. There are two loads and 3 branches. The bus-I is the reference bus with 1.040° pu voltage. Base MVA is 100 If the branch currents and branch impedance values are as follows -2.5-j0.50pu -2-j040 pu I 1.5-j0.3 pu Calculate: 7-0.05+j0.20 pu -0.02+j0.08 pu Z 0.025+j0.10 pu i. Current distribution factors (4 marks) ii. Power factor angles at bus 1 and...
The six-bus system shown in Figure 1 will be simulated using MATLAB. Transmission line data and bus data are given in Tables 1 and 2 respectively. The transmission line data are calculated on 100 MVA base and 230 (line-to-line) kV base for generator. Tasks: 1. Determine the network admittance matrix Y 2. Find the load flow solution using Gauss-Seidel/Newton Raphson method until first iteration by manual calculation. Use Maltab software to solve power flow problem using Gauss-Seidel method. Find the...
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
A generator bus(with 1.0 per unit voltage)supplies a 180MW, 60Mvar load through a lossless transmission line with per unit (100 MVA base) impedance of j0.1 and no line charging. Starting with an initial voltage guess of 0.8<0◦,iterate until converged using the Newton-Raphson power flow method. For a convergence criteria, use a maximum power flow mismatch of 0.1 MVA.